Onan generator
Hello everyone, I just recently bought a 2004 four winds c class and is very happy with it except for the generator It is a 4000 watt onan micro lite that starts and runs great,my problem is when I run it for awhile on full load and then shut it off it will not start until it cools down. It shows a 36 code.Ive changed the oil and reduced the amount and new spark plug. Any heip help would be appreciated, oh yeah I'm a noobie to this site and love it.
|
|
|
|
Join the #1 RV Forum Today - It's Totally Free!
iRV2.com RV Community - Are you about to start a new improvement on your RV or need some help with some maintenance? Do you need advice on what products to buy? Or maybe you can give others some advice? No matter where you fit in you'll find that iRV2 is a great community to join. Best of all it's totally FREE!
You are currently viewing our boards as a guest so you have limited access to our community. Please take the time to register and you will gain a lot of great new features including; the ability to participate in discussions, network with other RV owners, see fewer ads, upload photographs, create an RV blog, send private messages and so much, much more!
|
06-17-2021, 07:01 PM
|
#2
|
Senior Member
Join Date: Mar 2021
Posts: 518
|
Try running with the basement door open and a load on the generator. I've heard some of these have an air flow problem.
I actually think someone was just talking about this a couple weeks ago on this forum. Try and do a quick search and you will find the thread. A few good suggestions in that thread if I remember correctly.
__________________
"A Man's Gotta Do What a man's Gotta Do"
2000 Fleetwood Southwind Storm 30H- Workhorse
2016 Prime Time Tracer 3150BHD
|
|
|
06-17-2021, 07:20 PM
|
#3
|
Senior Member
Join Date: Feb 2013
Location: Sedona, AZ
Posts: 3,012
|
My (different Onan) does the same thing. I have been told it is because the fuel line to it gets hot near the hot generator and needs to be moved or insulated. I haven't done that, but I am on a hot trip now, and today I tried priming it longer than I usually do, and it started. Good luck.
__________________
Shell Bleiweiss
2014 1/2 Thor Challenger 37KT
Sedona, AZ
|
|
|
06-17-2021, 08:33 PM
|
#4
|
Junior Member
Join Date: Jun 2021
Posts: 5
|
Thanks guys,I'll try both suggestions.
|
|
|
06-18-2021, 07:01 AM
|
#5
|
Senior Member
Join Date: May 2010
Location: Part-time out of Mesquite, TX
Posts: 1,103
|
Quote:
Originally Posted by Duster73
Try running with the basement door open and a load on the generator. .
|
The owner's manual for my Onan says not to run it for very long or under load with the door open because the air movement was designed to operate with the door closed and that it will overheat if this is done.
|
|
|
06-18-2021, 07:36 AM
|
#6
|
Senior Member
Join Date: Mar 2021
Posts: 518
|
Quote:
Originally Posted by SKP Kirk
The owner's manual for my Onan says not to run it for very long or under load with the door open because the air movement was designed to operate with the door closed and that it will overheat if this is done.
|
I just went through the service manual for my 4k and it doesn't mention anything about air flow movement issues with the door open. It actually says what testing to do while the generator is running(need door open) But this wouldnt be for hours at a time I'm guessing.
O.P- You can always contact a service rep if needed. Also while going through the manual I found this info. Check that the oil level is perfect. If not, apparently it will cause a possible stall condition.
__________________
"A Man's Gotta Do What a man's Gotta Do"
2000 Fleetwood Southwind Storm 30H- Workhorse
2016 Prime Time Tracer 3150BHD
|
|
|
06-18-2021, 07:44 AM
|
#7
|
Senior Member
Join Date: Mar 2021
Posts: 518
|
https://www.irv2.com/forums/f59/gene...ff-539925.html
Here is the link I mentioned before. Some other suggestions are in that thread.
__________________
"A Man's Gotta Do What a man's Gotta Do"
2000 Fleetwood Southwind Storm 30H- Workhorse
2016 Prime Time Tracer 3150BHD
|
|
|
06-20-2021, 08:37 AM
|
#8
|
Senior Member
Join Date: Dec 2017
Posts: 1,698
|
They mean the door to the generator enclosure. Not the door to the compartment the generator is located in.
Quote:
Originally Posted by SKP Kirk
The owner's manual for my Onan says not to run it for very long or under load with the door open because the air movement was designed to operate with the door closed and that it will overheat if this is done.
|
__________________
TeamFoxy ~ Traveling North America
2016 Newmar Canyon Star 3710
2017 Chevy Equinox in tow.
|
|
|
06-20-2021, 05:59 PM
|
#9
|
Senior Member
Join Date: Apr 2017
Location: Vista, Ca
Posts: 497
|
I was having surging and what I thought were over heating issues with my 4K Microquiet. I recently changed the fuel pump with a Onan brand one, new Wix fuel filter and also pulled the Altitude Adjustment Cap off the main jet and back it out richer until the surging went away. Have ZERO issues now.
__________________
1992 Dodge D250, 18cm housing, getrag 5sp, 4" straight pipe
2015 Pacific Coachworks Sand sport 18SLE
|
|
|
06-20-2021, 09:32 PM
|
#10
|
Senior Member
Monaco Owners Club
Join Date: Jan 2010
Posts: 2,660
|
Might check the fuel line from the fuel pump to the carb for a kink in the rubber hose. Also, if you push the lower portion of the remote start switch on the generator, you should be able to hear the pump operating(priming). You can verify this by pulling the fuel hose end off where it attaches to the carb - making sure you have good fuel flow into a container.
Stabil or a heavy dose of Sea Foam in the fuel tank can't hurt either engine, especially with occasional use...keeps those fuel components from getting 'sticky'.
__________________
Jan and Bob
'05 Monaco Windsor 40 DST - ISL / '08 Wrangler
|
|
|
06-21-2021, 01:03 AM
|
#11
|
Registered User
Join Date: Aug 2016
Location: Seattle,WA/HB,CA./Fujieda-Japan
Posts: 849
|
Some of the 4k Microquiet gen sets do not have and LED light on the on/off switch (such as mine). So no error code/s to read. Mine also does not have a low oil shut off feature nor the prime feature.
First thing I check is the oil level. Be sure the coach is level. And make sure the oil is neither low or over full.
|
|
|
06-21-2021, 01:38 AM
|
#12
|
Senior Member
Join Date: Mar 2016
Location: Morehead City NC
Posts: 492
|
This is a common problem with the Onan 4000 which draws the cooling air from the side which is usually just inches from the compartment door when closed forcing the generator to pull hot air from underneath where the exhaust and engine are. They make a special compartment door vent to fix this. It has a rubber boot that mounts between the compartment door and fresh air intake forcing fresh air to be drawn from the outside instead of under the rv. Here is a pic of mine when I installed it.
__________________
2016 Jayco Precept 31 UL
|
|
|
06-21-2021, 06:58 AM
|
#13
|
Junior Member
Join Date: Jun 2021
Posts: 5
|
Thanks everyone, I ran it for a hour yesterday with the compartment door open and the air conditioner on and it ran perfect .I shut it down and it wouldn't restart,waited another hour and still wouldn't start.I am going to order a new onan fuel pump and filter and look into the vent for the door.Iwill let you all know the results .
|
|
|
06-21-2021, 07:09 AM
|
#14
|
Senior Member
Join Date: Jan 2017
Location: Titusville, FL
Posts: 5,164
|
You can get a filter and pump on Amazon and save a bunch of bucks.
Code 36 is nonspecific but usually fuel related. I believe overheat has it's own code. 36 is shut down for unknown reason. Like no fuel.
__________________
When seconds count, the police are only minutes away.
2023 Grand Design 2600RB, 2022 F-350 King Ranch tow vehicle, Titusville, FL when not on the road
|
|
|
|
|
Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
|
|