Old 12-06-2016, 08:20 PM   #1
Member
 
Holiday Rambler Owners Club
Join Date: Sep 2016
Location: Runaway Bay, TX
Posts: 57
Trouble with plugging in to 110 volt

Have a question about plugging my coach into a 110 volt outlet just to keep the batteries topped off during the winter. So I downsized my 50 amp plug all the way down to a 110 volt plug and tried to plug it in to the GFI outlet at the storage shed unit but it immediately tripped the breaker even though I had all the 110 volt appliances off including the refrigerator, appliances, heaters, ect.. The only thing that was on is the Xantrex 2500 watt inverter/charger that was set to charge the batteries. Is there a particular way to keep from tripping the GFI 110 volt breaker or is even having the inverter on too much for such a small plug? Thanks for any and all comments or replies.
CatchinRays is offline   Reply With Quote
Join the #1 RV Forum Today - It's Totally Free!

iRV2.com RV Community - Are you about to start a new improvement on your RV or need some help with some maintenance? Do you need advice on what products to buy? Or maybe you can give others some advice? No matter where you fit in you'll find that iRV2 is a great community to join. Best of all it's totally FREE!

You are currently viewing our boards as a guest so you have limited access to our community. Please take the time to register and you will gain a lot of great new features including; the ability to participate in discussions, network with other RV owners, see fewer ads, upload photographs, create an RV blog, send private messages and so much, much more!

Old 12-06-2016, 08:24 PM   #2
Senior Member
 
no3putt's Avatar
 
Join Date: Apr 2012
Location: Pueblo, CO
Posts: 624
Two GFI on one circit usually dosen't work. Try to flip off your breakers in the MH that have GFI on them, usually just the 110 volt outlets.
__________________
2009 Berkshire 390 QS and toad
Retired and traveling
no3putt is offline   Reply With Quote
Old 12-06-2016, 08:25 PM   #3
Senior Member
 
JohnBoyToo's Avatar
 
Monaco Owners Club
Join Date: May 2012
Location: DFW, Tex-US
Posts: 6,196
Plug ours into 20 amp all the time at our storage area... and do nothing special re gfi breakers...

I would bet that you think you have everything turned off
or either you have something else on OR
that circuit supplies too many other outlets and yours is the one that put it over the top !?!

I know we have 4 or 5 spots that run off the circuit I am on and if any one of us leave an AC or heavy duty heater on, it will trip the breaker.

You should turn the invertor portion of your charger/invertor OFF since it's not needed to charge the batteries and it is actually a power hog (relatively speaking )

Good luck
__________________
'11 Monaco Diplomat 43DFT RR10R pushed by a '14 Jeep Wrangler JKU. History.. 5'ers: 13 Redwood 38gk(junk!), 11 MVP Destiny, Open Range TT, Winn LeSharo, C's, popups, vans, tents...
JohnBoyToo is offline   Reply With Quote
Old 12-06-2016, 08:25 PM   #4
Senior Member
 
Join Date: Jul 2015
Posts: 680
What is the outlet rated for amperage? 2500 watts at 110 volts is almost 23 amps.
parkerbill is offline   Reply With Quote
Old 12-06-2016, 08:34 PM   #5
Registered User
 
Join Date: Nov 2016
Location: indio california
Posts: 963
Quote:
Originally Posted by CatchinRays View Post
Have a question about plugging my coach into a 110 volt outlet just to keep the batteries topped off during the winter. So I downsized my 50 amp plug all the way down to a 110 volt plug and tried to plug it in to the GFI outlet at the storage shed unit but it immediately tripped the breaker even though I had all the 110 volt appliances off including the refrigerator, appliances, heaters, ect.. The only thing that was on is the Xantrex 2500 watt inverter/charger that was set to charge the batteries. Is there a particular way to keep from tripping the GFI 110 volt breaker or is even having the inverter on too much for such a small plug? Thanks for any and all comments or replies.
turn off ALL 120V breakers in your panel except the one that runs the converter part of your inverter
turn your charger down to 50% or less then should be good to go
select55 is offline   Reply With Quote
Old 12-06-2016, 08:35 PM   #6
Registered User
 
Join Date: Nov 2016
Location: indio california
Posts: 963
Quote:
Originally Posted by parkerbill View Post
What is the outlet rated for amperage? 2500 watts at 110 volts is almost 23 amps.
that would be irrelevant unless he was running the inverter and the inverter had full draw on it which by all signs he is not doing such
select55 is offline   Reply With Quote
Old 12-06-2016, 08:36 PM   #7
Senior Member
 
chboone's Avatar


 
National RV Owners Club
Ford Super Duty Owner
Join Date: Sep 2010
Location: Horse Town USA, CA.
Posts: 3,783
If the batteries are low the Inverter/ charger will go in to boost mode (high amp draw) and could trip the breaker depending on the output of your charger. Is there a setting for your charger to limit the the charge output. If it does try adjusting the output down.
__________________
1999 35 ft. Dolphin 5350, F53, Banks System, 5 Stars Tune, Air Lift Air Bags, Koni Shocks, Blue OX TruCenter, TigerTrak track bars F&R, Roadmaster 1-3/4" rear auxiliary sway bar, 2004 F450 Lariat Pickup 6.0 Diesel Crew Cab DRW, 4X4, GVWR 15,000, Front GAWR 6,000, Rear GAWR 11,000, GCWR 26,000,1994 36ft Avion 5er, GVWR 13,700, 2,740 Pin Weight.
chboone is offline   Reply With Quote
Old 12-06-2016, 08:50 PM   #8
Registered User
 
Join Date: Nov 2016
Location: indio california
Posts: 963
Quote:
Originally Posted by chboone View Post
If the batteries are low the Inverter/ charger will go in to boost mode (high amp draw) and could trip the breaker depending on the output of your charger. Is there a setting for your charger to limit the the charge output. If it does try adjusting the output down.
yes as I already suggested such(set chg rate lower) but there no way a charger should trip a 15 amp circuit assuming it has the proper voltage supplying such but if u go gfi against another gfi it will trip the gfi on the output end and that's his problem
select55 is offline   Reply With Quote
Old 12-06-2016, 09:10 PM   #9
Senior Member
 
Old-Biscuit's Avatar
 
Join Date: Nov 2015
Posts: 26,837
Quote:
Originally Posted by select55 View Post
yes as I already suggested such(set chg rate lower) but there no way a charger should trip a 15 amp circuit assuming it has the proper voltage supplying such but if u go gfi against another gfi it will trip the gfi on the output end and that's his problem

Unless the outlet OP is plugging into already has other loads upstream on it.
__________________
I took my Medication today. HAVE YOU?
Dodge 3500 w/Tractor Motor
US NAVY---USS Decatur DDG-31
Old-Biscuit is offline   Reply With Quote
Old 12-06-2016, 09:11 PM   #10
Member
 
Holiday Rambler Owners Club
Join Date: Sep 2016
Location: Runaway Bay, TX
Posts: 57
Well thanks for all the quick replies...was not expecting so many people commenting so quickly - but if this makes any difference....I do have everything off - I even turned off the breaker to the refrigerator so that it wouldn't be part of the draw. No heat, no a/c, no Aqua-Hot, no pumps... nothing was on except the Inverter that was set to "charge". But reading through my owners manual it does say to make sure the breaker that I'm plugging into is off....and it was not...but I just kept tripping it. AND: my batteries were extremely low - so it was definitely in "bulk" and pumping as much into them as it could. So, given that information, would the inverter be tripping the GFI breaker? Also, I know no other way to charge the batteries without having the Inverter on and set to charge?? In fact, as soon as I flip the switch to turn on the 8 coach batteries, the inverter automatically comes on...but it just depends on what setting you have it set to as to what it will be doing - either OFF, or CHG, etc....Thanks again for the replies.
CatchinRays is offline   Reply With Quote
Old 12-06-2016, 09:20 PM   #11
Member
 
Holiday Rambler Owners Club
Join Date: Sep 2016
Location: Runaway Bay, TX
Posts: 57
CORRECTION: I only turned off the breaker going to the fridge...I didn't turn off any of the other breakers...so I will do that when I go back. I thought since everything was off, I shouldn't have to flip the breaker...so thanks again for all the replies...I appreciate it.
CatchinRays is offline   Reply With Quote
Old 12-06-2016, 09:27 PM   #12
Registered User
 
Join Date: Nov 2016
Location: indio california
Posts: 963
Quote:
Originally Posted by CatchinRays View Post
Well thanks for all the quick replies...was not expecting so many people commenting so quickly - but if this makes any difference....I do have everything off - I even turned off the breaker to the refrigerator so that it wouldn't be part of the draw. No heat, no a/c, no Aqua-Hot, no pumps... nothing was on except the Inverter that was set to "charge". But reading through my owners manual it does say to make sure the breaker that I'm plugging into is off....and it was not...but I just kept tripping it. AND: my batteries were extremely low - so it was definitely in "bulk" and pumping as much into them as it could. So, given that information, would the inverter be tripping the GFI breaker? Also, I know no other way to charge the batteries without having the Inverter on and set to charge?? In fact, as soon as I flip the switch to turn on the 8 coach batteries, the inverter automatically comes on...but it just depends on what setting you have it set to as to what it will be doing - either OFF, or CHG, etc....Thanks again for the replies.
could be just the fact the batterys are very low and the charger draws full power so the voltage drop may be just a tad low?(under 110)
Depends on how far the GFI breaker is from the main house panel and then by the time it goes through the MH SP cord etc so just maybe a GFI breaker cant take it?? seems odd u cant set your charger voltage ? all of mine I have always been able to set the charge rate?
anyhow may have to go with a standard breaker
select55 is offline   Reply With Quote
Old 12-06-2016, 09:27 PM   #13
Senior Member
 
Old-Biscuit's Avatar
 
Join Date: Nov 2015
Posts: 26,837
The outlet you are plugging into..........

Is anything else on that circuit in storage shed etc.

That outlet needs to be ONLY feeding your MH and every individual branch CB in your MH OFF except the one to inverter/charger


Which breaker is tripping.......?
GFCI outlet
CB for GFCI
CB in MH
__________________
I took my Medication today. HAVE YOU?
Dodge 3500 w/Tractor Motor
US NAVY---USS Decatur DDG-31
Old-Biscuit is offline   Reply With Quote
Old 12-06-2016, 11:18 PM   #14
Senior Member
 
chboone's Avatar


 
National RV Owners Club
Ford Super Duty Owner
Join Date: Sep 2010
Location: Horse Town USA, CA.
Posts: 3,783
Quote:
Originally Posted by select55 View Post
yes as I already suggested such(set chg rate lower) but there no way a charger should trip a 15 amp circuit assuming it has the proper voltage supplying such but if u go gfi against another gfi it will trip the gfi on the output end and that's his problem
You posted while I was typing mine.
__________________
1999 35 ft. Dolphin 5350, F53, Banks System, 5 Stars Tune, Air Lift Air Bags, Koni Shocks, Blue OX TruCenter, TigerTrak track bars F&R, Roadmaster 1-3/4" rear auxiliary sway bar, 2004 F450 Lariat Pickup 6.0 Diesel Crew Cab DRW, 4X4, GVWR 15,000, Front GAWR 6,000, Rear GAWR 11,000, GCWR 26,000,1994 36ft Avion 5er, GVWR 13,700, 2,740 Pin Weight.
chboone is offline   Reply With Quote
Reply



Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Two different voltage sources, one switch to switch between my 12 volt and 110 volt wrq1103 RV Systems & Appliances 23 12-01-2016 05:42 PM
SK-3005 trouble finding 110 ? SCVJeff Technology: Internet, TV, Satellite, Cell Phones, etc. 12 05-09-2016 01:29 AM
Bounder: 110 volt to 12 volt converter problems sandbums99 Fleetwood Owner's Forum 9 05-03-2016 06:20 PM
plugging into 110 outlet bmerritt Class A Motorhome Discussions 19 02-14-2011 07:15 AM
Plugging into 110 with coach batteries removed Nonno Winnebago Industries Owner's Forum 18 12-31-2006 11:10 AM

» Featured Campgrounds

Reviews provided by


All times are GMT -6. The time now is 03:51 AM.


Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.