Old 11-25-2020, 06:43 PM   #1
Junior Member
 
Join Date: Oct 2020
Posts: 16
Inverter pops GFCI when genset is plugged in

I have a Winnebago Outlook where the shore power cable plugs into the generator receptacle when not in use. Everything works as it should. Shore power / generator power runs through an automatic transfer switch that connects/disconnects both, hot and neutral. My new inverter (Renogy, 2 KW) has a built in GFCI that pops when the shore power cable is plugged into the generator receptacle (generator NOT running), it works fine when the generator cable is not plugged in.

Somewhere .. something is not right. Where should I start to investigate?

Thanks for your help.
mischmerz is offline   Reply With Quote
Join the #1 RV Forum Today - It's Totally Free!

iRV2.com RV Community - Are you about to start a new improvement on your RV or need some help with some maintenance? Do you need advice on what products to buy? Or maybe you can give others some advice? No matter where you fit in you'll find that iRV2 is a great community to join. Best of all it's totally FREE!

You are currently viewing our boards as a guest so you have limited access to our community. Please take the time to register and you will gain a lot of great new features including; the ability to participate in discussions, network with other RV owners, see fewer ads, upload photographs, create an RV blog, send private messages and so much, much more!

Old 11-26-2020, 09:29 AM   #2
Senior Member
 
Monaco Owners Club
Join Date: Sep 2014
Posts: 3,836
If you have a transfer switch it seems odd that you would ever "plug your shore power cable" into the gen. Try not doing that maybe. A schematic might help me better understand though.
__________________
1996 Tioga Class C
400 amp/hrs solar, Trimetric

2007 Monaco Diplomat 40 PDQ
okcnewbie is offline   Reply With Quote
Old 11-26-2020, 09:51 AM   #3
Senior Member
 
Join Date: Nov 2018
Location: Beaver Dam, Wisconsin
Posts: 1,737
GFI or Circuit Breaker

Circuit breakers trip when there is too much current.
GFI (Ground Fault Interrupter) trip when there is a "Ground Fault".

Assuming your GFI trips (not circuit breaker) and you have a transfer switch, you should not plug the shore power cord into the generator outlet. The transfer switch takes care of switching from shore to gen.

Some RV's do not have transfer switches. Plugging the shore power cord into the generator is how power source is switched.

When on shore power, your TT 120 volt system ground should not be grounded to the frame ground.

When using a generator, the system ground should be grounded to the frame.

The transfer switch takes care of connecting the frame ground. Not letting this happen can cause a Ground Fault Interrupter to trip.

I wish you good luck and happy trails ahead!
__________________
Paul Bristol
Kodiak Cub 176RD
Nissan Pathfinder 2015
Persistent is offline   Reply With Quote
Old 11-26-2020, 09:55 AM   #4
Senior Member
 
Join Date: Nov 2018
Location: Beaver Dam, Wisconsin
Posts: 1,737
Please post year, make, and model of your RV in your profile and possibly add it to you signature line. Help given is likely to be more accurate then.

Posting make and model of appliances like a transfer switch when asking questions about them is also much more useful.
__________________
Paul Bristol
Kodiak Cub 176RD
Nissan Pathfinder 2015
Persistent is offline   Reply With Quote
Old 11-26-2020, 10:35 AM   #5
Moderator Emeritus
 
Gary RVRoamer's Avatar


 
Join Date: Jan 2000
Location: Silver Springs, FL. USA
Posts: 23,605
You would not have to plug the shore cord into a genset receptacle if it has an auto-transfer switch, so either you are misunderstanding your equipment or using it wrong. Please take another look at your system, cause it probably does not have an auto-transfer switch.



The GFCI (Ground Fault) trip indicates that the genset wire polarity is different than the inverter. Possibly neutral or hot are reversed in one or the other.
__________________
Gary Brinck
Former owner of 2004 American Tradition and several other RVs
Home is in the Ocala Nat'l Forest near Ocala, FL
Summers in Black Mountain, NC
Gary RVRoamer is offline   Reply With Quote
Old 11-26-2020, 12:26 PM   #6
Member
 
Join Date: Mar 2019
Posts: 88
Likely the neutral is being connected to ground when plugged into the generator. That is a second thing that will cause a GFCI to trip.
Jkwilson1989 is offline   Reply With Quote
Old 11-26-2020, 02:59 PM   #7
Senior Member
 
153stars's Avatar
 
Join Date: Mar 2019
Location: Braidwood Il.
Posts: 2,221
What above post said....
Look for neutral and ground bonded on RV breaker panel. It really should not be because RV panel is classified a distribution panel if and when its plugged in to an outside AC panel.But many have found them bonded. Look for all Neutrals to neutral bar grounds to the ground bar and no jumper joing them.
__________________
95 Monaco Crown Royale
M11 400hp, 4060 trans.
Aquahot, Generac Guardian7.5k
153stars is online now   Reply With Quote
Old 11-26-2020, 03:33 PM   #8
Senior Member
 
Join Date: Jul 2014
Posts: 25,575
The RV breaker panel should not be, and probably is not bonded ( ground and neutral tied together ), but the generator will be, since it becomes the source of power.

If your inverter GFCI is tripping, you have something back feeding. There should be no connection to your shore cord.

Send us some info on your equipment and a sketch of how you wired it in.
twinboat is offline   Reply With Quote
Old 11-27-2020, 07:44 AM   #9
Junior Member
 
Join Date: Oct 2020
Posts: 16
Thanks for you answers. We are talking about a 2008 Winnebago Outlook. The shore power cable is used for both, shore power and generator. When not connected to shore power, the cable is plugged into the generator outlet.

The motor home was not originally equipped with an inverter. I added a transfer switch (Go Power) to switch from shore power / generator to inverter. If the shore power cable is plugged into the generator outlet, the inverter will complain with a GFCI error. When the shore power cable is NOT plugged in, everything works fine.


As I understand it, the inverter is internally bonded. The generator is probably too. What puzzles me is the fact that the transfer switch disconnects both, the hot and the neutral, so it should break the generators bond.

But it obviously doesn't.


Michaela
Attached Thumbnails
Click image for larger version

Name:	transfer_switch.jpg
Views:	6
Size:	12.7 KB
ID:	309461  
mischmerz is offline   Reply With Quote
Old 11-27-2020, 07:56 AM   #10
Senior Member
 
egwilly's Avatar
 
Outdoors RV Owners Club
Join Date: Jul 2012
Location: So Calif
Posts: 2,849
Please take some time to read about ground-neutral bonding at the no shock zone. Rv's are different than houses in regards to grounds.

This guy knows his stuff and has helped me in the past.

Generator Ground-Neutral Bonding - No~Shock~Zone

http://noshockzone.org/rv-electrical...oubleshooting/
__________________
Outdoors RV Glacier Peak 26RLS Fifth Wheel
Ford F350 Superduty 6.7 Powerstroke
“Stick around please...I may need someone to blame.”
egwilly is offline   Reply With Quote
Old 11-27-2020, 08:13 AM   #11
Senior Member
 
Join Date: Oct 2014
Posts: 1,512
Quote:
Originally Posted by mischmerz View Post
Thanks for you answers. We are talking about a 2008 Winnebago Outlook. The shore power cable is used for both, shore power and generator. When not connected to shore power, the cable is plugged into the generator outlet.

The motor home was not originally equipped with an inverter. I added a transfer switch (Go Power) to switch from shore power / generator to inverter. If the shore power cable is plugged into the generator outlet, the inverter will complain with a GFCI error. When the shore power cable is NOT plugged in, everything works fine.


As I understand it, the inverter is internally bonded. The generator is probably too. What puzzles me is the fact that the transfer switch disconnects both, the hot and the neutral, so it should break the generators bond.

But it obviously doesn't.


Michaela

That is a somewhat unusual use of an ATS which will account for many of our posts. Normally ATS's select between SHORE POWER and GENERATOR only. In this standard configuration, one does not change plugs based on source-- it is hardwired and automatic.



And part of your ATS's function (to select inverter) is more usually handled inside the inverter/charger (one unit, not two separate ones) by an internal ATS which selects and "passes through" 120 VAC when it receives it from either shore power or generator.
__________________
Brett Wolfe
Ex: 2003 Alpine 38FDDS. Ex: 1997 Safari Sahara. Ex: 1993 Foretravel U240
wolfe10 is offline   Reply With Quote
Old 11-27-2020, 10:15 AM   #12
Junior Member
 
Join Date: Oct 2020
Posts: 16
Not every inverter is able to sense line voltage and disconnect accordingly. I don't even know if my Renogy inverter would do that. This is why IMHO an ATS is much safer. The other reason for an ATS is simply to disconnect the charger if running on inverter. You wouldn't want to charge your batteries while you are powering the inverter from your batteries.


Edit: If have two different units: A converter/charger and an inverter.



In other words: An ATS has it's place in a setup like mine.
mischmerz is offline   Reply With Quote
Old 11-27-2020, 11:04 AM   #13
Senior Member
 
Join Date: Jul 2014
Posts: 25,575
I have basicly the same setup. I added a standard RV 30 amp ATS to switch some circuits between shore/generator OR inverter power.

I set it up that the shore / generator power goes to the generator input of the new ATS. That way, anytime 120 volts is there is it powers thru. ( Generator is priority on ATS s ).

When there is no shore/gen power, the ATS defaults to the inverter and powers the circuit.

If yours isn't wired that way, basicly inputs backwards, try it. May fix the issue.
twinboat is offline   Reply With Quote
Old 11-27-2020, 11:08 AM   #14
Junior Member
 
Join Date: Oct 2020
Posts: 16
I think I need to explain a bit more in detail. The inverter runs the motor home just fine. A line tester says everything is ok, the inverter's GFCI does not trip.


The inverter is internally bonded.


When I turn off the inverter and start the generator, power is supplied and everything works fine too. The line tester is still happy.



As I mentioned before - the generator has a dedicated outlet in a compartment and that's where one is supposed to plugin the shore power cable when not on shore power.


When the generator is NOT running, an automatic transfer switch disconnects the live and the neutral wire, ground however remains connected.


When I plug in the shore power into the generator outlet, the inverter's GFCI trips. In other words: By connecting the ground to the generator, I create a fault even though neutral and live are disconnected via transfer switch.



This doesn't make sense and it confuses the hell out of me.
mischmerz is offline   Reply With Quote
Reply

Tags
inverter



Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
No AC to GFCI outlet string, but GFCI is good Eric1959 RV Systems & Appliances 12 03-21-2019 09:38 PM
Bounder: 2016 Bounder 33C - GFCI keeps tripping (Internal to RV, not house GFCI) nehmia Fleetwood Owner's Forum 8 10-22-2016 08:34 AM
GFCI pops twdickson Monaco Owner's Forum 6 03-26-2011 11:45 AM
Heart Freedom 15 Inverter pops input circuit breaker. JB Texas MH-General Discussions & Problems 11 05-04-2005 09:53 AM


All times are GMT -6. The time now is 06:48 PM.


Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2021, vBulletin Solutions, Inc.