Pressure switch, not RV related

This is not RV related but I think someone here on iRV2 can help.

My irrigation system is powered by a rather expensive 220 volt pump with water from a lake. I'm concerned that if for some reason the water to the pump is stopped, (broken pipe, lake level low) and the pump continues to run, the pump would be ruined. So I would like to install a pressure switch on the output side that would disconnect electrical power to the pump if there is no flow to the pump when it is running. The pump output pressure is normally 50-60 psi. When the pump stops, the output side does not retain pressure and pressure on the output side drops to 0.


So does anyone know of such a pressure switch? The only thing I can come with is a pressure sensing relay, but it would have to include a timer to give the pump enough time to build pressure after it started before shutting the pump down if it did not build pressure.
__________________
Tim
Leesburg, FL '07 American Tradition 40Z Cummins 400 ISL
Towing a '14 Honda CRV
Both sold
2021 Vanleigh Beacon 41LKB 5th wheel
timjet is offline   Reply With Quote
Join the #1 RV Forum Today - It's Totally Free!

iRV2.com RV Community - Are you about to start a new improvement on your RV or need some help with some maintenance? Do you need advice on what products to buy? Or maybe you can give others some advice? No matter where you fit in you'll find that iRV2 is a great community to join. Best of all it's totally FREE!

You are currently viewing our boards as a guest so you have limited access to our community. Please take the time to register and you will gain a lot of great new features including; the ability to participate in discussions, network with other RV owners, see fewer ads, upload photographs, create an RV blog, send private messages and so much, much more!

Old 05-25-2022, 09:10 AM   #2
Senior Member
 
Join Date: Aug 2019
Location: Eastern outskirts of Dallas, TX
Posts: 4,530
You use the NC contacts in a “time delay on” relay that allows the pump to run for a second or two before it opens the contacts, and a pressure switch on the output of the pump whose connections are across that set of contacts.
Those contacts then power the contactor coil for the pump.
__________________
‘91 Ultrastar Champion‘02 Georgie Boy Landau 8.1l Workhorse
‘03 Jeep Wrangler TJ 2018 Jeep Wrangler JK toad
MrMark52 is offline   Reply With Quote
Old 05-25-2022, 09:41 AM   #3
Senior Member
 
Old-Biscuit's Avatar
 
Join Date: Nov 2015
Posts: 26,800
Every well pump I have ever been around had a pressure switch on pump discharge with delay relay

Just Goggle 'Well Pump Pressure Switch'
__________________
I took my Medication today. HAVE YOU?
Dodge 3500 w/Tractor Motor
US NAVY---USS Decatur DDG-31
Old-Biscuit is online now   Reply With Quote
Old 05-25-2022, 10:00 AM   #4
Senior Member




 
Join Date: Mar 2016
Posts: 2,960
Thanks Mark, let me see if I've got this right. When power is supplied to the NC time delay relay, the pump contacts which are closed and the pump starts. Lets say for 10 seconds. During that 10 seconds the pump pressure builds and the pressure switch closes. After 10 sec this relay opens. At this point I'm a little foggy.

Are you suggesting a 2nd NO relay is added wired in parallel to the NC time relay where the closed pressure switch allows power to the coil of this second relay thus closing the relay and allowing the pump to continue running after the 10 sec relay has opened?
__________________
Tim
Leesburg, FL '07 American Tradition 40Z Cummins 400 ISL
Towing a '14 Honda CRV
Both sold
2021 Vanleigh Beacon 41LKB 5th wheel
timjet is offline   Reply With Quote
Old 05-25-2022, 10:02 AM   #5
Senior Member




 
Join Date: Mar 2016
Posts: 2,960
Quote:
Originally Posted by Old-Biscuit View Post
Every well pump I have ever been around had a pressure switch on pump discharge with delay relay

Just Goggle 'Well Pump Pressure Switch'

I think most of those switches turn off power to the pump when the pressure reaches the cut off point. I want the opposite, power removed from the pump if it drops to 0.
__________________
Tim
Leesburg, FL '07 American Tradition 40Z Cummins 400 ISL
Towing a '14 Honda CRV
Both sold
2021 Vanleigh Beacon 41LKB 5th wheel
timjet is offline   Reply With Quote
Old 05-25-2022, 10:19 AM   #6
Senior Member
 
JellyBean's Avatar
 
Monaco Owners Club
Join Date: Aug 2020
Posts: 216
.

My house is on a pump. I installed a Square D control for exactly this event. On/off at "you" set limit. AND it also shuts off if the pressure falls below a "you set" level.

If your system is asking for pressure and it runs dry the pump shuts down.

It is a Class: 9013 Type: FSG 2 Form: M4 Ser: B

Sorry it doesn't show a part number. Just ask a pump supplier and they can provide that number.

regards Glenn
__________________
2002 Monaco Windsor 8.3 350hp
34ft 3 slides 6 solar panels
Santa Cruz Mts, Calif
JellyBean is offline   Reply With Quote
Old 05-25-2022, 10:33 AM   #7
Senior Member
 
Join Date: Aug 2019
Location: Eastern outskirts of Dallas, TX
Posts: 4,530
Quote:
Originally Posted by timjet View Post
Thanks Mark, let me see if I've got this right. When power is supplied to the NC time delay relay, the pump contacts are closed and the pump starts. Lets say for 10 seconds. During that 10 seconds the pump pressure builds and the pressure switch closes. After 10 sec this relay opens. At this point I'm a little foggy.

Are you suggesting a 2nd NO relay is added wired in parallel to the NC time relay where the closed pressure switch allows power to the coil of this second relay thus closing the relay and allowing the pump to continue running after the 10 sec relay has opened?
You got the first part right.

Your pump should have a contactor or relay that is driven by the output from your irrigation controller.

You take that signal off of the existing pump relay and feed it to an NC terminal of a time delay relay (tdr) and to the coil of the tdr.
You then take the wires from the pressure switch and parallel with the above NC and C contacts.

And you take a wire from the C contact of the tdr back to the pump relay where the wire was previously removed.

Operation -

Pressure switch is open
NC contacts of tdr are of course, closed.

1) Irrigation controller calls for pump
2) Pump starts as NC contacts are closed, but pressure switch contacts are open.
3) Pressure builds and satisfies pressure switch - they are now closed.
4) tdr times out, NC contacts open
5a) if pressure switch is satisfied, pump continues to run
5b) if pressure switch is not satisfied, pump stops
6) tdr remains latched (NC contacts are open) until power is removed from circuit - but at this point the tdr is out of the circuit

Let me know if you need a sketch
__________________
‘91 Ultrastar Champion‘02 Georgie Boy Landau 8.1l Workhorse
‘03 Jeep Wrangler TJ 2018 Jeep Wrangler JK toad
MrMark52 is offline   Reply With Quote
Old 05-25-2022, 10:36 AM   #8
Senior Member
 
Old-Biscuit's Avatar
 
Join Date: Nov 2015
Posts: 26,800
Quote:
Originally Posted by JellyBean View Post
.

My house is on a pump. I installed a Square D control for exactly this event. On/off at "you" set limit. AND it also shuts off if the pressure falls below a "you set" level.

If your system is asking for pressure and it runs dry the pump shuts down.

It is a Class: 9013 Type: FSG 2 Form: M4 Ser: B

Sorry it doesn't show a part number. Just ask a pump supplier and they can provide that number.

regards Glenn
YEP^^^^^^^^^
__________________
I took my Medication today. HAVE YOU?
Dodge 3500 w/Tractor Motor
US NAVY---USS Decatur DDG-31
Old-Biscuit is online now   Reply With Quote
Old 05-25-2022, 11:32 AM   #9
Senior Member
 
Join Date: Aug 2019
Location: Eastern outskirts of Dallas, TX
Posts: 4,530
With all due respect - depending on the design of the irrigation system, there may not be any pressure in the pump discharge line when the controller tells the pump to run.

The Square D Pumptroller requires there to be pressure in the discharge pipe such as for a fresh water or fire safety system. The delta between the settings allows for pressure fluctuations. But that control will not allow the pump to run if there is no initial pressure at the pump discharge.

Many irrigation controllers provide for pump control. And when the last station is finished, it simultaneously cuts the signal to the pump and to the valve that is currently open.
But irrigation valves don’t slam shut, and close even more slowly the lower the pressure differential across the valve is. Hence, the pumps discharge line pressure could very well fall below that of the low pressure setting of the Pumptrol, if not 0 psi.

Either stated methodology would work - it’s just that one would likely be a little more problematic than the other.
__________________
‘91 Ultrastar Champion‘02 Georgie Boy Landau 8.1l Workhorse
‘03 Jeep Wrangler TJ 2018 Jeep Wrangler JK toad
MrMark52 is offline   Reply With Quote
Old 05-25-2022, 12:35 PM   #10
Senior Member




 
Join Date: Mar 2016
Posts: 2,960
Quote:
Originally Posted by Old-Biscuit View Post
YEP^^^^^^^^^
When I googled that part it came up with a well pump controller. It did have a low pressure cutoff circuit but you have to manually start the pump each time. After you manually started the pump then if pressure dropped below 5 psi the pump would shut off. At least that's how I understand it. Am I wrong??
__________________
Tim
Leesburg, FL '07 American Tradition 40Z Cummins 400 ISL
Towing a '14 Honda CRV
Both sold
2021 Vanleigh Beacon 41LKB 5th wheel
timjet is offline   Reply With Quote
Old 05-25-2022, 12:40 PM   #11
Senior Member




 
Join Date: Mar 2016
Posts: 2,960
Mark, I know the diagram below is not how you described the circuitry. I think in my diagram voltage would back feed back to the circuit breakers during the time between the low pressure switch closed and the time delay ended. Could you please correct the diagram?
Attached Thumbnails
Click image for larger version

Name:	Low Pressure pump cutout.jpg
Views:	26
Size:	53.4 KB
ID:	366554  
__________________
Tim
Leesburg, FL '07 American Tradition 40Z Cummins 400 ISL
Towing a '14 Honda CRV
Both sold
2021 Vanleigh Beacon 41LKB 5th wheel
timjet is offline   Reply With Quote
Old 05-25-2022, 02:24 PM   #12
Senior Member
 
Join Date: Aug 2019
Location: Eastern outskirts of Dallas, TX
Posts: 4,530
Easier for me to just draw by hand (I’ve lost all my chair licenses to AutoCAD).

Let me know if you need it drawn as a wiring diagram.
Attached Thumbnails
Click image for larger version

Name:	D8D93A5B-E456-494A-BA28-A87BFE118441.jpg
Views:	22
Size:	318.1 KB
ID:	366558  
__________________
‘91 Ultrastar Champion‘02 Georgie Boy Landau 8.1l Workhorse
‘03 Jeep Wrangler TJ 2018 Jeep Wrangler JK toad
MrMark52 is offline   Reply With Quote
Old 05-25-2022, 02:30 PM   #13
Senior Member




 
Join Date: Mar 2016
Posts: 2,960
Thanks Mark. Hate to ask but I think I need it as a wiring diagram. Also do you know where to get a flow sensor and time delay relay. I can't believe how hard to find these items has been. I haven't been able to find a time delay relay that is 30 amps and flow switches are just not made for this. I guess I could use an automotive oil pressure switch.
__________________
Tim
Leesburg, FL '07 American Tradition 40Z Cummins 400 ISL
Towing a '14 Honda CRV
Both sold
2021 Vanleigh Beacon 41LKB 5th wheel
timjet is offline   Reply With Quote
Old 05-25-2022, 02:47 PM   #14
Senior Member
 
Argosy's Avatar
 
Join Date: May 2004
Location: MI
Posts: 2,189
You need a low pressure cut off switch. I got one from a reverse osmosis water system that I use to control the electric element in my RV water heater. The pump in the RO system pressurizes the plumbing, if the filter hasn't made enough water for the pump to do that the low pressure switch won't close and the pump won't run, or quits running.


Use that to control a relay capable of the power your pump draws.
Argosy is offline   Reply With Quote
Reply

Tags
switch



Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Tire pressure related to ride comfort Ebuss Trailer Towing and Tow Vehicles Discussion 16 02-20-2018 01:19 AM
Palazzo Issues..and Hopefully Fixes NOT related to slides Butte64 Palazzo Motorhomes 134 04-03-2014 08:54 PM
Texas weather (not RV related) TXBart Entegra Owner's Forum 12 12-19-2013 05:31 AM
quality control and warranty-related or not? bigmichael Excel Owner's Forum 3 01-14-2010 08:53 AM

» Featured Campgrounds

Reviews provided by


All times are GMT -6. The time now is 12:41 PM.


Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.