The national electrical code is said to ban RV autotransformers in the new edition. I will attempt explain autotransformers simply.

Autotransformers have been used in the electrical distribution industry for a very long time. They are used in power distribution, electronics, etc.

They are different from what you think of as conventional transformers as the primary coil is not separate from the secondary. It doesn't isolate the secondary system. The secondary system is not a "separately derived system." They are designed to provide a given boost in voltage.

The typical electrical distribution system is a "radial" distribution system with breakers protecting each feeder and branch circuit. It is a "constant" voltage system (as opposed to constant current systems used by airport runways, christmas light strings, etc). As long as you stay within the current you designed for, the voltage is relatively constant. if more current is drawn than was designed for, then the voltage begins to drop.

in an old RV park that wasn't designed for large rigs, it wasn't designed for the maximum current that will be drawn on a worst case day. Hence the park voltage will begin to reduce. Alternatively if the park is on a rural utility distribution system on a worst case day the utilities power can begin to drop. What is called a "brown-out."

The problem for you is that if your RV is plugged in an the shore power voltage drops, this can adversely affect some of your appliances or equipment. Most electronics can operate at a wide range of voltages. But motors particularly are adversely affected, like your AC units. When the voltage drops the AC unit motors will draw more current to try to operate at the same RPM. This can burn up the motor windings. motor windings have "turn-to-turn" very thin insulation.

An autotransformer can boost low voltage only by a given amount. If the shore power voltage is too low you can still damage your AC unit motors.

The argument against autotransformers is that during a brown-out if everybody reduces their usage/load then everyone will have some power. If everyone has a autotransformer and runs everything hence max load the park power system will draw too much current, then trip out and no one will have power. If only a few people have a autotransformer and draw full power, thus all the current they want, then others in the park will have further reduced voltage.

This an attempt at a simple explanation.
swduns is offline   Reply With Quote
Join the #1 RV Forum Today - It's Totally Free!

iRV2.com RV Community - Are you about to start a new improvement on your RV or need some help with some maintenance? Do you need advice on what products to buy? Or maybe you can give others some advice? No matter where you fit in you'll find that iRV2 is a great community to join. Best of all it's totally FREE!

You are currently viewing our boards as a guest so you have limited access to our community. Please take the time to register and you will gain a lot of great new features including; the ability to participate in discussions, network with other RV owners, see fewer ads, upload photographs, create an RV blog, send private messages and so much, much more!

Old 11-15-2020, 03:27 PM   #2
Senior Member
 
Join Date: Mar 2019
Posts: 251
Good explanation, but it still doesn’t explain why this is a code issue. A system incapable of supplying the needed power is the problem. Implementing code requirements that could never be enforced is not an appropriate action.
Jkwilson1989 is offline   Reply With Quote
Old 11-15-2020, 03:31 PM   #3
Senior Member
 
knightstorm's Avatar
 
Newmar Owners Club
Ford Super Duty Owner
Join Date: Aug 2015
Posts: 1,152
And the Hughes Autoformer is not an autotransformer.
__________________
2017 Newmar Bay Star 3113.

Former owner of a Morgan powered Bennington
knightstorm is offline   Reply With Quote
Old 11-15-2020, 03:32 PM   #4
Senior Member
 
cavie's Avatar
 
Join Date: Jul 2018
Posts: 3,165
Quote:
Originally Posted by Jkwilson1989 View Post
Good explanation, but it still doesn’t explain why this is a code issue. A system incapable of supplying the needed power is the problem. Implementing code requirements that could never be enforced is not an appropriate action.
Click image for larger version

Name:	What he said in that comment up there (1).jpg
Views:	14
Size:	17.1 KB
ID:	308151
__________________
2011 Keystone Sprinter 323 BHS. Port Charlotte Fl/Hinsdale MA. Retired Master Electrician. All Motor homes are RV's. All RV's are not Motor homes.
cavie is offline   Reply With Quote
Old 11-15-2020, 03:44 PM   #5
"Formerly Diplomat Don"
 
Dutch Star Don's Avatar
 
Newmar Owners Club
Join Date: Apr 2005
Location: Moorpark, Ca.
Posts: 18,979
Technically, there is no ban. NFPA says that autoformers shouldn't be used in RV parks, but they're not an enforcement agency. Usually, their decisions on electrical are used in lawsuits. Many members of the NFPA are attorneys trying to secure things that benefit them.

With that said, RV parks don't like autoformers which is fine.....but then they should upgrade their power grid so autoformers aren't needed. Now in some rural areas, the campground is limited because of local City and County infrastructure.
__________________
Don & Mary
2019 Newmar Dutch Star 4018 (Freightliner)
2019 Ford Raptor
Dutch Star Don is online now   Reply With Quote
Old 11-16-2020, 07:31 AM   #6
Senior Member
 
jacwjames's Avatar
 
Monaco Owners Club
Join Date: Jun 2014
Posts: 10,019
Sometimes you have no choice but to use one.


I was staying in an older campground in northern Michigan, I was there for an extended time starting in April (yup, colder then $%!). As the campground started to fill up I started to have problems. Once my wife came in July it started to get hot and she was running 1 AC hooked to a 30 amp circuit. She had dogs and when she got back after a short trip the AC unit had quite because of low voltage. I did not have a surge protector at the time.

After checking voltage, which was extremely low, I complained to the campground owners who blamed it on the utility. Well, I was working on a project that required me to be working with the Electric Utility and had contacts so I made some calls to complain. The informed me that the campground had a known problem and that the line feeding their system was all good.

I had no choice but to buy and Autoformer to maintain decent power to the coach. We used it the whole time we were there through Sept.

This explained why when checking in back in late March the owners said that I couldn't used electric heaters and/or AC (huh???)! I said there was no way I would use the electric heaters when I got there so I offered to pay an additional $100 per month, which they happily accepted but did now explain the reason.
__________________
Jim J
2002 Monaco Windsor 38 PKD Cummins ISC 350 8.3L
2005 Jeep Grand Cherokee w/5.7 Hemi
jacwjames is online now   Reply With Quote
Old 11-16-2020, 09:23 AM   #7
Senior Member
 
Join Date: Mar 2019
Posts: 251
Quote:
Originally Posted by knightstorm View Post
And the Hughes Autoformer is not an autotransformer.
Very true. “Multiple input transformer with automatic ratio selection” is maybe a better term, but autoformer is a cool name!
Jkwilson1989 is offline   Reply With Quote
Old 11-17-2020, 11:49 AM   #8
Registered User
 
Join Date: Oct 2020
Posts: 137
Autotransformer is a marketing term for what are commonly known as line conditioners. I have been using Oneac line conditioners for 40 years and they are designed primarily to stabilize the voltage going to any connected device. They do not change the current draw of amps from anything plugged in downstream, only the supplied voltage.

As electronic devices have become smaller they have become more vulnerable to voltage spikes which line conditioners also suppress with isolated transformers. With low voltage devices can run hotter and with digital devices the logic chips performance can become erratic or fail altogether.

A separate but even more deadly problem is stray voltage on the ground line. Electronic devices are not designed to deal with voltage on the ground connection and this is why some device that can detect this problem, either a tester or a VOM, is important.

Get quotes on replacing the circuit board for a Norcold or the cost of a new TV or a new inverter and the cost for a line conditioner and an outlet tester becomes cheap insurance.

Also the NEC covers buildings and not motor vehicles or trailers. It has been a problem with solar panel and charge converter installations as the codes are nebulous. With the solar panel and inverter installed on my house the only approvals mandated was an inspection by the fire department. This was to confirm that there was an accessible power shutoff switch and room for their people to maneuver on the roof in the event of a fire.

And there is the state of Arizona which has long dragged its feet on adopting NEC codes and still has no statewide electrical code so it can vary county by county and city by city.
Calson is offline   Reply With Quote
Old 11-17-2020, 04:44 PM   #9
Senior Member


 
Join Date: Feb 2020
Location: NY State
Posts: 1,299
Quote:
Originally Posted by Calson View Post
Autotransformer is a marketing term for what are commonly known as line conditioners. <snip>
I think you might have meant "autoformer." "Autotransformer" describes a specific electrical device, one with a single coil (vs. the two in a regular transformer) and a fixed or movable tap. One side of the autotransformer is connected to the ends of the coil, and the other to one end of the coil and the tap.

Good diagram here, but I didn't read the article:

https://en.wikipedia.org/wiki/Autotransformer
__________________
John
1976 Southwind 28', '96 Winnie 34WK,
2006 Tiffin Allegro Bus 40QDP
n2zon is offline   Reply With Quote
Old 11-18-2020, 04:13 AM   #10
Senior Member
 
cavie's Avatar
 
Join Date: Jul 2018
Posts: 3,165
Quote:
Originally Posted by Calson View Post
Autotransformer is a marketing term for what are commonly known as line conditioners. I have been using Oneac line conditioners for 40 years and they are designed primarily to stabilize the voltage going to any connected device. They do not change the current draw of amps from anything plugged in downstream, only the supplied voltage.

As electronic devices have become smaller they have become more vulnerable to voltage spikes which line conditioners also suppress with isolated transformers. With low voltage devices can run hotter and with digital devices the logic chips performance can become erratic or fail altogether.

A separate but even more deadly problem is stray voltage on the ground line. Electronic devices are not designed to deal with voltage on the ground connection and this is why some device that can detect this problem, either a tester or a VOM, is important.

Get quotes on replacing the circuit board for a Norcold or the cost of a new TV or a new inverter and the cost for a line conditioner and an outlet tester becomes cheap insurance.

Also, the NEC covers buildings and not motor vehicles or trailers. It has been a problem with solar panel and charge converter installations as the codes are nebulous. With the solar panel and inverter installed on my house the only approvals mandated was an inspection by the fire department. This was to confirm that there was an accessible power shutoff switch and room for their people to maneuver on the roof in the event of a fire.

And there is the state of Arizona which has long dragged its feet on adopting NEC codes and still has no statewide electrical code so it can vary county by county and city by city.
You need to read up on 2014 NEC 550, 551, 552 and 690 and the manufacturer's sticker on the side of your RV. RV's are covered by the NEC.
__________________
2011 Keystone Sprinter 323 BHS. Port Charlotte Fl/Hinsdale MA. Retired Master Electrician. All Motor homes are RV's. All RV's are not Motor homes.
cavie is offline   Reply With Quote
Old 11-18-2020, 01:15 PM   #11
NXR
Senior Member
 
NXR's Avatar
 
Join Date: Mar 2019
Posts: 3,103
Quote:
Originally Posted by knightstorm View Post
And the Hughes Autoformer is not an autotransformer.
And the so-called National Electrical Code is neither "national" nor a "code". It's guidance produced by the National Fire Protection Association with input from various groups.

Each AHJ ( Authority Having Jurisdiction) such as a county, city, village, whatever, must specifically adopt any updates to the NEC. They actually must also specifically adopt the NEC itself and are free to adopt 100%, free to 100% ignore it, free to adopt sections of it, and free to change any section of it to meet their local needs.

In practice almost no one adopts updates as they come out and many jurisdictions intentionally stay one revision behind because so much local effort is required to vet very change for its local impact. Especially nowadays.

Ray
__________________
2020 Forest River Georgetown GT5 34H5
NXR is offline   Reply With Quote
Old 11-18-2020, 02:05 PM   #12
Senior Member
 
Join Date: Nov 2015
Posts: 19,000
More accurate name would be Voltage Regulator/Booster

Hughes, TRC/Southwire, Power Masters all market Voltage Boosters
(Autoformers, Voltage Controllers, Voltage Boosters)

NFPA publishes 'guidelines/recommendations' which can be made into a law by various governing bodies...RIVA is NOT one

A voltage booster simply converts amps to volts. Since the breaker at the pole regulates the maximum amount of power you are able to draw, it would be impossible to “take” more power than the amount the park allocated to you
Use 'em if you got'em ......damage to your RV electronics/motors will not be covered by the CG
__________________
Is it time for YOUR Medication or Mine?
Dodge 3500 w/Tractor Motor & NUWA 5vr
US NAVY---USS Decatur DDG-31
Old-Biscuit is offline   Reply With Quote
Old 11-18-2020, 02:34 PM   #13
Senior Member
 
Join Date: Jul 2018
Posts: 3,578
Quote:
Originally Posted by Dutch Star Don View Post
Technically, there is no ban. NFPA says that autoformers shouldn't be used in RV parks, but they're not an enforcement agency. Usually, their decisions on electrical are used in lawsuits. Many members of the NFPA are attorneys trying to secure things that benefit them.

With that said, RV parks don't like autoformers which is fine.....but then they should upgrade their power grid so autoformers aren't needed. Now in some rural areas, the campground is limited because of local City and County infrastructure.
I fundamentally disagree. I've attached the Code Panel from the 2017 NEC articles that apply to RVs and RV parks. Not a lawyer on the list.
Attached Thumbnails
Click image for larger version

Name:	NEC 551 panel.jpg
Views:	27
Size:	196.7 KB
ID:	308465  
__________________
2005 Four Winds Majestic 23A
“To the world you may be one person; but to one person you may be the world.” - Dr Suess
Solo_RV_Guy is offline   Reply With Quote
Old 11-18-2020, 09:43 PM   #14
Senior Member
 
Ray,IN's Avatar
 
Join Date: Aug 2001
Location: North America somewhere
Posts: 24,411
Quote:
Originally Posted by NXR View Post
And the so-called National Electrical Code is neither "national" nor a "code". It's guidance produced by the National Fire Protection Association with input from various groups.

Each AHJ ( Authority Having Jurisdiction) such as a county, city, village, whatever, must specifically adopt any updates to the NEC. They actually must also specifically adopt the NEC itself and are free to adopt 100%, free to 100% ignore it, free to adopt sections of it, and free to change any section of it to meet their local needs.

In practice almost no one adopts updates as they come out and many jurisdictions intentionally stay one revision behind because so much local effort is required to vet very change for its local impact. Especially nowadays.

Ray
I agree with old-biscuit.
NFPA recommendations have been adopted as laws by some governmental units.
__________________
2000 Winnebago Ultimate Freedom USQ40JD, ISC 8.3 Cummins 350, Spartan MM Chassis. USA IN 1SG 11B5MX,Infantry retired;Good Sam Life member,FMCA." My fellow Americans, ask not what your country can do for you, ask what you can do for your country. John F. Kennedy
Ray,IN is offline   Reply With Quote
Reply

Tags
electric, electrical



Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Can electrical ever be simple?? 6x16inside Vintage RV's 48 03-15-2018 10:36 PM
TriMark keyless entry - AUTH code vs ACCESS code? Jtrving Newmar Owner's Forum 20 02-20-2018 03:41 PM
Simple question/simple answer JF1957 Allison Transmission Forum 5 10-10-2016 11:54 AM
2 Simple but Unrelated Electrical Questions cekkk RV Systems & Appliances 2 09-12-2015 09:23 PM