1st step, make sure generator is producing current/voltage. USE VOLT METER AT GEN TERMINALS WHILE GEN IS RUNNING
2nd step, is transfer switch engaging? USE VOLTMETER AT IN AND OUT CONTACT POINYS W GEN RUNNING AND AGAIN W SHORE PWR AND NO GEN
3rd step, is distribution system (breakers) getting input and passing it to output VOLT METER BETWEEN BREAKER AND GROUND BUS W GEN RUNNING AND W SHORE PWR, NO GEN.
4th step are recept circuits working/ connected. VOLT NETER AGAIN CONNECTED W SHORE POWER AND THEN W GEN RUNNING