Old 03-07-2012, 12:50 PM   #15
Senior Member
 
Steve N Sal's Avatar
 
Newmar Owners Club
Workhorse Chassis Owner
Join Date: Oct 2007
Location: Michigan
Posts: 5,692
Quote:
Originally Posted by Clifftall View Post
Thanks Joe. I have the plugs, so my best bet would be to get a length of 6/4 and be sure. I still don't know what SO and SOOW means. Does it have to say that on the wire?
SO and SOOW is a rating appied to the outside jacket of the wire. They are both 600Volt rated cords and either rating will work. The labeling is in concern with environment conditions of various type. Wet, Oil, Chemicals etc. In this case any would work for application you are using it for.

The range cable mentioned is a pre-assembled cord cut to length with the male end already attached. You would need to purchase the female end and attach it yourself. I've never heard of one that has 6/2/-8/2. They are usually 6/3 - 8/1 meaning you have three #6 conductors (L1-L2& Neut) plus one #8 conductor (green) which will be the grounding conductor. This cord would work as well but sometime trying to remove it from a receptacle can be a little difficult as it may hard to get a good grip on it to pull it out.

Hope this helps a bit.
__________________
Steve & Sally / Hudson Our Little Pom / Heidi, Houston & HiTee Forever in our Hearts
04 NEWMAR MACA 3778 W22 / 05 PT Vert
Michigan (Summer) Michigan (Winter For Now)
Steve N Sal is offline   Reply With Quote
Join the #1 RV Forum Today - It's Totally Free!

iRV2.com RV Community - Are you about to start a new improvement on your RV or need some help with some maintenance? Do you need advice on what products to buy? Or maybe you can give others some advice? No matter where you fit in you'll find that iRV2 is a great community to join. Best of all it's totally FREE!

You are currently viewing our boards as a guest so you have limited access to our community. Please take the time to register and you will gain a lot of great new features including; the ability to participate in discussions, network with other RV owners, see fewer ads, upload photographs, create an RV blog, send private messages and so much, much more!

Old 03-07-2012, 12:53 PM   #16
Community Administrator
 
CLIFFTALL's Avatar


 
Join Date: Aug 2009
Posts: 53,561
Blog Entries: 1
Quote:
Originally Posted by Steve N Sal

SO and SOOW is a rating appied to the outside jacket of the wire. They are both 600Volt rated cords and either rating will work. The labeling is in concern with environment conditions of various type. Wet, Oil, Chemicals etc. In this case any would work for application you are using it for.

The range cable mentioned is a pre-assembled cord cut to length with the male end already attached. You would need to purchase the female end and attach it yourself. I've never heard of one that has 6/2/-8/2. They are usually 6/3 - 8/1 meaning you have three #6 conductors (L1-L2& Neut) plus one #8 conductor (green) which will be the grounding conductor. This cord would work as well but sometime trying to remove it from a receptacle can be a little difficult as it may hard to get a good grip on it to pull it out.

Hope this helps a bit.
Yes it does. Thank you.
__________________


Cliff,Tallulah and Buddy ( 1999-2012 )
CLIFFTALL is offline   Reply With Quote
Old 03-07-2012, 02:58 PM   #17
Moderator Emeritus
 
SarahW's Avatar


 
Join Date: Oct 2011
Location: In a lawnchair
Posts: 11,993
Quote:
Originally Posted by Clifftall View Post
Home Depot had 6/4. $ 5.50 a ft. EEK

Attachment 18557
Peanuts to you rich RV guys.
__________________
SarahW is offline   Reply With Quote
Old 03-07-2012, 03:08 PM   #18
Community Administrator
 
CLIFFTALL's Avatar


 
Join Date: Aug 2009
Posts: 53,561
Blog Entries: 1
Quote:
Originally Posted by SarahW

Peanuts to you rich RV guys.
I only bought 4'.
__________________


Cliff,Tallulah and Buddy ( 1999-2012 )
CLIFFTALL is offline   Reply With Quote
Old 03-07-2012, 03:13 PM   #19
Senior Member
 
codgerbill's Avatar
 
Winnebago Owners Club
Join Date: Sep 2007
Location: Ann Arbor Michigan
Posts: 792
If you dont need the plug, you can go to any electric supply house and buy the cable for however many feet you need. If you do need the plug the supply house and any place like Home Depot or Lowes will have it.
__________________
2005 Suncruiser
Banks Powerpack
Chocolate lab (Buster)
2007 Jeep Wrangler
codgerbill is offline   Reply With Quote
Old 03-07-2012, 03:19 PM   #20
Community Administrator
 
CLIFFTALL's Avatar


 
Join Date: Aug 2009
Posts: 53,561
Blog Entries: 1
Quote:
Originally Posted by codgerbill
If you dont need the plug, you can go to any electric supply house and buy the cable for however many feet you need. If you do need the plug the supply house and any place like Home Depot or Lowes will have it.
That's what I did. See above.
__________________


Cliff,Tallulah and Buddy ( 1999-2012 )
CLIFFTALL is offline   Reply With Quote
Old 03-07-2012, 03:23 PM   #21
Senior Member
 
Steve N Sal's Avatar
 
Newmar Owners Club
Workhorse Chassis Owner
Join Date: Oct 2007
Location: Michigan
Posts: 5,692
Yeah the price of copper these days is out of site. Just like the fuel prices.
__________________
Steve & Sally / Hudson Our Little Pom / Heidi, Houston & HiTee Forever in our Hearts
04 NEWMAR MACA 3778 W22 / 05 PT Vert
Michigan (Summer) Michigan (Winter For Now)
Steve N Sal is offline   Reply With Quote
Old 03-08-2012, 07:35 AM   #22
Moderator Emeritus
 
Gary RVRoamer's Avatar


 
Join Date: Jan 2000
Location: West Palm Beach, FL. USA
Posts: 27,713
AWG merely tells you the size of the wires inside. Other designations refer to the whole package, e.g. insulation type, heat range, indoor or outdoor use, voltage, etc. Some common examples are type NM (regular indoor house wiring) and UF (underground feeder). For RV shore cord usage, you want something rated for outdoor use (not range wire "pigtail") and resistance to damage from rocks and such. Theer are several wire types rated for use as a "Portable Cable" but SOOW is the most common one used for Rvs.

Type SOOW is designated for portable power cables and rated for indoor or outdoor use and resistance to water, abrasion and ultraviolet

POrtable Cable Wire types:
Power Cables & Portable Cord from Allied Wire & Cable

You really want 6/4 (or 6/3,8/1) for an RV 50A power cord. The electrical load in an RV is often severely imbalanced, which means the neutral has to be the same #6 size as the two #6 hots. It's ok to have the ground be slightly smaller (#8) becasue it is not normally a current carrying wire and thus not subject to heat and overload concerns.

I would not use a range cord pigtail because the wire is not rated for outdoor use.
__________________
Gary Brinck
Former owner of 2004 American Tradition and several other RVs
Home is West Palm Beach, FL
Gary RVRoamer is offline   Reply With Quote
Old 03-08-2012, 09:38 AM   #23
Registered User
 
Ford Super Duty Owner
Join Date: Mar 2011
Posts: 520
Quote:
Originally Posted by Clifftall View Post
No problem. I am installing a 50 amp portable progressive surge protector in a basement compartment. I need to make a 3-4' cord coming from ceiling of compartment ( where power cord comes down from transfer switch in bedroom ) to plug into surge protector.
I plan to do the same thing in a couple of weeks. I am going to cut my existing power cord 3 to 4 feet from the end that connects to the Bounder and install connectors to connect to the EMS-PT50C. This will keep the surge protector in the wet/sewer/electrical bay out of weather and out of sight. I know this will make my power cord a few feet shorter but I carry a 30' extension.
Great minds do think alike Cliff.
Hipshot is offline   Reply With Quote
Old 03-08-2012, 09:53 AM   #24
Community Administrator
 
CLIFFTALL's Avatar


 
Join Date: Aug 2009
Posts: 53,561
Blog Entries: 1
Yeah buddy.
__________________


Cliff,Tallulah and Buddy ( 1999-2012 )
CLIFFTALL is offline   Reply With Quote
Old 03-08-2012, 10:30 AM   #25
Community Administrator
 
CLIFFTALL's Avatar


 
Join Date: Aug 2009
Posts: 53,561
Blog Entries: 1
Quote:
Originally Posted by Hipshot
I plan to do the same thing in a couple of weeks. I am going to cut my existing power cord 3 to 4 feet from the end that connects to the Bounder and install connectors to connect to the EMS-PT50C. This will keep the surge protector in the wet/sewer/electrical bay out of weather and out of sight. I know this will make my power cord a few feet shorter but I carry a 30' extension.
Great minds do think alike Cliff.
I have a few ideas of where I'm going to mount it , but don't like any of them. Have you given any thought on how you plan to do it?
__________________


Cliff,Tallulah and Buddy ( 1999-2012 )
CLIFFTALL is offline   Reply With Quote
Old 03-08-2012, 11:15 AM   #26
Registered User
 
Ford Super Duty Owner
Join Date: Mar 2011
Posts: 520
Quote:
Originally Posted by Clifftall View Post
I have a few ideas of where I'm going to mount it , but don't like any of them. Have you given any thought on how you plan to do it?
I don't know yet. I was going to lay it on it's back in front of the water panel just inside the storage compartment door. Don't realy like that location, puts it in direct line of the water connection and as we know want can go wrong will. I have a couple of weeks so I may take another look about where to mount it. Maybe on the right wall near the plug. It depends on how tight the cable will bend. What have you come up with?
Hipshot is offline   Reply With Quote
Old 03-08-2012, 11:31 AM   #27
Senior Member
 
Ramblin's Avatar
 
National RV Owners Club
Workhorse Chassis Owner
Ford Super Duty Owner
Carolina Campers
Join Date: Aug 2011
Posts: 2,266
Quote:
Originally Posted by Clifftall View Post
I have a few ideas of where I'm going to mount it , but don't like any of them. Have you given any thought on how you plan to do it?
Mine's mounted in the electrical bay right where the 50A cable comes in from the pedistal. Just cut it and wired it in, no plugs necessary. I don't have a transfer switch though. *I* am the transfer switch.
__________________
2002 National Dolphin LX 6356
Workhorse W-22 chassis
Don't believe everything you think.
Ramblin is offline   Reply With Quote
Old 03-08-2012, 11:45 AM   #28
Community Administrator
 
CLIFFTALL's Avatar


 
Join Date: Aug 2009
Posts: 53,561
Blog Entries: 1
Quote:
Originally Posted by Hipshot View Post
I don't know yet. I was going to lay it on it's back in front of the water panel just inside the storage compartment door. Don't realy like that location, puts it in direct line of the water connection and as we know want can go wrong will. I have a couple of weeks so I may take another look about where to mount it. Maybe on the right wall near the plug. It depends on how tight the cable will bend. What have you come up with?
Stay tuned for the 5:00 report . I was hopeing you'd bail me out. I will get to the Bounder in a few days and will come up with something.
__________________


Cliff,Tallulah and Buddy ( 1999-2012 )
CLIFFTALL is offline   Reply With Quote
Reply



Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Newmar QUICK TIPS & EASY MODS # 3 -- PLUS OLD COACH's "007" Newmar Owner's Forum 22 03-14-2017 12:38 PM
Can you start coach to re-level while on shore power? Jewelsinmo Winnebago Industries Owner's Forum 18 03-15-2012 07:51 AM
Bob & Sue from Florida Rbocwkbs New Member Check-In 12 03-08-2012 06:10 PM
Ray & Tina, Missouri rayz379 New Member Check-In 9 03-07-2012 12:12 PM
Hello all, and some power questions Mirageags Travel Trailer Discussion 4 03-07-2012 04:41 AM

» Featured Campgrounds

Reviews provided by


All times are GMT -6. The time now is 04:38 AM.


Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.