Old 01-15-2012, 09:54 AM   #1
Member
 
Join Date: Jun 2011
Posts: 50
Will 50 Amps run 3 AC's

I want to add a 3rd air conditioner, the hole/vent is already there as well as the wiring. Here's the thing. i have a 1989 Gulfstream Classic 36' The unit only has 30 amp, But has a 6500 watt onan generator. the rear ac is wired directly to the generator, no switch inside. you can only run the rear ac if the generator is running! very annoying.So i figured i would just wire the rear ac to its own 20 amp plug, that way i could just plug in the rear ac to most campgrounds 20 amp. But if i add a 3rd ac, do i change over to a 50 amp system? I was told that even 50 amp wont run 3 15000 BTU air conditioners. Should i just wire the other 2 Ac's to its own 20 amp plug? So i would have a total of 3 plugs, 1 30 amp and 2 20 amp plugs. I could plug the coach into a 30 amp plug and use a 50 amp plug with a splitter for both 20 amp plugs. Since it seems a lot of campgrounds have both a 30 and a 50 amp plug.Now this 2nd and 3rd air conditioner would only be used in extreme heat, like when im in Vegas during the summer. All 3 would be wired to the generator, which leads to another question.. will a 6500 watt generator run 3 Ac's? And will these plugs be up to code? It seems technically i would be bringing 80 amps into the coach. I have no idea on the legalities.
Krazzykitt is offline   Reply With Quote
Join the #1 RV Forum Today - It's Totally Free!

iRV2.com RV Community - Are you about to start a new improvement on your RV or need some help with some maintenance? Do you need advice on what products to buy? Or maybe you can give others some advice? No matter where you fit in you'll find that iRV2 is a great community to join. Best of all it's totally FREE!

You are currently viewing our boards as a guest so you have limited access to our community. Please take the time to register and you will gain a lot of great new features including; the ability to participate in discussions, network with other RV owners, see fewer ads, upload photographs, create an RV blog, send private messages and so much, much more!

Old 01-15-2012, 11:50 AM   #2
Moderator Emeritus
 
RickO's Avatar


 
Join Date: Jan 2007
Location: Litchfield Park, Arizona
Posts: 10,530
The term 50 amp service is a bit misleading... since it's actually TWO 120v 50amp legs coming into the coach so I would think a properly converted 50 amp rig would handle three AC units.

Rick
__________________
Rick, Nancy, Peanut & Lola our Westie Dogs & Bailey the Sheltie.

2007 Itasca Ellipse 40FD
RickO is offline   Reply With Quote
Old 01-15-2012, 02:55 PM   #3
Senior Member
 
Wizard's Avatar
 
Winnebago Owners Club
Freightliner Owners Club
Join Date: Mar 2007
Location: Home on the hill in Georgia
Posts: 2,742
As Rick stated is correct. Be sure 2 units are on one 50 amp leg and the other unit is wired to the other 50 amp power leg. I would also recommend the water heater and microwave be on the single unit leg.
__________________
Jerry Potter, Taz
1999 Coachman Catalina Sport
[SIGPIC][/SIGPIC]
Wizard is offline   Reply With Quote
Old 01-15-2012, 03:29 PM   #4
Senior Member
 
Join Date: Apr 2010
Posts: 661
I have 3 AC/heat pumps in my rig and they run fine on a conventional 50 amp plug in. They are wired from the factory so that if the clothes dryer is running, only 2 AC's will run at the same time.
bucks2 is offline   Reply With Quote
Old 01-15-2012, 04:09 PM   #5
Senior Member
 
Join Date: Sep 2011
Posts: 982
With a code standard RV 50amp circuit (yes it IS a 240v circuit) and if you load balance the two legs, you can run 3 15kBTU A/Cs AND clothes dryer AND convection oven and plenty more (like elec water heater) all at the same time.

15kBTU A/C will max out at about 16amp ea that's only 48 amps of the 100 amps available on the RV 50amp standard circuit.... Make sure to distrubute the expected loads as evenly as you can across L1 and L2.

An RV 30amp plug is a 120v circuit and thus has only one "leg" and provides only 30amps. Similar to a 20amp 120v circuit thus providing only 20amps.

A standard RV 50amp has 2 50amp 120v "legs" for a total of 100amps at 120v (equivalently 50amps at 240v) because this by code standard is a 240v circuit. The RV 50amp is the exact same outlet used for residential stoves and the like. The 30amp RV outlet is, by code, used ONLY for RV service and no other application and is 120v.

If this does not make sense to you, seek a qualified electrician. (just make sure they don't accidentally wire the RV 30amp plug at 240v "because it looks like it is a 240v" as the RV 30amp is very uniquely and by code ONLY a 120v circuit. It happens regularly.)

A properly sized genset to power a 50amp RV circuit will be >10,000watts (usually 12,500watts)
ottffss is offline   Reply With Quote
Old 01-15-2012, 05:04 PM   #6
Member
 
Join Date: Jun 2011
Posts: 50
So if 3 ac's require 48 amps then it migbt be possible to run all 3 with a 6500 watt generator? Probably couldnt run anything else but it seems possibel. I talked to an electrician and it appears I would only have to change out the converter box with a single phase 50 amp box, change the poor mans switch box.. I don't have an automatic one but will add one. And of course ill need the actual 50 amp cable. It appears this unit had an optional 50 amp system that could be added. The wires that go to where a 3rd AC can be added are capped off behind the 30 amp converter. Which is actually a 45 amp converter. The generator puts out 52 amps. Doesnt really make sense to me why the manufacturer would only use a 30 amp system when it's wired for more.
Krazzykitt is offline   Reply With Quote
Old 01-15-2012, 06:06 PM   #7
Senior Member
 
Pusherman's Avatar
 
Join Date: Oct 2006
Location: Rochester NY
Posts: 2,706
Ohm's Law: Watts = Volts x Amps.

A 20A 120V circuit provides 2400 watts of power. This is a typical '20A' service for a motorhome.
A 30A 120V circuit provides 3600 watts of power. This is a typical '30A' service for a motorhome.

A 50A 240 circuit provides 12,000 watts of power. This is a typical '50A' service for a motorhome.

Now, an RV air conditioner draws about 12 amps of current at 120V = 1440 watts.

2-AC's draw 2880 watts.

3-AC's therefore will draw 4320 watts of power.

As you can see, a 20A 120V service will supply enough wattage for 1-AC unit.

A 30A 120V service will supply enough wattage for 2-AC units.

A 50A 240V service has plenty of wattage to run 3-AC units. Your generator will have to supply at least 4320 watts of continuous power to run all 3 AC's at once. Mine's a 7500 watt generator.

Simple math.
__________________
Don
'07 Winnebago Journey 34H - CAT C7, Koni's, MCU's, SS Bell Crank, Safe-T-Plus
'07 HHR Toad, SMI AFO, Blue OX
Pusherman is offline   Reply With Quote
Old 01-15-2012, 07:47 PM   #8
Senior Member
 
Dave78Chief's Avatar
 
Join Date: Jun 2009
Posts: 1,528
One thing to remember is while a 12,000 -13,000 btu ac will pull 12-13 amps while running it will also need 25 or so amps for 2 secs during startup. The startup amps is what can result in a 50 amp leg shutting down if both AC's on one leg startup at the same time; (25*2)*120=6000 watts total at initial turn ON.

For the 6500 generator, it is divided into a 30 amp (normal RV supply) and a 20 amp rear AC service. It is 50 amps total (6500/120=54 amps) not 50 amps on each side.

Dave
__________________
Dave in Virginia
1978 Winnebago Chieftain
Dodge M400 - 440-3
Classic Winnebago Site: https://www.classicwinnebagos.com/forum/index.php
Dave78Chief is offline   Reply With Quote
Reply



Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Xantrex panel charging amps JLMunsil Alpine Coach Owner's Forum 14 09-06-2011 10:52 PM
Inverter - what will it run? BudtheDiplomat Monaco Owner's Forum 13 01-17-2011 07:25 PM
10th Anniversary Rally Package Payments Madame Boomer Texas Boomers 2 07-29-2010 05:33 AM
2nd Annual Last Hurrah at Deer Run Campground Doris Northeast Region 32 11-02-2009 05:20 PM
Generator AMPs available pocoloco Boondocking 4 06-12-2009 03:16 PM

» Featured Campgrounds

Reviews provided by


All times are GMT -6. The time now is 04:09 AM.


Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.