40Hz to 60Hz Generator frequency

Hi Guys.

I have an Onan 6.5 kW LPG generator which is running nicely. It run exactly at 1800 rpm and it produces also 120V.

Now I have an inverter (Xantrex Freedom 2000W) which also works like a charm. The problem is when I try to charge the batteries with the generator the inverter will not 'accept' the current as it reads 40Hz coming from the generator at 120V (on the display). I have yet to measure the wave with an oscilloscope.

They funny thing is when I turn my rear A/C on and put load on the generator you can hear the generator putting on load, RPM stay around 1800 but now the magic happens: the Inverter reads now 60Hz from the Generator and 'accepts' the signal. Hence it charges batteries.

I don't want to always run a heavy load to have the batteries charged so any clue what can cause this weird phenomena?

Again the RPM is OK. No drops or overshoots, voltage reads OK. Just needs significant load to get to 60Hz otherwise 40Hz.
Rick3010 is offline   Reply With Quote
Join the #1 RV Forum Today - It's Totally Free!

iRV2.com RV Community - Are you about to start a new improvement on your RV or need some help with some maintenance? Do you need advice on what products to buy? Or maybe you can give others some advice? No matter where you fit in you'll find that iRV2 is a great community to join. Best of all it's totally FREE!

You are currently viewing our boards as a guest so you have limited access to our community. Please take the time to register and you will gain a lot of great new features including; the ability to participate in discussions, network with other RV owners, see fewer ads, upload photographs, create an RV blog, send private messages and so much, much more!

Old 09-18-2020, 11:16 AM   #2
Senior Member
 
HarryStone's Avatar


 
Damon Owners Club
Join Date: Apr 2020
Location: Clovis NM
Posts: 4,389
Blog Entries: 4
It sounds like your tach is in error, or your generator idles at 1800 RPM. According to what I found, is that at idle, your generator puts out 40 Hz, and at full throttle, 2880 RPM, puts out between 58 and 62 Hz. So, apparently, with your inverter on, and nothing else, the generator isn't sensing a load, and is staying at idle.
__________________
2006 Damon Daybreak 3276 35'with 5 Star Tuner. 3 200 Amp Lithium batteries and 2000 watt PSW inverter/charger. 2013 Elantra on a Master Tow dolly.
Retired USAF
HarryStone is offline   Reply With Quote
Old 09-18-2020, 01:58 PM   #3
Junior Member
 
Join Date: Sep 2020
Posts: 7
Quote:
Originally Posted by HarryStone View Post
It sounds like your tach is in error, or your generator idles at 1800 RPM. According to what I found, is that at idle, your generator puts out 40 Hz, and at full throttle, 2880 RPM, puts out between 58 and 62 Hz. So, apparently, with your inverter on, and nothing else, the generator isn't sensing a load, and is staying at idle.
Hey that's an interesting thought which I will test today. I have a buddy coming over so we can test a few more things like signals with the oscilloscope.

Maybe we test your hypnosis first: Check RPM at Idle and at load look if there is linear correlation with the frequency.

Even if this is the case I'm in trouble because it is a chicken-egg story. The Inverter does not take the signal when not at 58-62 hertz, gen set does not make 60 hertz unless there is a draw.

Don't want to have to put a big resistor somewhere just to trigger this
Rick3010 is offline   Reply With Quote
Old 09-18-2020, 02:11 PM   #4
Senior Member
 
Join Date: Jun 2017
Posts: 2,807
Well, that's about a worthless generator. How much load does it need to change to 60 Hz? How do you think small AC motors feel about that 40 Hz? Would a residential fridge even start or kick the generator up to speed?


For the OP: If you start the A/C and now the inverter becomes happy, can you turn off the A/C and the inverter load be enough to continue charging?
aether_one is offline   Reply With Quote
Old 09-18-2020, 02:52 PM   #5
Junior Member
 
Join Date: Sep 2020
Posts: 7
Quote:
Originally Posted by tfryman View Post
Well, that's about a worthless generator. How much load does it need to change to 60 Hz? How do you think small AC motors feel about that 40 Hz? Would a residential fridge even start or kick the generator up to speed?


For the OP: If you start the A/C and now the inverter becomes happy, can you turn off the A/C and the inverter load be enough to continue charging?
Ha, yes that is the first thing I tried but it switches back to 40Hz on the inverter display hence kicking off the signal again.
Rick3010 is offline   Reply With Quote
Old 09-18-2020, 03:25 PM   #6
Senior Member
 
Join Date: Jul 2014
Posts: 35,442
You don't say what year your unit is but on the new ones the engine turn 2880 RPMs.

The generator head is belt driven to 3600 RPMs for 60 HZs.

They don't idle at all, only inverter style generators idle. They run at constant speed. What your hearing is the load changing the sound.

Read the specs of your unit to see what constant speed the engine should run.
twinboat is offline   Reply With Quote
Old 09-18-2020, 04:28 PM   #7
Senior Member
 
Corc's Avatar
 
Thor Owners Club
Freightliner Owners Club
Join Date: Feb 2018
Location: Huntsville, AL.
Posts: 249
There is no idle on your generator, constant speed at all loads. What you are likely seeing is waveform distortion from cheap electronic switching type devices. This would smooth out at even slightly heavier loads. This would not be seen on shore power, since it has a VERY large ‘backup’.

You would have to figure out which device in your electrical system is causing the distortion or extra zero crosses. Could actually even be your Ground Fault AC outlet. A filter could then be used. Alternative generator, maybe a new voltage regulator. Have see this before, it is odd and rare, but understood in tight generator circles.
__________________
Huntsville, Alabama
2018 Thor Palazzo 33.2
2009 Jeep Liberty
Corc is offline   Reply With Quote
Old 09-20-2020, 09:48 AM   #8
Junior Member
 
Join Date: Sep 2020
Posts: 7
The oscilloscope gave the breakthrough. We measured during load 62Hz but without load a whopping 79 Hz. The inverter read 39Hz so roughly half that. Likely the inverter did not register all peaks at that high frequency. So instead of suspect low RPM the generator now seemed to do too high. I looked into that and indeed saw 2200 instead 1800 at no load. Tuned the Gen set to 1850 at no load and now it works like a charm. Governor needed some finetuning.
Rick3010 is offline   Reply With Quote
Old 09-20-2020, 11:45 AM   #9
Senior Member
 
HarryStone's Avatar


 
Damon Owners Club
Join Date: Apr 2020
Location: Clovis NM
Posts: 4,389
Blog Entries: 4
__________________
2006 Damon Daybreak 3276 35'with 5 Star Tuner. 3 200 Amp Lithium batteries and 2000 watt PSW inverter/charger. 2013 Elantra on a Master Tow dolly.
Retired USAF
HarryStone is offline   Reply With Quote
Old 09-20-2020, 07:07 PM   #10
Senior Member
 
Corc's Avatar
 
Thor Owners Club
Freightliner Owners Club
Join Date: Feb 2018
Location: Huntsville, AL.
Posts: 249
Great job, it all works. Sounds like you still have wave form distortion. Would be interesting to see what you get with breakers on gen thrown.

However; if it all works move on to the next item that is broke.
__________________
Huntsville, Alabama
2018 Thor Palazzo 33.2
2009 Jeep Liberty
Corc is offline   Reply With Quote
Reply

Tags
generator



Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
What is your frequency in changing Oil in D/P and the Generator Kro1957 Class A Motorhome Discussions 32 08-15-2017 06:40 PM
Generator service frequency Smitty77 RV Systems & Appliances 8 04-04-2016 10:49 PM
Checking frequency output and voltage output of Onan 5000 Genset Generator. MajesticRV MH-General Discussions & Problems 4 11-07-2012 10:16 AM
k7wn on frequency! Texigan CB & Ham Radio 2 03-12-2009 06:22 AM
Generator Frequency is High Warren&Renee MH-General Discussions & Problems 8 08-06-2008 03:05 AM

» Featured Campgrounds

Reviews provided by


All times are GMT -6. The time now is 10:17 AM.


Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.