Journey with Confidence RV GPS App RV Trip Planner RV LIFE Campground Reviews RV Maintenance Take a Speed Test Free 7 Day Trial ×
RV Trip Planning Discussions

Go Back   iRV2 Forums > iRV2.com COMMUNITY FORUMS > iRV2.com General Discussion
Click Here to Login
Register FilesVendors Registry Blogs FAQ Community Calendar Today's Posts Search Log in
Join iRV2 Today

Mission Statement: Supporting thoughtful exchange of knowledge, values and experience among RV enthusiasts.
Reply
  This discussion is proudly sponsored by:
Please support our sponsors and let them know you heard about their products on iRV2
 
Thread Tools Search this Thread Display Modes
 
Old 01-11-2023, 08:59 PM   #1
Senior Member
 
Duster73's Avatar
 
Join Date: Mar 2021
Posts: 519
RV Generator for House Use

Hello all, I have a question that will hopefully be a simplei-sh answer for some.

I have my 4k watt, 120V 60hz, 30A generator that I use for my camper. It has a L5-30, 30A outlet for residential use also.

My question is, can I take a 3 prong (L5-30) inlet box that will go on the outside of my home. Wire 10/3 romex (ground, neutral, black and red) in a way where the black and red power is on one pin of the inlet box so I have two power wires going into my houses breaker panel. Then attach this to a double pole 30A breaker in the available space?

My goal is to energize both legs of my houses panel at 120V. I understand that there will be no 240V and the only 240V breaker I have, will be turned off. But I'd like to be able to choose which breakers I need in the entire panel.

Unfortunately whoever owned the house before me cut the wires in the panel so short, I can't really rearrange the breakers to 1 leg.

If I did the above install, will everything work at 60hz and function normal at 120V on both legs?

Is my thinking correct or way off base?

I am not buying a 240V generator, and I understand limiting power usage.
Duster73 is offline   Reply With Quote
Join the #1 RV Forum Today - It's Totally Free!

iRV2.com RV Community - Are you about to start a new improvement on your RV or need some help with some maintenance? Do you need advice on what products to buy? Or maybe you can give others some advice? No matter where you fit in you'll find that iRV2 is a great community to join. Best of all it's totally FREE!

You are currently viewing our boards as a guest so you have limited access to our community. Please take the time to register and you will gain a lot of great new features including; the ability to participate in discussions, network with other RV owners, see fewer ads, upload photographs, create an RV blog, send private messages and so much, much more!

Old 01-11-2023, 09:07 PM   #2
Member
 
Join Date: Feb 2022
Posts: 45
yes, I have done that with a interlock device to protect from back feeding. Works with no issues.

I have two 200 amp panels in my house and the way it was wired was all the 120 outlets are in one panel, so this is the one I used.

If you have 240 volt double pole breakers in that panel I would turn them off. That device might have some parts that use 120 volts along with the 240 and may cause issues.
Learjet 1 is offline   Reply With Quote
Old 01-12-2023, 04:36 AM   #3
Senior Member
 
Join Date: Mar 2019
Posts: 1,964
The key words in the previous post are "interlock device".

Check your local codes before wiring in a generator.
bentjm is offline   Reply With Quote
Old 01-12-2023, 04:51 AM   #4
Senior Member
 
Join Date: Dec 2021
Location: Florida
Posts: 151
you will need to install something similar to this so you do not back-feed the grid and kill a lineman; suggest an electrician if you are not handy.
https://www.lowes.com/pd/Reliance-30...E&gclsrc=aw.ds
__________________
2019 Coachmen Freelander 32DS/E450 V10
--------------
2023 Entegra Ethos 20A
Piney2 is offline   Reply With Quote
Old 01-12-2023, 04:53 AM   #5
Senior Member
 
MRUSA14's Avatar
 
Entegra Owners Club
Join Date: Nov 2012
Posts: 8,149
Quote:
Originally Posted by bentjm View Post
The key words in the previous post are "interlock device".

Check your local codes before wiring in a generator.
Ditto. Without the proper interlock devise you could kill someone. Don’t do it without being sure you meet all the codes.
__________________
Marc and Jill, Wellington FL
2013 Entegra Anthem 44SL
2018 Lincoln MKX
MRUSA14 is offline   Reply With Quote
Old 01-12-2023, 05:53 AM   #6
Member
 
BasicDude's Avatar
 
Join Date: Jan 2023
Location: Heart of Dixie
Posts: 30
Quote:
Originally Posted by Duster73 View Post
Unfortunately whoever owned the house before me cut the wires in the panel so short, I can't really rearrange the breakers to 1 leg.
You do not want to even consider this rearranging of circuits anyway. You need to have the electrical load balanced between what in reality is two halves of the 240V feed. You do not want to load up everything on one side for the sake of convenience for your generator.

It is feasible to feed the two separate 120V legs with the same 120V feed - but I anticipate you are aware; you need be very cautions to not have the main breaker on or any other two pole breakers. It won't even take half a second for things go bad over even the simplest lapse in judgement.

I have done this for a living, and yes - I have back fed my home panels with generators in the past (the I'm not going to spend a lot of money methods) and it is all too easy to make a mistake and let the smoke out of some things...
__________________
Tow Vehicle - 2020 RAM 3500 6.7HO AS69RC 3.73 SRW SBCC 4WD
Camper - 2017 Forest River Wildwood 232 RB XL
BasicDude is offline   Reply With Quote
Old 01-12-2023, 06:23 AM   #7
Senior Member
Commercial Member
 
Join Date: Jun 2005
Location: behind the steering wheel
Posts: 2,576
its easy enough to do. just be sure to use a licensed electrician to do it.
its done all the time by companies that sell generators for home power back up. its usually done with an automatic transfer switch in the middle to protect everyone involved.
an electrician is much cheaper than a lawyer.
i just run a couple of cords into the house from my rv to run the refrig and the tv.
azpete is offline   Reply With Quote
Old 01-12-2023, 07:09 AM   #8
Senior Member
 
Join Date: Jan 2009
Posts: 5,399
Not supposed to do it but I've pulled the meter a time or two when I knew it would be a long while before power was restored. This was my sure fire disconnect to keep my genset voltage from getting out. This was with a 4k watt Onan and was to run refrigerator, washing machine, and a few lights in the house.

That was convenient but I probably won't do that again since it's really just as easy to run a heavy extension cord from the genset into the house. Then use it to power different items as needed. It was hot back when Rita came through, we couldn't run the residential hvac system off the genset, so we slept in the motorhome anyway.

Imo, it's not worth the trouble trying to get both legs hot with a small 4k watt genset. You can only run a few things at a time anyway and there'll probably be some tripping of breakers if you or a family member isn't paying attention.
__________________
03 Itasca Sunova, Workhorse P32 with the 8.1 and 4L85-E
Mudfrog is offline   Reply With Quote
Old 01-12-2023, 07:46 AM   #9
Senior Member
 
Duster73's Avatar
 
Join Date: Mar 2021
Posts: 519
Thanks for the replies, I do plan to install an interlock switch.

Before I had two little kids, I'd just run the cord into the house from the generator to power certain items. But now with night lights and noise machines. I need to power different rooms along with the refrigerator and deep freezer. So that's why I am looking into this option. 4000 watts is more than enough to power what I need for emergencies.

I'm glad it will power both legs at 120V as I thought.
__________________
"A Man's Gotta Do What a man's Gotta Do"
2000 Fleetwood Southwind Storm 30H- Workhorse
2016 Prime Time Tracer 3150BHD
Duster73 is offline   Reply With Quote
Old 01-12-2023, 11:08 AM   #10
Senior Member
 
Join Date: May 2019
Location: NJ
Posts: 474
We've lost power enough over the years to where we purchased a coleman 5500 watt 220 volt generator.

We just throw the main breaker to disconnect from the grid along with breakers for our AC and electric water heater, then back feed thru a 30 amp 220 volt ac outlet in our garage.

The cost of that gen set was about $600. It got us thru 14 days after hurricane Sandy, and many outages over the years.. The fact that we have a well for water supply, a deep freezer and sump pump in our basement were major factors in our decision.
Based on our situation it does the job at a reasonable cost.

I would recommend against any fancy wiring arrangements and be sure to comply with local codes.

All the best
1stimerveer is offline   Reply With Quote
Old 01-13-2023, 04:04 PM   #11
Senior Member
 
153stars's Avatar
 
Join Date: Mar 2019
Location: Braidwood Il.
Posts: 8,300
Oops double post ....below
__________________
95 Monaco Crown Royale
M11 400hp, 4060 trans.
Aquahot, Generac Guardian7.5k
153stars is offline   Reply With Quote
Old 01-13-2023, 05:01 PM   #12
Senior Member
 
153stars's Avatar
 
Join Date: Mar 2019
Location: Braidwood Il.
Posts: 8,300
Look for generator interlock kit for your brand of home CB panel. No need for a $400 generator ATS load center IMHO. You would need to rearrange the one breaker/location for use. Hopefully I don't have to mention not to consider any suicide cord or anything else crazy that comes up. https://www.google.com/search?q=gene...8s2NiAE_25:620
There are a ton of posts on powering house from MH already if you do a search.You may want future-proof your install by running the extra wire and 6ga wire or at least large enough conduit to pull 50amp wires. NEC grounding wire chart I checked shows #10ga copper good up to 60A for ground wire.
__________________
95 Monaco Crown Royale
M11 400hp, 4060 trans.
Aquahot, Generac Guardian7.5k
153stars is offline   Reply With Quote
Old 01-13-2023, 08:16 PM   #13
Senior Member
 
TB673's Avatar
 
Join Date: Sep 2018
Location: Cleveland, Ohio
Posts: 1,055
Quote:
Originally Posted by 1stimerveer View Post
We've lost power enough over the years to where we purchased a coleman 5500 watt 220 volt generator.

We just throw the main breaker to disconnect from the grid along with breakers for our AC and electric water heater, then back feed thru a 30 amp 220 volt ac outlet in our garage.

The cost of that gen set was about $600. It got us thru 14 days after hurricane Sandy, and many outages over the years.. The fact that we have a well for water supply, a deep freezer and sump pump in our basement were major factors in our decision.
Based on our situation it does the job at a reasonable cost.

I would recommend against any fancy wiring arrangements and be sure to comply with local codes.


All the best

How can you tell the OP to be sure to comply with local codes, when what you do is illegal as per the National Electrical Code by backfeeding your panel?
Article 702.2 of the NEC addresses this.


Tim
__________________
2015 Silverado 3500HD CC DRW Duramax
2006 Hitchhiker Champagne
TB673 is offline   Reply With Quote
Old 01-13-2023, 08:53 PM   #14
Senior Member
 
Join Date: Dec 1969
Posts: 2,668
Quote:
Originally Posted by Duster73 View Post
...

Before I had two little kids, ....
Now that is a good reason not to power your house with an RV toy.

My emergency plan included flash lights, candles, and board games.

Did not have a generator when camping either with small kids. No TV either.
__________________
Kit & Rita (in memory)
37 foot ‘98 HolidayRambler Endeavor diesel pusher
followingsea is offline   Reply With Quote
Reply

Tags
generator



Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
How to use RV generator as home backup generator? ShawofNH RV Systems & Appliances 16 08-14-2021 07:17 AM
Use RV generator to power my house? HECthe2 Class A Motorhome Discussions 113 12-23-2018 08:05 AM
How I use my motor home generator as a standby for my house mmcl26554 Class A Motorhome Discussions 28 05-26-2012 03:56 PM
What does everyone use for a shower caddy..if you use anything? StansCustoms Alpine Coach Owner's Forum 9 07-19-2011 06:37 PM

» Featured Campgrounds

Reviews provided by


All times are GMT -6. The time now is 11:29 AM.


Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.