01-17-2023, 02:19 PM
|
#1
|
Senior Member
Join Date: Feb 2020
Posts: 1,431
|
RV electric outlet in garage
We travel a lot in the summer, trying to get away from the heat here in southern Arizona, and we prep our RV in our driveway. But to do that we need to run the roof AC to get the inside cool enough to allow the fridge to cool down and I don't want to use the generator to do that. In the past (with other RVs) we used to just plug the RV into the 15 amp outlet in our garage and run the AC, but our current RV draw about 16-17 amps just to run the AC so that no longer works for us.
I thought I would have either a 20 amp regular outlet or a 30 amp RV outlet installed in the garage to take care of the issue, but many of the electricians I have spoken with are unfamiliar with the 30 amp RV outlet and all of the normal-outlet-to-RV adapters I have or have seen are 15 amps, so I am a bit stuck. (The adapter type I am talking about is one like this one).
Are there any 20 amp adapters available? If so, where? I have not seen any on Amazon. And are there any special wiring instructions for a normal 30 amp RV outlet?
I am a bit nervous about having an electrician who does not know about RV outlets wire up something that I will plug the RV into. The last one I spoke with said he assumed it was 220 volts and that does not give me much confidence. Also, any other suggestions would be helpful.
Thanks.
__________________
2020 Regency Ultra Brougham, Island Bed Model
2022 Jeep Wranger 2 door Sport S toad
Roadmaster baseplate and tow bar
|
|
|
|
Join the #1 RV Forum Today - It's Totally Free!
iRV2.com RV Community - Are you about to start a new improvement on your RV or need some help with some maintenance? Do you need advice on what products to buy? Or maybe you can give others some advice? No matter where you fit in you'll find that iRV2 is a great community to join. Best of all it's totally FREE!
You are currently viewing our boards as a guest so you have limited access to our community. Please take the time to register and you will gain a lot of great new features including; the ability to participate in discussions, network with other RV owners, see fewer ads, upload photographs, create an RV blog, send private messages and so much, much more!
|
01-17-2023, 02:34 PM
|
#2
|
Senior Member
Join Date: Jul 2014
Posts: 35,349
|
Tell them a 30 amp RV outlet, TT30, is a 120 volt outlet.
Make sure they use a single pole breaker.
Another option is to have them install a L5-30 outlet. It's a twist lock 120 volt outlet.
With that you'll need a adaptor.
|
|
|
01-17-2023, 02:36 PM
|
#3
|
Senior Member
Join Date: Apr 2018
Posts: 3,441
|
30 amp rv is just a 120v circuit. wire just like a 20 or 15. EXCEPT.. you will
be using 10 gauge romex to the 30 amp receptacle from the 30 amp breaker . your 50 to 30 amp adapter will do the rest.
__________________
2004 Dynasty 4
|
|
|
01-17-2023, 03:11 PM
|
#4
|
Senior Member
Alpine Owners Club
Join Date: Oct 2019
Location: Hoodsport Wa
Posts: 3,116
|
RV Electrical Wiring
Personally I wouldn’t bother with a 20a.
Run the 30a just like this to a 30a dedicated breaker in the garage panel. (Or better yet 50a if your garage circuit is capable)
Many use a simple wall mount conduit drop out of the panel to your desired location. A NEC approved ground rod should be utilized for this circuit.
__________________
2000 Alpine 36 FDS #74058
04 Jeep Wrangler TJ
"On the road to find out..."
|
|
|
01-17-2023, 03:16 PM
|
#5
|
Community Administrator
Tiffin Owners Club
Join Date: Sep 2013
Location: DFW, Texas
Posts: 21,262
|
The main thing is do not let them wire a 30amp RV outlet like a dryer or stove outlet as those are 240v not 120v.
__________________
2017 Phaeton 40IH XSH Maroon Coral - Power Glide Chassis with IFS
Previous '15 Tiffin Allegro RED 38QRA and '06 Itasca Sunrise 35A
'16 Jeep JKU Wrangler Sahara or '08 Honda Goldwing
|
|
|
01-17-2023, 03:22 PM
|
#6
|
Senior Member
Join Date: Apr 2018
Posts: 3,441
|
Quote:
Originally Posted by Alpine36
Personally I wouldn’t bother with a 20a.
Run the 30a just like this to a 30a dedicated breaker in the garage panel. (Or better yet 50a if your garage circuit is capable)
Many use a simple wall mount conduit drop out of the panel to your desired location. A NEC approved ground rod should be utilized for this circuit.
|
One ground rod at the main. You can add a second if you are 100s of feet away. You don't want a lighting strike using your lawn as a path. Especially with you walking across it at the time.
__________________
2004 Dynasty 4
|
|
|
01-17-2023, 03:38 PM
|
#7
|
Senior Member
Alpine Owners Club
Join Date: Oct 2019
Location: Hoodsport Wa
Posts: 3,116
|
Quote:
Originally Posted by shootist
One ground rod at the main. You can add a second if you are 100s of feet away. You don't want a lighting strike using your lawn as a path. Especially with you walking across it at the time.
|
Exactly. Best not to bond the neutral and the ground though.
So many panels are, I’d always suggest dedicating a stand alone ground on all 30-50a RV circuits.
For that reason I believe they actually call it a “chassis” ground.
But that’s just me, too many years working around energized sub stations with equipment lol.
__________________
2000 Alpine 36 FDS #74058
04 Jeep Wrangler TJ
"On the road to find out..."
|
|
|
01-17-2023, 03:45 PM
|
#8
|
Senior Member
Join Date: May 2018
Posts: 3,157
|
So disappointing that an electrician would not correctly connect a TT-30. The terminals themselves are identified, one is silver and one is gold. I am a retired electrician, if you live in Tucson I would be happy to stop by and inspect their work before you use it.
__________________
Brian, 2011 Winnebago Via Class A on Sprinter Chassis
2000 Jeep TJ toad
Tucson, AZ
|
|
|
01-17-2023, 03:54 PM
|
#9
|
Senior Member
Join Date: Feb 2020
Posts: 1,431
|
Quote:
Originally Posted by shootist
30 amp rv is just a 120v circuit. wire just like a 20 or 15. EXCEPT.. you will
be using 10 gauge romex to the 30 amp receptacle from the 30 amp breaker . your 50 to 30 amp adapter will do the rest.
|
I guess I was not complete enough. Our RV is a 30 amp B+/C. The adapter I was speaking of is the one that adapts from a standard home 110 3 plug outlet to the standard 30 amp RV connection.
__________________
2020 Regency Ultra Brougham, Island Bed Model
2022 Jeep Wranger 2 door Sport S toad
Roadmaster baseplate and tow bar
|
|
|
01-17-2023, 04:00 PM
|
#10
|
Community Administrator
Tiffin Owners Club
Join Date: Sep 2013
Location: DFW, Texas
Posts: 21,262
|
Quote:
Originally Posted by AJMike
I guess I was not complete enough. Our RV is a 30 amp B+/C. The adapter I was speaking of is the one that adapts from a standard home 110 3 plug outlet to the standard 30 amp RV connection.
|
Yes, 20 amp household to 30 amp RV connections are readily available on Amazon. Most of us carry one and here is just one listing.
https://www.amazon.com/RVGUARD-Adapt.../dp/B09TFCKN2J
__________________
2017 Phaeton 40IH XSH Maroon Coral - Power Glide Chassis with IFS
Previous '15 Tiffin Allegro RED 38QRA and '06 Itasca Sunrise 35A
'16 Jeep JKU Wrangler Sahara or '08 Honda Goldwing
|
|
|
01-17-2023, 04:02 PM
|
#11
|
Senior Member
Join Date: Feb 2020
Posts: 1,431
|
Quote:
Originally Posted by bigb56
So disappointing that an electrician would not correctly connect a TT-30. The terminals themselves are identified, one is silver and one is gold. I am a retired electrician, if you live in Tucson I would be happy to stop by and inspect their work before you use it.
|
Thank you for the offer, but we live in the Phoenix area, way on the outside of the metroplex.
Is there any way to tell if a 30 amp RV outlet is wired correctly using just a voltmeter? I do have one of those outlet testers ( here) that is supposed to tell me if there are any wiring problems, but I really don't know how much mis-wiring they can identify.
__________________
2020 Regency Ultra Brougham, Island Bed Model
2022 Jeep Wranger 2 door Sport S toad
Roadmaster baseplate and tow bar
|
|
|
01-17-2023, 04:06 PM
|
#12
|
Senior Member
Join Date: Feb 2020
Posts: 1,431
|
Quote:
Originally Posted by Lt Dan
|
But that is only 15 amps on the standard outlet side (15A male to 30A female, as stated in the description). I would need 20 amps. They may make those, but I have not found one yet.
__________________
2020 Regency Ultra Brougham, Island Bed Model
2022 Jeep Wranger 2 door Sport S toad
Roadmaster baseplate and tow bar
|
|
|
01-17-2023, 04:24 PM
|
#13
|
Senior Member
Alpine Owners Club
Join Date: Oct 2019
Location: Hoodsport Wa
Posts: 3,116
|
Running the AC (17a) and fridge simultaneously is pushing 20a. A 20a wall outlet upgrade won’t solve your issue long term. I wouldn’t, especially with an adaptor involved, it’s just way too easy to overload.
30a circuit is relatively inexpensive insurance.
__________________
2000 Alpine 36 FDS #74058
04 Jeep Wrangler TJ
"On the road to find out..."
|
|
|
01-17-2023, 04:26 PM
|
#14
|
Senior Member
Join Date: Feb 2020
Posts: 1,431
|
Quote:
Originally Posted by Alpine36
Personally I wouldn’t bother with a 20a.
Run the 30a just like this to a 30a dedicated breaker in the garage panel. (Or better yet 50a if your garage circuit is capable)
Many use a simple wall mount conduit drop out of the panel to your desired location. A NEC approved ground rod should be utilized for this circuit.
|
Thank you for the information. I have downloaded the images and will use them if I find an electrician who seems to know what he (or she) is doing.
__________________
2020 Regency Ultra Brougham, Island Bed Model
2022 Jeep Wranger 2 door Sport S toad
Roadmaster baseplate and tow bar
|
|
|
|
|