IMHO...
Asking a 3 KW genset to start a 15K BTU air conditioner is a lot.
I have a Coleman 3.5 KW genset and it worked "ok" for the 13,500 BTU a/c I had on my old trailer, but every once and a while if it was really hot outside, and the compressor cycled a little too fast (before the head pressure had a chance to drop on the compressor) it would pop the circuit breaker.
Remember, running the a/c is not a big deal. Starting it is the problem, and after the first initial cycle that compressor starts hard.
I think a 4 KW genset would be the minimum for a 15,000 BTU a/c, or like RVhauler said...
Quote:
Originally Posted by RVhauler
Solution was to add a A/C Hard start kit which solved the problem for about $25. (Kit is available from A/C supply houses and is basically a large start capacitor which plugs into the start capactor on the A/C unit. No modifying needed. Instructions included)
|
I am going to look into this idea myself!
__________________
Mark
2004 Montana 3295RK pushing a 2019 Ram Laramie 2500/Cummins truck.
|
|
|
 |
Join the #1 RV Forum Today - It's Totally Free!
iRV2.com RV Community - Are you about to start a new improvement on your RV or need some help with some maintenance? Do you need advice on what products to buy? Or maybe you can give others some advice? No matter where you fit in you'll find that iRV2 is a great community to join. Best of all it's totally FREE!
You are currently viewing our boards as a guest so you have limited access to our community. Please take the time to register and you will gain a lot of great new features including; the ability to participate in discussions, network with other RV owners, see fewer ads, upload photographs, create an RV blog, send private messages and so much, much more!
|
07-06-2010, 11:37 PM
|
#16
|
Junior Member
Join Date: Feb 2010
Posts: 15
|
Thanks Popeye59. My "belief" about not hooking 2 unlike wattage generators was based on my memory of the owner's manuals for my 2 2000i s.
All the ACs I've seen are on a 20amp CB. The CB will tolerate a higher amp draw for a short period. It sounds like some here are talking about the RV CB popping from too high a draw + others about the Gen. CB popping.
Regardless, for $25 the hard start kit should be standard on RV ACs.
Frank
|
|
|
07-07-2010, 04:01 PM
|
#17
|
Junior Member
Join Date: Sep 2009
Posts: 2
|
Hi All,
I figure I'd add my $.02 as well. I've owned an Onan 4kw (in my old MH), Onan 6.5kw (in a box van), and currently own a Honda portable EU3000iSA with an aftermarket remote control kit (used for my cab-over camper).
I can say without out a doubt, the Honda has been the easiest to work on, lowest cost of ownership, quietest generator I have ever owned. I too looked at using an LP Onan to eliminate a 3rd fuel to haul but, after looking at my options and buying / working on Onan generators in the past I was ready to try something different. I've personally watched a Honda EU2000iA run a 12,500 A/C and my 3000 will run the A/C, TV, and microwave all at the same time so, it wouldn't surprise me to see one run a 15,000 BTU A/C. I think Honda is a little conservative on their ratings.
Someone expressed the cost of the Honda. I too looked at cheapie Harbor Freight generators thinking why are the Hondas so much? I can tell you now, QUALITY! Oh, and the price a paid for an Onan starter would have bought 25% of my Honda generator.
If it were me, I'd try the Honda especially since you already own it. No I don't work for Honda I'm just a satisfied customer. Their generators are like their cars and motorcycles, they work, and work good. No more, no less!
FYI the new Honda EU3000i Handi doesn't have electric start if that kind of thing matters to you. It did for me as I wanted to be able to add a remote kit and / or have someone who knows nothing about it be able to start it so I stuck with the big cube shaped EU3000iSA.
I won't ever go back to Onan again but, that's just me. If I had a large rig I probably wouldn't have a choice.
Be sure to let us know how it works,
Todd
|
|
|
07-07-2010, 04:28 PM
|
#18
|
Junior Member
Join Date: Oct 2008
Posts: 9
|
lp generator vrs. honda
stay away from lp gen , they work fine but are about 30 % lest efficient
|
|
|
07-08-2010, 06:18 PM
|
#19
|
Junior Member
Join Date: Jun 2010
Posts: 12
|
Quote:
Originally Posted by RVhauler
Solution was to add a A/C Hard start kit which solved the problem for about $25. (Kit is available from A/C supply houses and is basically a large start capacitor which plugs into the start capactor on the A/C unit. No modifying needed. Instructions included)
|
I appreciate all the feedback and insight. I am leaning toward the concensus here on what to do, and I'll stick with the Honda, at least for now.
Regarding the a/c hard start kit....I am a complete electrical idiot. I can change an outlet and install a light switch (one melted screwdriver in the process  ). I can even change a light bulb, but that's about it. Who would I talk to to make sure I did this right? Would the a/c supplier know about the rv unit? Would my rv dealer know about the hard start kit? Or, will they both look at me like I am nuts??
__________________
2007 Ford F350 Lariat Powerstroke
2011 Silverback 35QB
2004 Honda Shadow Sabre 1100C2
|
|
|
07-27-2010, 07:59 PM
|
#20
|
Junior Member
Join Date: Jun 2010
Posts: 12
|
OK, so the new unit came in, and there is now no question that a 3KW Honda will NOT start the 15K BTU a/c. I had no other appliances running during the attempt. I'm looking into the hard start kit, and am debating on selling the 3KW and buying two 2KW, or adding another 3KW (expensive, but gives me a full 50 amps of power). Thanks again for all the advice!
__________________
2007 Ford F350 Lariat Powerstroke
2011 Silverback 35QB
2004 Honda Shadow Sabre 1100C2
|
|
|
07-28-2010, 06:22 PM
|
#21
|
Junior Member
Join Date: Sep 2009
Posts: 2
|
Wow, I'm shocked and sorry to hear that. Did you ensure that the Eco-Throttle switch on the front panel is in the "off" position when trying to start the A/C? Keep us in the loop on the hard start kit.
|
|
|
07-28-2010, 07:11 PM
|
#22
|
Junior Member
Join Date: Jun 2010
Posts: 12
|
Quote:
Originally Posted by Desertlife
Wow, I'm shocked and sorry to hear that. Did you ensure that the Eco-Throttle switch on the front panel is in the "off" position when trying to start the A/C? Keep us in the loop on the hard start kit.
|
Yeah, I had that off  . Nothing else was drawing power except the LP detector and whatever battery charge inherently takes place. I realized last night I did not get a manual on my a/c unit, so I don't even know the brand let alone the specs on what it draws on startup. I called the dealer for a copy. I'm climbing up over the weekend to pull the a/c cover off and figure out what I need to buy.
__________________
2007 Ford F350 Lariat Powerstroke
2011 Silverback 35QB
2004 Honda Shadow Sabre 1100C2
|
|
|
08-01-2010, 04:31 PM
|
#23
|
Senior Member
Join Date: Apr 2010
Location: Full Timer / Vagabond
Posts: 609
|
Most of the newer A/C units have a time delay on the compressor starts. It gives the refrigerant time to equalize so the compressor does not start against high pressure. It is part of the energy efficiency requirements. A hard start kit is a good idea. One never knows which CG has bad power and it will help save a unit. My fan starts before the compressor starts. That helps to lower the initial power draw. It came that way.
__________________
Ralph & Snickers
2006 3500 Chevy Dually - 8.1 - Allison
2006 30' New Horizon - Solar
|
|
|
 |
|
Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
|
|
Thread Tools |
Search this Thread |
|
|
Display Modes |
Linear Mode
|
Posting Rules
|
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts
HTML code is Off
|
|
|
|
» Recent Discussions |
|
|
|
|
|
|
|
|
|
|
|
|
|