Newbie electrical question

Our rig is a 30a coach. I understand i can safely plug into a 50a plug with the proper adapter/dog bone. My question is how often do you encounter campsites with only 50a service? I don't have the dog bone and wonder how often i would need one...


Thanks!
__________________
2016 Big Country 4010RD
PB2 is offline   Reply With Quote
Join the #1 RV Forum Today - It's Totally Free!

iRV2.com RV Community - Are you about to start a new improvement on your RV or need some help with some maintenance? Do you need advice on what products to buy? Or maybe you can give others some advice? No matter where you fit in you'll find that iRV2 is a great community to join. Best of all it's totally FREE!

You are currently viewing our boards as a guest so you have limited access to our community. Please take the time to register and you will gain a lot of great new features including; the ability to participate in discussions, network with other RV owners, see fewer ads, upload photographs, create an RV blog, send private messages and so much, much more!

Old 09-06-2021, 06:59 AM   #2
Senior Member
 
Join Date: Jul 2017
Posts: 1,343
It's always the other way for me I find. No 50amp just 30amp.
__________________
98 Monaco Windsor
2015 Rubicon Toad
Craig1960 is offline   Reply With Quote
Old 09-06-2021, 07:09 AM   #3
Senior Member
 
The Brews Cruise's Avatar
 
Newmar Owners Club
Coastal Campers
Freightliner Owners Club
Join Date: Jan 2017
Location: Tampa, Florida
Posts: 737
As a retired electrician, I wouldn't call connecting a 30 amp coach to a 50 amp circuit "safe". It can be done with a "dogbone" adapter. The problem I see is that your cord and internal wiring to your panel is sized for 30 amps, but the 50 amp overcurrent protection will not protect the wiring for overload. An overload condition could possibly allow 40 to 50 amps to flow on the smaller size wiring, causing it to overheat. If you had a way to have 30 amp protection connected to the 50 amp at the power post, then your wiring would be properly protected.
I'm sure that many people carry the adapters to connect their 30 amp coach to the 50 amp circuit, and they have had no problems...yet. You're going to get conflicting advice on this, and I'm sure there are plenty that disagree with me. With 47 years active in the electrical trade prior to retirement I've seen enough to know that it's not something I would do.
__________________
Ken & Ara Brewer
2020 Newmar Ventana 3407 DP. (Previous 2016 Newmar Canyon Star 3710 gasser). 2014 V-6 Chevy Equinox Toad.
The Brews Cruise is offline   Reply With Quote
Old 09-06-2021, 07:13 AM   #4
Epp
Senior Member
 
Join Date: Aug 2020
Posts: 142
It only takes one time and you will need it. LOL.
On our last trip we stayed on site at a car show being held at an older airport. Where I had to park the rig my 50 amp cord would not reach the power box. So I used a 50 to 30 adapter and ran my 30 amp cord over to the power box only to discover the power box only had a 50 amp and 20 amp connection. I carry every adapter known to mankind except for 30 to 50. I have one of these now. So yes some places do only have 50 amp outlets, the adapters really don’t take up that much space for the convenience of not having to run out to the store to pick up an adapter when you’re setting up camp.

The post above brings up a good point about whether or not you have a 30 amp breaker installed in your rv breaker box to prevent an overload. This was not a factor in the example I gave for my particular situation.

Epp
__________________
Thescoutranch
2001 Newmar DSDP/Spartan Chassis/Cummins ISC
Epp is offline   Reply With Quote
Old 09-06-2021, 07:13 AM   #5
Community Moderator


 
Join Date: Aug 2018
Location: Full timing
Posts: 6,345
Quote:
Originally Posted by PB2 View Post
Our rig is a 30a coach. I understand i can safely plug into a 50a plug with the proper adapter/dog bone. My question is how often do you encounter campsites with only 50a service? I don't have the dog bone and wonder how often i would need one...


Thanks!
We are going to a Famcamp in Mayport, Osprey Cove, it only has 50 amp.
But when we run into a situation like you are asking, it is only 30 amp, 50 amp not available. Some times we run across this in some Thousand Trails parks.
Carry a dog bone with you so you will be prepared.
__________________
2018 Road Warrior 427
2013 Can Am Spyder RT Limited
2017 Ram 3500 w/Aisin w/4:10
2 Dachshunds DJ (RIP 9-12-19) & Joey (RIP 5-14-21)
hamm2018 is offline   Reply With Quote
Old 09-06-2021, 07:15 AM   #6
Community Administrator
 
CLIFFTALL's Avatar


 
Join Date: Aug 2009
Posts: 53,561
Blog Entries: 1
This will depend on how often you camp and where. It only takes one time to realize it’s a good investment. I wouldn’t leave home without it when I had a 30 amp RV and conversely a 50 to 30 when I had a 50 amp RV.
Quote:
Originally Posted by PB2 View Post
Our rig is a 30a coach. I understand i can safely plug into a 50a plug with the proper adapter/dog bone. My question is how often do you encounter campsites with only 50a service? I don't have the dog bone and wonder how often i would need one...


Thanks!
__________________


Cliff,Tallulah and Buddy ( 1999-2012 )
CLIFFTALL is offline   Reply With Quote
Old 09-06-2021, 07:34 AM   #7
PB2
Member
 
PB2's Avatar
 
Join Date: Jul 2021
Location: Michigan
Posts: 56
Quote:
Originally Posted by The Brews Cruise View Post
As a retired electrician, I wouldn't call connecting a 30 amp coach to a 50 amp circuit "safe". It can be done with a "dogbone" adapter. The problem I see is that your cord and internal wiring to your panel is sized for 30 amps, but the 50 amp overcurrent protection will not protect the wiring for overload. An overload condition could possibly allow 40 to 50 amps to flow on the smaller size wiring, causing it to overheat. If you had a way to have 30 amp protection connected to the 50 amp at the power post, then your wiring would be properly protected.
I'm sure that many people carry the adapters to connect their 30 amp coach to the 50 amp circuit, and they have had no problems...yet. You're going to get conflicting advice on this, and I'm sure there are plenty that disagree with me. With 47 years active in the electrical trade prior to retirement I've seen enough to know that it's not something I would do.

Really good advice - thanks! I have a 30a surge protector with EMS. Does that offer me some level of protection if i plug into 50a service?


Thanks all for the comments. I think having one in the kit will be a good idea.
__________________
2016 Big Country 4010RD
PB2 is offline   Reply With Quote
Old 09-06-2021, 07:48 AM   #8
Senior Member
 
Join Date: Sep 2009
Location: Central Indiana
Posts: 1,422
Quote:
Originally Posted by PB2 View Post
Really good advice - thanks! I have a 30a surge protector with EMS. Does that offer me some level of protection if i plug into 50a service?


Thanks all for the comments. I think having one in the kit will be a good idea.


Not knowing which EMS you have, I suggest that you check the specifications to see if it has over current protection. I doubt that it does. One could make their own 50 to 30 adapter with a 30 amp breaker in the line. If you dont know how, please don’t try it.
mrboyer is offline   Reply With Quote
Old 09-06-2021, 07:53 AM   #9
Senior Member
 
Join Date: Aug 2016
Location: Payson, AZ
Posts: 1,282
Quote:
Originally Posted by PB2 View Post
Really good advice - thanks! I have a 30a surge protector with EMS. Does that offer me some level of protection if i plug into 50a service?


Thanks all for the comments. I think having one in the kit will be a good idea.
the EMS will provide over / under voltage protection. it will not provide overload protection. that is the job of the circuit breakers on the pedestal and the main breaker in you distribution panel.
bigchick is offline   Reply With Quote
Old 09-06-2021, 08:11 AM   #10
Senior Member
 
Join Date: Jul 2014
Posts: 35,446
Quote:
Originally Posted by The Brews Cruise View Post
As a retired electrician, I wouldn't call connecting a 30 amp coach to a 50 amp circuit "safe". It can be done with a "dogbone" adapter. The problem I see is that your cord and internal wiring to your panel is sized for 30 amps, but the 50 amp overcurrent protection will not protect the wiring for overload. An overload condition could possibly allow 40 to 50 amps to flow on the smaller size wiring, causing it to overheat. If you had a way to have 30 amp protection connected to the 50 amp at the power post, then your wiring would be properly protected.
I'm sure that many people carry the adapters to connect their 30 amp coach to the 50 amp circuit, and they have had no problems...yet. You're going to get conflicting advice on this, and I'm sure there are plenty that disagree with me. With 47 years active in the electrical trade prior to retirement I've seen enough to know that it's not something I would do.
You are only carrying a 50 amp potential thru the power cord, ATS, and short wire to the 30 amp main breaker.
Any overload beyond that will trip the 30 amp main breaker.

I mentioned 50 amp potential because you will probably need a dead short to draw over 30 amps.

Its no different then plugging a lamp, with 16 gauge wire, into a 20 amp outlet. You just can't put a big enough bulb in to trip the breaker.
Cut the cord and connect the wires together and it will probably trip the breaker.
twinboat is offline   Reply With Quote
Old 09-06-2021, 09:00 AM   #11
Senior Member/RVM #90
 
MSHappyCampers's Avatar


 
Monaco Owners Club
Join Date: Nov 2002
Location: Columbus, MS
Posts: 54,794
I've never seen a campground with 50A service that didn't also have a 30A outlet on the same post.

The dogbones aren't expensive, so I would have one, just in case!
__________________
Joe & Annette
Sometimes I sits and thinks, sometimes I just sits.....
2002 Monaco Windsor 40PBT, 2013 Honda CRV AWD
MSHappyCampers is offline   Reply With Quote
Old 09-06-2021, 09:18 AM   #12
Senior Member
 
Join Date: Jun 2016
Location: De
Posts: 494
Get the dog bone, 30 amp rig pulled in next to us an the park pedestal had the normal 50 30 20 amp plugs but the 30 amp receptacle was broken and unusable, they called, campground maintenance, they showed up checked it out and gave them a 50 to 30 amp dog bone to use until it could be fixed.
Wrapped is offline   Reply With Quote
Old 09-06-2021, 10:54 AM   #13
Senior Member
 
Join Date: Mar 2021
Location: Northern California
Posts: 1,285
Quote:
Originally Posted by The Brews Cruise View Post
As a retired electrician, I wouldn't call connecting a 30 amp coach to a 50 amp circuit "safe". It can be done with a "dogbone" adapter. The problem I see is that your cord and internal wiring to your panel is sized for 30 amps, but the 50 amp overcurrent protection will not protect the wiring for overload. An overload condition could possibly allow 40 to 50 amps to flow on the smaller size wiring, causing it to overheat. If you had a way to have 30 amp protection connected to the 50 amp at the power post, then your wiring would be properly protected.
I'm sure that many people carry the adapters to connect their 30 amp coach to the 50 amp circuit, and they have had no problems...yet. You're going to get conflicting advice on this, and I'm sure there are plenty that disagree with me. With 47 years active in the electrical trade prior to retirement I've seen enough to know that it's not something I would do.
Good stuff, thanks for sharing. I am wrong to assume that if I used my 30 AMP power/surge guard I would be protected? EDIT: Sorry, I see this was already addressed. Thanks.
Ldubs is offline   Reply With Quote
Old 09-06-2021, 11:01 AM   #14
Senior Member
 
Podivin's Avatar
 
Winnebago Owners Club
Join Date: Dec 2015
Location: Jacksonville, Fl
Posts: 3,542
Quote:
Originally Posted by The Brews Cruise View Post
As a retired electrician, I wouldn't call connecting a 30 amp coach to a 50 amp circuit "safe". It can be done with a "dogbone" adapter. The problem I see is that your cord and internal wiring to your panel is sized for 30 amps, but the 50 amp overcurrent protection will not protect the wiring for overload. An overload condition could possibly allow 40 to 50 amps to flow on the smaller size wiring, causing it to overheat. If you had a way to have 30 amp protection connected to the 50 amp at the power post, then your wiring would be properly protected.
I'm sure that many people carry the adapters to connect their 30 amp coach to the 50 amp circuit, and they have had no problems...yet. You're going to get conflicting advice on this, and I'm sure there are plenty that disagree with me. With 47 years active in the electrical trade prior to retirement I've seen enough to know that it's not something I would do.
Seems to me that's what the 30 amp main breaker in the RV is for. The RV isn't going to pull more than 30 amps, if it tries to it will trip the main.
__________________
2013 Winnebago Sightseer 36V
Podivin is offline   Reply With Quote
Reply

Tags
electric, electrical, newbie



Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Newbie electrical question taylormclam RV Systems & Appliances 27 09-06-2016 11:35 AM
Newbie electrical question rjasutton Class C Motorhome Discussions 8 04-27-2016 01:54 PM
Ultra-newbie electrical question Pgustaf249 RV Systems & Appliances 6 07-17-2014 05:38 AM
Newbie Question About Power Inverters and Electrical exploring RV Systems & Appliances 11 01-05-2014 03:18 PM
Newbie to forum, newbie to rv'ing, and I have a newbie problem last_lemming Class B Motorhome Discussions 36 09-06-2012 06:14 PM

» Featured Campgrounds

Reviews provided by


All times are GMT -6. The time now is 12:39 AM.


Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.