Old 09-06-2021, 11:10 AM   #15
Senior Member
 
Join Date: Oct 2014
Posts: 7,870
Yes, the only (minuscule) risk with plugging a 30 amp coach into 50 amp outlet is "before" the 30 amp main breaker in the coach.


And, only a dead short before your coach main breaker box could cause anything in access of 30 amps.


A very small risk that most of us have safely assumed for decades.


Guess it is kind of like the risk of driving with your propane refrigerator on, generator running, etc. A risk most of us find acceptable.
__________________
Brett Wolfe
Ex: 2003 Alpine 38FDDS. Ex: 1997 Safari Sahara. Ex: 1993 Foretravel U240
wolfe10 is offline   Reply With Quote
Join the #1 RV Forum Today - It's Totally Free!

iRV2.com RV Community - Are you about to start a new improvement on your RV or need some help with some maintenance? Do you need advice on what products to buy? Or maybe you can give others some advice? No matter where you fit in you'll find that iRV2 is a great community to join. Best of all it's totally FREE!

You are currently viewing our boards as a guest so you have limited access to our community. Please take the time to register and you will gain a lot of great new features including; the ability to participate in discussions, network with other RV owners, see fewer ads, upload photographs, create an RV blog, send private messages and so much, much more!

Old 09-06-2021, 12:05 PM   #16
PB2
Member
 
PB2's Avatar
 
Join Date: Jul 2021
Location: Michigan
Posts: 56
I confirmed i have a 30a main breaker in my panel. This is the surge protector i have...


https://www.amazon.com/gp/product/B0...?ie=UTF8&psc=1



I'll probably pick up a 50a to 30a dog bone, but not in a hurry to do so as it seems there are not many instances of 50a being the only option.


Thanks for the good discussion!
__________________
2016 Big Country 4010RD
PB2 is offline   Reply With Quote
Old 09-06-2021, 12:18 PM   #17
Senior Member
 
Old-Biscuit's Avatar
 
Join Date: Nov 2015
Posts: 26,689
Get the 50A to 30A Adapter.......
Many times the 30A power pedestal receptacle is worn out and the 50A can then be used

RV 30A Main CB protects the RV
50A CB at pedestal would trip if shore power cord/adapter shorted
*Same if connected to 30A pedestal


Where do you put the water pressure regulator?
At spigot or side of RV
__________________
I took my Medication today. HAVE YOU?
Dodge 3500 w/Tractor Motor
US NAVY---USS Decatur DDG-31
Old-Biscuit is offline   Reply With Quote
Old 09-06-2021, 05:59 PM   #18
Member
 
Winnebago Owners Club
Join Date: May 2021
Posts: 98
Quote:
Originally Posted by The Brews Cruise View Post
As a retired electrician, I wouldn't call connecting a 30 amp coach to a 50 amp circuit "safe". It can be done with a "dogbone" adapter. The problem I see is that your cord and internal wiring to your panel is sized for 30 amps, but the 50 amp overcurrent protection will not protect the wiring for overload. An overload condition could possibly allow 40 to 50 amps to flow on the smaller size wiring, causing it to overheat. If you had a way to have 30 amp protection connected to the 50 amp at the power post, then your wiring would be properly protected.
I'm sure that many people carry the adapters to connect their 30 amp coach to the 50 amp circuit, and they have had no problems...yet. You're going to get conflicting advice on this, and I'm sure there are plenty that disagree with me. With 47 years active in the electrical trade prior to retirement I've seen enough to know that it's not something I would do.
True to a point, Also a sparky here. Its never a good idea to connect a 30 amp device to a 50 amp feed however most RV including ours included have a main breaker that is matched to cord rating. The main breaker in the RV (30amp in this example) is protecting the RV while the feeder breaker (50Amp in this example) is protecting the supply cord.
Sparky19053 is offline   Reply With Quote
Old 09-07-2021, 12:21 AM   #19
Senior Member
 
Isaac-1's Avatar
 
Join Date: Jun 2016
Location: SW Louisiana
Posts: 8,849
I have almost never seen a site with a 50 amp outlet and no 30 amp (maybe once or twice), however what I have seen fairly often is a site with a 50 amp outlet and a damaged, loose, or missing 30 amp outlet.
__________________
2002 Safari Trek 2830 on P32 Chassis with 8.1L w/ 400 watts solar 420Ah LiFePo4
2017 Jeep Cherokee Overland & 2007 Toyota Yaris TOADs with Even Brake,
Demco Commander tow bar and Blue Ox / Roadmaster base plates
Isaac-1 is offline   Reply With Quote
Old 09-07-2021, 12:57 AM   #20
Member
 
Join Date: Jul 2019
Posts: 91
Quote:
Originally Posted by Podivin View Post
Seems to me that's what the 30 amp main breaker in the RV is for. The RV isn't going to pull more than 30 amps, if it tries to it will trip the main.
Wouldn't the concern would be between the RV 30 amp main breaker and the pedestal 50 amp breaker? The shore power cord and NEMA L5-30R plug are only rated for 30 amps. If you had a short between the 2 breakers or low voltage condition you could put 50 amps in a 30 amp cord/plug before the 30 amp RV breaker would trip.
__________________
2021 Renegade Verona LE 38LDG
2019 Silverado 2500 HD Duramax
Blue Ox Apollo 15K-M&G Original braking system
emdoc is offline   Reply With Quote
Old 09-07-2021, 06:33 AM   #21
Senior Member
 
Join Date: Jul 2014
Posts: 35,349
Quote:
Originally Posted by emdoc View Post
Wouldn't the concern would be between the RV 30 amp main breaker and the pedestal 50 amp breaker? The shore power cord and NEMA L5-30R plug are only rated for 30 amps. If you had a short between the 2 breakers or low voltage condition you could put 50 amps in a 30 amp cord/plug before the 30 amp RV breaker would trip.
Its rated for 30 amps, that don't mean it can't handle 50 amps long enough to trip the breaker.

Low voltage will trip the RV breaker, that's where the combined amp draw will be adding up. There is no one 30 amp item in the RV.
twinboat is offline   Reply With Quote
Old 09-07-2021, 09:58 AM   #22
Senior Member
 
Join Date: Apr 2017
Location: Ga
Posts: 402
Ok just my 2 cents worth.
I'm assuming camper feeder cable is #10 AWG (30A) which is rated up to 40 amps depending on insulation, although NEC says must be fused at no more than 30A. Hypothetical situation, cord gets damaged but not enough for a dead short, pulls ~49A could get hot enough to catch fire and RV way before it ever trips breaker.
Just food for thought with a lot of IFs.
Maintenance electrician 30+ yrs. Sean electricity do some strange things.
__________________
2013 Ram 1500 Laramie
2002 R-Vision Trail-Lite 8261 (no longer under construction . Anyone need parts? )
ratherberv is offline   Reply With Quote
Old 09-07-2021, 10:19 AM   #23
Senior Member
 
The Brews Cruise's Avatar
 
Newmar Owners Club
Coastal Campers
Freightliner Owners Club
Join Date: Jan 2017
Location: Tampa, Florida
Posts: 737
Quote:
Originally Posted by PB2 View Post
Really good advice - thanks! I have a 30a surge protector with EMS. Does that offer me some level of protection if i plug into 50a service?


Thanks all for the comments. I think having one in the kit will be a good idea.
Only if it has 30 amp overcurrent protection (30 amp breaker) built in.
__________________
Ken & Ara Brewer
2020 Newmar Ventana 3407 DP. (Previous 2016 Newmar Canyon Star 3710 gasser). 2014 V-6 Chevy Equinox Toad.
The Brews Cruise is offline   Reply With Quote
Old 09-07-2021, 10:36 AM   #24
Senior Member
 
Old-Biscuit's Avatar
 
Join Date: Nov 2015
Posts: 26,689
Quote:
Originally Posted by ratherberv View Post
Ok just my 2 cents worth.
I'm assuming camper feeder cable is #10 AWG (30A) which is rated up to 40 amps depending on insulation, although NEC says must be fused at no more than 30A. Hypothetical situation, cord gets damaged but not enough for a dead short, pulls ~49A could get hot enough to catch fire and RV way before it ever trips breaker.
Just food for thought with a lot of IFs.
Maintenance electrician 30+ yrs. Sean electricity do some strange things.
RV 30A CB will trip if more then 30A is on circuit
50A Pedestal CB would trip if short occurred on circuit to RV otherwise the RV 30A CB controls total amps pulled

Other then direct short...30A total
__________________
I took my Medication today. HAVE YOU?
Dodge 3500 w/Tractor Motor
US NAVY---USS Decatur DDG-31
Old-Biscuit is offline   Reply With Quote
Old 09-07-2021, 11:16 AM   #25
Moderator Emeritus
 
Gary RVRoamer's Avatar


 
Join Date: Jan 2000
Location: West Palm Beach, FL. USA
Posts: 27,563
LOL! The sparkies can surely prove that there is some situation where a safety problem is conceivable. The question is how much risk & how likely? It's also risky to plug a 1A table lamp into a 15A outlet in your living room, and that lamp doesn't even have a breaker of its own. But we do it without a thought.

This is like the risk of crossing a street on foot - you take steps to minimize risk but it's never going to be 100% risk free.
__________________
Gary Brinck
Former owner of 2004 American Tradition and several other RVs
Home is West Palm Beach, FL
Gary RVRoamer is offline   Reply With Quote
Old 09-07-2021, 12:12 PM   #26
Senior Member
 
Alan_Hepburn's Avatar


 
Fleetwood Owners Club
Workhorse Chassis Owner
Join Date: Feb 2000
Location: San Jose, Ca, USA
Posts: 2,693
Quote:
Originally Posted by Mrueth View Post
Its never a good idea to connect a 30 amp device to a 50 amp feed
It's really no different from plugging a 2 amp appliance into a 15 amp outlet in your home...
__________________
Alan Hepburn - San Jose, Ca
2007 Bounder 35E being pushed by a 2020 Jeep Gladiator Sport S or a 2022 Jeep Wrangler Unlimited (JLU) Sport S
Alan_Hepburn is offline   Reply With Quote
Old 09-07-2021, 12:18 PM   #27
Senior Member
 
Old-Biscuit's Avatar
 
Join Date: Nov 2015
Posts: 26,689
Quote:
Originally Posted by Alan_Hepburn View Post
It's really no different from plugging a 2 amp appliance into a 15 amp outlet in your home...
You failed to post the full statement.....
True to a point, Also a sparky here. Its never a good idea to connect a 30 amp device to a 50 amp feed however most RV including ours included have a main breaker that is matched to cord rating. The main breaker in the RV (30amp in this example) is protecting the RV while the feeder breaker (50Amp in this example) is protecting the supply cord.
__________________
I took my Medication today. HAVE YOU?
Dodge 3500 w/Tractor Motor
US NAVY---USS Decatur DDG-31
Old-Biscuit is offline   Reply With Quote
Reply

Tags
electric, electrical, newbie



Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Newbie electrical question taylormclam RV Systems & Appliances 27 09-06-2016 11:35 AM
Newbie electrical question rjasutton Class C Motorhome Discussions 8 04-27-2016 01:54 PM
Ultra-newbie electrical question Pgustaf249 RV Systems & Appliances 6 07-17-2014 05:38 AM
Newbie Question About Power Inverters and Electrical exploring RV Systems & Appliances 11 01-05-2014 03:18 PM
Newbie to forum, newbie to rv'ing, and I have a newbie problem last_lemming Class B Motorhome Discussions 36 09-06-2012 06:14 PM

» Featured Campgrounds

Reviews provided by


All times are GMT -6. The time now is 11:51 AM.


Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.