That black capacitor you are talking about is a start capacitor these have to come out of the circuit after the motor starts usually by a relay. The metal case capacitors are run capacitors they are in the circuit all the time. Normally start capacitors are used to start the compressor not the fan motor. Probably that start capacitor was for the compressor. You probably have a dead spot in the windings of the motor and if it stops on that point it will not restart. Motor is probably bad and will need to be replaced. Sorry but I have never taken a fan motor out of one of these units so I don't know specifically how they come apart. RV rooftop A/C unit I think are like window A/C units. Which have a double shaft motor with a fan on one end and a squirrel cage blower on the other end. The fan is usually not hard to remove but getting to the squirrel cage may be harder to get to for removal. Sorry I don't have more specific info.
__________________
2004 Itasca Horizon 40AD caterpillar C7 engine 350 HP with 2016 Smart car toad
Heating man is offline   Reply With Quote
Join the #1 RV Forum Today - It's Totally Free!

iRV2.com RV Community - Are you about to start a new improvement on your RV or need some help with some maintenance? Do you need advice on what products to buy? Or maybe you can give others some advice? No matter where you fit in you'll find that iRV2 is a great community to join. Best of all it's totally FREE!

You are currently viewing our boards as a guest so you have limited access to our community. Please take the time to register and you will gain a lot of great new features including; the ability to participate in discussions, network with other RV owners, see fewer ads, upload photographs, create an RV blog, send private messages and so much, much more!

Old 11-19-2013, 08:56 AM   #16
Member
 
Join Date: Oct 2010
Posts: 80
Yea, it looks like I'm going to have to remove the fan motor & replace it. Guess when I get up there, I'll have to figure out how to get it out. It has a Styrofoam box over the squirrel cage part so I'll have to see how to remove that without busting it up.
cubano222 is offline   Reply With Quote
Old 11-26-2013, 10:44 AM   #17
Member
 
Join Date: Oct 2010
Posts: 80
I don't get it. It's too cold here for the compressor to start but I turned the fan motor on several times last weekend, at least 10 times over 2 days, & it came on every time, moving lots of air & spinning freely. If my fan motor is bad, why does it come on so many times & then every once in a while, just hums, even with new capacitor?
cubano222 is offline   Reply With Quote
Old 11-26-2013, 11:06 AM   #18
Senior Member
 
aschuh53's Avatar
 
Ford Super Duty Owner
Join Date: May 2013
Posts: 1,126
has a bad spot on the armitcher that is why
aschuh53 is offline   Reply With Quote
Old 11-26-2013, 11:56 AM   #19
Senior Member
 
Join Date: Feb 2010
Posts: 4,654
Fan motor is shaded pole, no brushes so no windings in armature.

If will run with push then starting issue.

Confirm correct cap, then ohm out windings.

Also confirm wiring via diagram, easy to get copies but exact model model.
__________________
Tony & Lori
1989 Country Coach Savannah SE
TQ60 is offline   Reply With Quote
Old 11-27-2013, 07:19 PM   #20
Senior Member
 
Roosters 67's Avatar
 
Join Date: Nov 2013
Posts: 214
Jerry,

The fan motors are not that hard to replace on most standard design roof units. last one I did required seperating the evaporator case(cold side, inside coil), removing the styrofoam insulation and removing every screw that held the condenser (hot side, or outside coil) shroud to the pan. Once I had the condenser loose from the pan, i had to move it slightly up and away from the fan. The copper lines will flex as needed, just avoid to much bending of the lines. Don't recall where I got the motor from but it was online and ran about $115 shipped. While I had it apart I went ahead and replaced the capacitors, after all they are cheap enough.

Get all the numbers and specs off of the existing motor and some google action should find a replacement.

Good Luck my friend,
Spence
__________________
Spencer & Tracie RVM#62
2013 RAM 3500DRW 4x4 Laramie, Cummins, 385HP,850FTLBS Aisin Trans
2014 DRV Elite Suite 41RESB4
Spare puller:2004 RAM3500DRW Cummins (DW's truck)
Roosters 67 is offline   Reply With Quote
Old 11-28-2013, 04:27 AM   #21
Senior Member
 
94-Newmar's Avatar
 
Join Date: Nov 2009
Posts: 2,043
Quote:
Originally Posted by Heating man View Post
That black capacitor you are talking about is a start capacitor these have to come out of the circuit after the motor starts usually by a relay. The metal case capacitors are run capacitors they are in the circuit all the time. Normally start capacitors are used to start the compressor not the fan motor. Probably that start capacitor was for the compressor. You probably have a dead spot in the windings of the motor and if it stops on that point it will not restart. Motor is probably bad and will need to be replaced.
Cubano, Heating Man has it correct. The round black capacitor is indeed the start capacitor for the compressor, not the fan. I don't know how they tested them, but checking them with a multimeter that will test capacitance (micro/pico/nano/farads) still isn't a real world test with high voltage, amperage and load. Replace them all. After replacing them should you find it still is inconsistent in starting the fan I suggest checking amperage draw and voltage drop upon start-up/cycling with a good meter. It is entirely possible that you are getting a large voltage drop up there. I'm not telling you to simply throw parts at it, but in order to properly check voltage drop/amp draw you'll need to make sure that the capacitors are indeed good.
__________________
94-Newmar Kountry Star 40-KSDP
Spartan/Cummins 8.3C-300HP/Allison 3060 WTEC-II/25yr RV Tech RVIA Certified/Onan-Cummins Certified
94-Newmar is offline   Reply With Quote
Reply

Tags
roof



Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


» Featured Campgrounds

Reviews provided by


All times are GMT -6. The time now is 07:49 PM.


Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.