Old 08-15-2019, 09:47 AM   #71
Member
 
HORNETD's Avatar
 
Join Date: May 2008
Posts: 77
Quote:
Originally Posted by twinboat View Post
You say that all conductors must be the same gauge, yet this is out there for sale.

Maybe because it is specific to a range ?Attachment 256985
Specific cords which are pre-terminated with plugs and are cut to length are not subject to the no reduction in Equipment Grounding Conductor (EGC) size. Service Cord (Type S) is.
__________________
Tom Horne

HORNETD is offline   Reply With Quote
Join the #1 RV Forum Today - It's Totally Free!

iRV2.com RV Community - Are you about to start a new improvement on your RV or need some help with some maintenance? Do you need advice on what products to buy? Or maybe you can give others some advice? No matter where you fit in you'll find that iRV2 is a great community to join. Best of all it's totally FREE!

You are currently viewing our boards as a guest so you have limited access to our community. Please take the time to register and you will gain a lot of great new features including; the ability to participate in discussions, network with other RV owners, see fewer ads, upload photographs, create an RV blog, send private messages and so much, much more!

Old 08-15-2019, 11:05 AM   #72
Senior Member
 
Join Date: Jul 2014
Posts: 35,446
OK , that makes sense, I suppose.

Fact is, some RVers are using that kind of cord to wire in portable surge protectors, in their compartments.
Quote:
Originally Posted by HORNETD View Post
Specific cords which are pre-terminated with plugs and are cut to length are not subject to the no reduction in Equipment Grounding Conductor (EGC) size. Service Cord (Type S) is.
twinboat is online now   Reply With Quote
Old 08-16-2019, 08:17 AM   #73
Senior Member
 
Join Date: Jul 2018
Posts: 4,925
Quote:
Originally Posted by twinboat View Post
OK , that makes sense, I suppose.

Fact is, some RVers are using that kind of cord to wire in portable surge protectors, in their compartments.

Some folks pick their noses in public, too. That doesn't make it right.


The reduced size of the neutral and equipment grounding conductor in the example is based on the use: the elements of a typical electric range are all 240V, and the neutral exists to derive the 120V needed for the tiny load of control electronics, timers, etc. The ground is there to trip the breaker in the event the neutral is compromised and the smaller conductor still passes sufficient current to trip the overcurrent protection device.


I'll see if I can find the NEC Article that allows this (probably in the 400 series).
__________________
2005 Four Winds Majestic 23A
“To the world you may be one person; but to one person you may be the world.” - Dr Suess
Solo_RV_Guy is offline   Reply With Quote
Old 08-16-2019, 06:34 PM   #74
Senior Member
 
Join Date: Nov 2009
Posts: 324
Quote:
Originally Posted by Solo_RV_Guy View Post
Some folks pick their noses in public, too. That doesn't make it right.


The reduced size of the neutral and equipment grounding conductor in the example is based on the use: the elements of a typical electric range are all 240V, and the neutral exists to derive the 120V needed for the tiny load of control electronics, timers, etc. The ground is there to trip the breaker in the event the neutral is compromised and the smaller conductor still passes sufficient current to trip the overcurrent protection device.


I'll see if I can find the NEC Article that allows this (probably in the 400 series).
You are partially correct, depending on the design of the stove, the neutral is used for more than the lights and controls. Many use 120 volts to the stove top burners to regulate the heat, so on lower heat settings, the burner is supplied with 120 volts to lower the burner output. The selector switch determines how the lines are connected. Usually this can be accomplished by switches that "click" (have definite position switches) while others have varible position (smooth) that incorporate a thermostat to turn the burners off and on. Modern upscale ovens use SCR electronic switches that turns power off and on electronically to pulse the power output, in turn controlling the amount of heat produced. Just installed a commercial deep fryer that uses this technology. Allows for more even heating.
hillbilly3 is offline   Reply With Quote
Old 08-16-2019, 11:40 PM   #75
Member
 
Join Date: Mar 2019
Posts: 35
Quote:
Originally Posted by Mageksl View Post
The circuit I described is indeed a 240v circuit. Inside the RV it is treated and used as two 120v circuits which each need it's own neutral leg. They don't share a neutral. This is why it is important to have an electrician that is familiar with RV requirements do your working.

The main point I was trying to make is that all four wires, red, black, white and green need to be the same size and separately insulated. Look at the wire you use to plug in your 50 amp plug and you will see it indeed has four wires. All the same size, all separately insulated and colored as described above.
This is not correct, a 240v connection is wired with two hot legs and one neutral .
ToppDogg is offline   Reply With Quote
Old 08-17-2019, 04:04 AM   #76
Senior Member
 
Join Date: Jul 2014
Posts: 35,446
If you had read the posts, you would see that the guy your quoting has replied that he stands corrected and now understands.
Quote:
Originally Posted by ToppDogg View Post
This is not correct, a 240v connection is wired with two hot legs and one neutral .
twinboat is online now   Reply With Quote
Old 08-17-2019, 05:37 AM   #77
Senior Member
 
hohenwald48's Avatar
 
Join Date: Jan 2017
Location: Titusville, FL
Posts: 5,164
Nobody ever reads a thread. They just jump in the middle of the conversation. [emoji57]
__________________
When seconds count, the police are only minutes away.
2023 Grand Design 2600RB, 2022 F-350 King Ranch tow vehicle, Titusville, FL when not on the road
hohenwald48 is offline   Reply With Quote
Reply

Tags
electric



Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Question for Electricians Startech RV Systems & Appliances 24 10-05-2018 01:31 PM
Calling All Electricians, Looking 4 Advice 45Auto RV Systems & Appliances 18 06-07-2017 12:11 AM
For you electricians - 30A outlet install questions Steverino iRV2.com General Discussion 35 12-02-2013 09:31 PM
Electricians & Math folk, please check my math on Solar Energy. Branndon Technology: Internet, TV, Satellite, Cell Phones, etc. 16 07-03-2012 06:33 AM
Something for you electricians out there. Spur iRV2.com General Discussion 12 08-27-2007 01:47 AM

» Featured Campgrounds

Reviews provided by


All times are GMT -6. The time now is 05:50 AM.


Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.