Old 05-28-2008, 11:28 AM   #1
Junior Member
 
TruckMechanic's Avatar
 
Join Date: Feb 2006
Location: Newburgh, NY
Posts: 28
I have a Kohler 7CCKMR61 Generator and it is suffering from low AC voltage output. I am currently reading 95 AC Volts at 1800 RPM. I removed the panel for the circuit breakers at the generator and read the line voltage at the generator itself. These are the readings from the generator. I get the same voltage at the AC outlet when I throw the generator switch on.

Question: How does one go about increasing the AC voltage on this generator?

On Edit: Changed RPMs to AC Voltage
__________________
https://truckroadservice.com/Mini-Barth.jpg1991 Barth Regal

460 EFI C6 Transmission
TruckMechanic is offline   Reply With Quote
Join the #1 RV Forum Today - It's Totally Free!

iRV2.com RV Community - Are you about to start a new improvement on your RV or need some help with some maintenance? Do you need advice on what products to buy? Or maybe you can give others some advice? No matter where you fit in you'll find that iRV2 is a great community to join. Best of all it's totally FREE!

You are currently viewing our boards as a guest so you have limited access to our community. Please take the time to register and you will gain a lot of great new features including; the ability to participate in discussions, network with other RV owners, see fewer ads, upload photographs, create an RV blog, send private messages and so much, much more!

Old 05-28-2008, 11:28 AM   #2
Junior Member
 
TruckMechanic's Avatar
 
Join Date: Feb 2006
Location: Newburgh, NY
Posts: 28
I have a Kohler 7CCKMR61 Generator and it is suffering from low AC voltage output. I am currently reading 95 AC Volts at 1800 RPM. I removed the panel for the circuit breakers at the generator and read the line voltage at the generator itself. These are the readings from the generator. I get the same voltage at the AC outlet when I throw the generator switch on.

Question: How does one go about increasing the AC voltage on this generator?

On Edit: Changed RPMs to AC Voltage
__________________
https://truckroadservice.com/Mini-Barth.jpg1991 Barth Regal

460 EFI C6 Transmission
TruckMechanic is offline   Reply With Quote
Old 05-28-2008, 03:28 PM   #3
Senior Member
 
Damon Owners Club
Join Date: Jun 2006
Location: Middletown,OH
Posts: 183
You may NOT have a 'speed' problem. You need to measure the frequency as well. The voltage adjustment on my kohler konfidant is located behind the 'visible' panel in the genset. You may have to remove the mounting screws to get to the pots(potentiometers) .

cheers.
__________________
Dave

Callsign: KD8W
hamdave is offline   Reply With Quote
Old 05-28-2008, 04:03 PM   #4
Junior Member
 
TruckMechanic's Avatar
 
Join Date: Feb 2006
Location: Newburgh, NY
Posts: 28
<BLOCKQUOTE class="ip-ubbcode-quote"><div class="ip-ubbcode-quote-title">quote:</div><div class="ip-ubbcode-quote-content">Originally posted by hamdave:
You may NOT have a 'speed' problem. </div></BLOCKQUOTE>Sorry, I don't know why I put speed down - I meant to say Volts
__________________
https://truckroadservice.com/Mini-Barth.jpg1991 Barth Regal

460 EFI C6 Transmission
TruckMechanic is offline   Reply With Quote
Old 05-29-2008, 03:36 AM   #5
Moderator Emeritus
 
Gary RVRoamer's Avatar


 
Join Date: Jan 2000
Location: West Palm Beach, FL. USA
Posts: 28,639
Unless that is an inverter type generator (unlikely in that vintage) both frequency and voltage are dependent on an exact speed (RPMs). Typically in a gas generator the speed will be 3600 RPMS, but you said yours is running at 1800 (but perhaps geared to drive the armature at 3600?).
__________________
Gary Brinck
Former owner of 2004 American Tradition and several other RVs
Home is now West Palm Beach, FL
Gary RVRoamer is offline   Reply With Quote
Old 05-29-2008, 02:51 PM   #6
Senior Member
 
Join Date: Dec 2007
Location: Blairsville,GA
Posts: 257
1800 rpm is one of the speeds generators use, they just double the number of poles. It is a much quieter genset than the 3600 rpm models, the only drawback is heavy loads fluctuate the voltage easier.
Hillbilly2 is offline   Reply With Quote
Old 05-31-2008, 04:59 PM   #7
Senior Member
 
Join Date: May 2005
Posts: 733
Onan has some models whose engines run at 2400 RPM that belt drive the alternator at 3600.If the the subject genset is one of these,then the revs need to be increased to increase the voltage to a usable level.In any event,use an electric clock to check hertz(RPM)
__________________
04 Southwind 37C W22

DIY Rear Panhard Rod
exrench is offline   Reply With Quote
Reply



Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Low DC voltage MA4529 Newmar Owner's Forum 7 07-23-2008 11:33 PM
Battery Voltage How Low is TOO LOw??? Latitude MH-General Discussions & Problems 5 01-08-2008 02:11 PM
Low Voltage Alarm BobD Workhorse and Chevrolet Chassis Motorhome Forum 2 07-02-2006 12:23 PM

» Featured Campgrounds

Reviews provided by


All times are GMT -6. The time now is 12:35 AM.


Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2025, vBulletin Solutions, Inc.