If you've proven that you are getting propane by doing the steps above. Here's some possibilities:
1) you say you have power. Does that mean you're plugged in to shore power, or that your on batteries and the blower is running. The blower must have enough power to move enuf air to 'make' the sail switch. If not, the safety system will not allow the igniter to energize and the gas valve to open
2)If all above is OK, is the igniter gap correct? Should be about 1/16 to 1/8"
3) If still OK, is the thermocouple responding? If furnace lights (go outside and listen) then shuts off, the T/C is probably bad. Easy to replace (but not fun when it's 20 deg out)
4) Still no luck, most likely the control board has failed.