Old 01-12-2020, 06:10 PM   #15
Registered User
 
Join Date: Jan 2019
Posts: 396
Quote:
Originally Posted by Dutch Star Don View Post
Your statement would be correct if you tried to tie the two together with a cheater box and the second outlet was GFI protected. If you read what I wrote, I added a second power cord with separate outlets using two different circuits in the coach.
I think you will find that many 30 amp pedestals are wired as branch circuits with the box protected by a separate 30 amp breaker at the distribution panel. I have bought two parks that were wired this way, apparently it was the way to do it in the 60s and 70s. There was no loop feed of any kind, so the whole park needed to be rewired to upgrade them to 50 amp services.
Also, there are older pedestal boxes where the 30 amp breaker acts as a main breaker for the box and the 20 amp breaker feeds off the 30. In both of those cases there is only a total of 30 amps available off of that pedestal whether it is all taken from the 30 amp outlet of split between the 30 and 20.
kcdogger is offline   Reply With Quote
Join the #1 RV Forum Today - It's Totally Free!

iRV2.com RV Community - Are you about to start a new improvement on your RV or need some help with some maintenance? Do you need advice on what products to buy? Or maybe you can give others some advice? No matter where you fit in you'll find that iRV2 is a great community to join. Best of all it's totally FREE!

You are currently viewing our boards as a guest so you have limited access to our community. Please take the time to register and you will gain a lot of great new features including; the ability to participate in discussions, network with other RV owners, see fewer ads, upload photographs, create an RV blog, send private messages and so much, much more!

Old 01-12-2020, 06:58 PM   #16
Senior Member
 
KanzKran's Avatar
 
Join Date: Sep 2018
Posts: 1,944
The ANSI C84.1 voltage tolerance on nominal 120V systems that utilities are supposed to adhere to is -10 to +5%, which means 106-124V. That’s at the service equipment or meter, and that’s also essentially continuous, not counting switching transients or reaction time during voltage adjustment on the part of the utility. There will be voltage drop from there in the distribution and branch circuit wiring and equipment, of course, per the NEC.

Induction motors per the NEMA MG1 standard are designed for 115V (or 230V, 460V, 575V etc. for 240, 480, 600V, etc. systems), which means there’s a built-in allowance for voltage drop in the wiring. That doesn’t mean the compressor in a roof unit is rated 115V (though they should be, IMO), but low voltage and motors is never a good combo.
__________________
Tom & Jeri
2018 Coachmen Galleria 24T Li3
KanzKran is offline   Reply With Quote
Old 01-12-2020, 07:21 PM   #17
"Formerly Diplomat Don"
 
Dutch Star Don's Avatar
 
Newmar Owners Club
Join Date: Apr 2005
Location: Moorpark, Ca.
Posts: 24,076
Quote:
Originally Posted by kcdogger View Post
I think you will find that many 30 amp pedestals are wired as branch circuits with the box protected by a separate 30 amp breaker at the distribution panel. I have bought two parks that were wired this way, apparently it was the way to do it in the 60s and 70s. There was no loop feed of any kind, so the whole park needed to be rewired to upgrade them to 50 amp services.
Also, there are older pedestal boxes where the 30 amp breaker acts as a main breaker for the box and the 20 amp breaker feeds off the 30. In both of those cases there is only a total of 30 amps available off of that pedestal whether it is all taken from the 30 amp outlet of split between the 30 and 20.
Not what I've found.
__________________
Don & Mary
2019 Newmar Dutch Star 4018 (Freightliner)
2019 Ford Raptor
Dutch Star Don is offline   Reply With Quote
Old 01-13-2020, 12:45 PM   #18
Senior Member
 
Alan_Hepburn's Avatar


 
Fleetwood Owners Club
Workhorse Chassis Owner
Join Date: Feb 2000
Location: San Jose, Ca, USA
Posts: 2,697
Quote:
Originally Posted by KanzKran View Post
The ANSI C84.1 voltage tolerance on nominal 120V systems that utilities are supposed to adhere to is -10 to +5%, which means 106-124V.

I guess common core math really is different from traditional math: in my world 120V -10%/+5% works out to be 108V/126V...
__________________
Alan Hepburn - San Jose, Ca
2007 Bounder 35E being pushed by a 2020 Jeep Gladiator Sport S or a 2022 Jeep Wrangler Unlimited (JLU) Sport S
Alan_Hepburn is offline   Reply With Quote
Old 01-13-2020, 12:56 PM   #19
Senior Member
 
96 Wideglide's Avatar
 
Holiday Rambler Owners Club
Join Date: Aug 2010
Posts: 9,746
Quote:
Originally Posted by edmck101 View Post
I have a 39-foot Bighorn fifth wheel with two 15,000 BTU roof airs. Visiting friends here in Tucson, I’m connected to their 30 amp garage connection. Last week on two occasions I ran both ACs with no problem — the voltage meter I’m using (plugged into one of the 110V galley outlets) never dropped below 109 which I am told is well within the safe range.
If your going to do this, keep a close eye on your plugs!

I melted one on a 30A extension doing this, and that was with a Hughes Autoformer hooked up, keeping the voltage at about 112V!
__________________
Ben & Sharon
2008 43' Holiday Rambler Scepter PDQ
96 Wideglide is offline   Reply With Quote
Old 01-13-2020, 01:13 PM   #20
Senior Member
 
Busskipper's Avatar
 
Join Date: Sep 2007
Location: Grasonville, MD -- Golden, CO
Posts: 6,222
Quote:
Originally Posted by rvingwil View Post
I am brand new to Workamping and have an electrical question. I have an '05 Monaco Diplomat 40PDQ with W/D, micro, satellite, etc. I have been offered a Workamping position in Central CA but the campground only has 30amp service. I will be onsite for 5 months. What types of limits will that put on me? I know I wouldn't be able to run everything at the same time. Can anyone offer some advice on this?? Thx Bill
Sure as long as Heavy A/C is not needed then limits the space where you spend the day.

Without getting into all the Electrical BS - just means you have conserve and only run one major appliance at a time - we do it all the time with no air and only 20 amps - just start the generator every now and then.

Seriously not a big deal if in the Mountains and the evening are Cool.

Best of Luck,
__________________
Busskipper
Location - Grasonville, Maryland - and/or - Superior, Colorado
2005 Travel Supreme 42DS04 - GX470 Toad
Busskipper is offline   Reply With Quote
Old 01-14-2020, 08:47 AM   #21
Senior Member
 
KanzKran's Avatar
 
Join Date: Sep 2018
Posts: 1,944
Quote:
Originally Posted by Alan_Hepburn View Post
I guess common core math really is different from traditional math: in my world 120V -10%/+5% works out to be 108V/126V...
Don't know much about common core, but it seems my K&E slide rule needs adjustment.
__________________
Tom & Jeri
2018 Coachmen Galleria 24T Li3
KanzKran is offline   Reply With Quote
Old 01-14-2020, 03:47 PM   #22
Registered User
 
Join Date: Jan 2019
Posts: 396
Quote:
Originally Posted by Dutch Star Don View Post
Not what I've found.
My apologies. I didn't realize you examined RV park wiring whenever you stay at parks. It wouldn't be apparent to most people, since the only way to know is to examine the distribution panel at the main and take the cover off of the pedestal. It isn't your everyday park guest that has the inclination and the bravado to make such investigations. I guess we are both lucky you apparently haven't visited any of my parks because we would take a dim view of a guest taking either of those actions.
kcdogger is offline   Reply With Quote
Reply

Tags
workamping



Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Question about reducing a 50amp down to a 30amp cord for 30amp service Tony4qts Class C Motorhome Discussions 22 04-13-2019 03:15 PM
Only showing 30amp when connected 50amp Hanktheyank Fleetwood Owner's Forum 8 04-08-2016 05:57 PM
AC Electrical Feed Problem -- Only partial AC power available Birddog Pilot Alpine Coach Owner's Forum 21 07-11-2009 10:22 AM
Help is the Comfort Drive only available thru Newmar? T&G Spartan Motorhome Chassis Forum 9 06-01-2008 06:22 AM
What's NOT Available on '07 Journeys - Available Prior Pusherman Winnebago Industries Owner's Forum 7 01-05-2007 05:06 PM

» Featured Campgrounds

Reviews provided by


All times are GMT -6. The time now is 09:37 AM.


Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.