Hi All:

I have a 50 amp Motorhome with a hardwired Progressive EMS system. When I plugged into the electrical pedestal at the park yesterday, only one A/C would run.

I checked the Progressive display and it is reading for both Line 1 and 2 that it is drawing close to 120 volts, but the amp reading is very low. 4 amps on one line and 0-2 on the other line. Shouldn't it be reading much higher?

Do you know what would be the cause of such a low amp reading?

When I disconnect from the power pedestal and run my onboard generator, both air conditioners run fine.

I confess that I don't understand all I need to know about the electrical system and your help is very much appreciated!

Mark
Mark Lane is offline   Reply With Quote
Join the #1 RV Forum Today - It's Totally Free!

iRV2.com RV Community - Are you about to start a new improvement on your RV or need some help with some maintenance? Do you need advice on what products to buy? Or maybe you can give others some advice? No matter where you fit in you'll find that iRV2 is a great community to join. Best of all it's totally FREE!

You are currently viewing our boards as a guest so you have limited access to our community. Please take the time to register and you will gain a lot of great new features including; the ability to participate in discussions, network with other RV owners, see fewer ads, upload photographs, create an RV blog, send private messages and so much, much more!

Old 06-03-2023, 08:41 AM   #2
Senior Member
 
xrated's Avatar
 
Join Date: Jan 2017
Location: "Murvul", TN
Posts: 1,595
Quote:
Originally Posted by Mark Lane View Post
Hi All:

I have a 50 amp Motorhome with a hardwired Progressive EMS system. When I plugged into the electrical pedestal at the park yesterday, only one A/C would run.

I checked the Progressive display and it is reading for both Line 1 and 2 that it is drawing close to 120 volts, but the amp reading is very low. 4 amps on one line and 0-2 on the other line. Shouldn't it be reading much higher?

Do you know what would be the cause of such a low amp reading?

When I disconnect from the power pedestal and run my onboard generator, both air conditioners run fine.

I confess that I don't understand all I need to know about the electrical system and your help is very much appreciated!

Mark
If everything runs fine with the genny, that may be an issue with your automatic transfer switch. I would check it out as a first place to look.
__________________
2016 F350 Crew Cab Dually Diesel King Ranch 4x4
2018 Grand Design Momentum 394M Toy Hauler
Excessive Payload Capacity is a Wonderful Thing!
xrated is online now   Reply With Quote
Old 06-03-2023, 08:44 AM   #3
Senior Member
 
Join Date: Oct 2014
Posts: 7,278
Quote:
Originally Posted by Mark Lane View Post
Hi All:

I have a 50 amp Motorhome with a hardwired Progressive EMS system. When I plugged into the electrical pedestal at the park yesterday, only one A/C would run.

I checked the Progressive display and it is reading for both Line 1 and 2 that it is drawing close to 120 volts, but the amp reading is very low. 4 amps on one line and 0-2 on the other line. Shouldn't it be reading much higher?

The voltage of 120 VAC is perfect.



The amp reading depends totally on what you are running in your RV. If nothing is on, zero amps are being used. If both A/C's are running both L1 and L2 will show higher readings since you are using more power.

What was on in your RV when you got the "very low" amp rating?


What did not run on shore power?
__________________
Brett Wolfe
Ex: 2003 Alpine 38FDDS. Ex: 1997 Safari Sahara. Ex: 1993 Foretravel U240
wolfe10 is offline   Reply With Quote
Old 06-03-2023, 09:15 AM   #4
Senior Member
 
Join Date: Aug 2016
Location: Payson, AZ
Posts: 1,251
i'm assuming the ems is wired into the shore power line before the transfer switch.

if everything works from the generator then you problem is between the ems output and the shore power input of the transfer switch.

the ems displays the voltage from its input side and the amperage that is flowing through it. since it shows voltage on both legs it is getting input power.

you problem is most likely a loose connection. it it could be that the ems is not passing both legs of its input power or the transfer switch in not passing both legs of shore power input to its outputs. or perhaps a disconnection in a junction box between the two. it should be quite easy to find by tracing voltage with a multimeter. and the correction is probably to reattach the loose cable and tighten the connection.

but you say you are not real familiar with electrical work. do not work on it while it is live unless you are confident with what you are doing. you would be working around live 120 volt circuits!!!

one thing you could do, again if you feel confident, is to completely unplug from shore power. then you could open the case of the ems and the transfer switch to visually look for a loose connection. you might find it and be able to fix it. if you don't feel capable your best bet might be to call a mobile rv mechanic.

you problem is is a very constrained location which should be very easy to find. it is resolvable!
bigchick is offline   Reply With Quote
Old 06-03-2023, 09:41 AM   #5
Junior Member
 
Freightliner Owners Club
Overland Owners Club
Join Date: Apr 2020
Posts: 9
Thank you very much for your suggestions and guidance!
Mark Lane is offline   Reply With Quote
Old 06-03-2023, 11:38 AM   #6
Senior Member
 
Tha_Rooster's Avatar
 
Join Date: Aug 2008
Location: Georgia
Posts: 8,580
Quote:
Originally Posted by Mark Lane View Post
Hi All:

I have a 50 amp Motorhome with a hardwired Progressive EMS system. When I plugged into the electrical pedestal at the park yesterday, only one A/C would run.

I checked the Progressive display and it is reading for both Line 1 and 2 that it is drawing close to 120 volts, but the amp reading is very low. 4 amps on one line and 0-2 on the other line. Shouldn't it be reading much higher?

Do you know what would be the cause of such a low amp reading?

When I disconnect from the power pedestal and run my onboard generator, both air conditioners run fine.

I confess that I don't understand all I need to know about the electrical system and your help is very much appreciated!

Mark


No way you could have airs running at 4 amps.
Are you sure you have power on L1 and L2?
Have you turned pedestal breaker on and off?
__________________
2007 Fleetwood Revolution LE 40V
Tha_Rooster is offline   Reply With Quote
Old 06-03-2023, 12:49 PM   #7
Senior Member
 
Newmar Owners Club
Entegra Owners Club
Join Date: Dec 2015
Posts: 1,475
Suspect problem in the shore power pedestal, the shore power plug, the Progressive decide or its wiring, the shore power cord reel connectors, the Automatic Transfer Switch or its wiring.
Are you reading the voltages/currents on the display on the Progressive power monitor or are you reading from the display inside the coach?
It sounds like you are dropping one of the 2 legs of shore power.
__________________
2021 Entegra Aspire 44W
Previous: 2006 Newmar Essex 4508
2013 Tiffin Allegro Open Road
Archer2 is offline   Reply With Quote
Old 06-03-2023, 01:01 PM   #8
Junior Member
 
Freightliner Owners Club
Overland Owners Club
Join Date: Apr 2020
Posts: 9
Well, new wrinkle.

I didn't find any loose connections and both air conditioners worked fine on shore power until 1 pm today when the back a/c started clicking again trying to start the compressor.

Thinking it was some low voltage in the park during the heat of the day, I unhooked power at the pedestal and turned on the generator. But now that same air conditioner in the back still won't start the compressor. It tries, but shuts off immediately. It tries again at short intervals.

Does it sound like now, it was really an air conditioning problem all along?

Should I consider changing the control panel in the air conditioner?

Thanks for your guidance.
Mark Lane is offline   Reply With Quote
Old 06-03-2023, 05:47 PM   #9
Senior Member
 
chuckftboy's Avatar
 
Winnebago Owners Club
Fleetwood Owners Club
Holiday Rambler Owners Club
Join Date: Dec 2011
Location: North East Florida
Posts: 1,869
Might be as simple as a bad run capacitor or start capacitor on the a/c that is dropping out. If you have a bad run capacitor the compressor will draw high amps and eventually go out on its thermal overload.
__________________
2019 Horizon 42Q
Cummins L-9 450 HP
Maxum Chassis / IFS with Tag
chuckftboy is offline   Reply With Quote
Old 06-03-2023, 07:23 PM   #10
Senior Member
 
2004Horizon's Avatar
 
Join Date: May 2023
Posts: 558
Everything above is possible.

Off hand, did you open your ATS can torque down your lugs?

Mark Lane:

What is your RV year and model?

Do you have a basement AC or rooftop?

Any idea on what type of ATS you have?

What generator are you running?

Note: If you have pre-2010 RV with an Onan QD7500/QD8000, then all these questions need to be answered.
__________________
2004 Itasca Horizon 40AD
2004Horizon is offline   Reply With Quote
Old 06-04-2023, 03:10 AM   #11
Junior Member
 
Freightliner Owners Club
Overland Owners Club
Join Date: Apr 2020
Posts: 9
Thank you!

Thanks to all who helped with this issue. I have a RV Tech coming out this afternoon to look into all that you have suggested. I will give you an update when it is solved.

Many thanks for taking the time to help!
Mark Lane is offline   Reply With Quote
Old 06-04-2023, 04:46 PM   #12
Senior Member
 
TimmyB's Avatar
 
Join Date: Apr 2019
Location: Florida, originally Michigan
Posts: 1,410
Quote:
Originally Posted by Mark Lane View Post
Thanks to all who helped with this issue. I have a RV Tech coming out this afternoon to look into all that you have suggested. I will give you an update when it is solved.

Many thanks for taking the time to help!
We had a similar problem at our "home" park in FL, where we stay for 7 months. Right after we arrived, we noticed one of the AC's kept turning off, especially when we would fire up the other one or the microwave or the dryer, etc. Both sides of the pedestal read correctly at around 120V. What we DIDN'T know was to check them together. Should have read 240V; it read .3V!!! They simply split one 120 line and ran it to BOTH sides, giving the impression that it was a 50A site. Our Hughes PWD50 was tricked into thinking everything was OK, but only at 30A. Make sure your pedestal is wired truly at 240. Might save you a lot of work.
__________________
==============================
2020 Fleetwood Bounder 35P, Blue Ox Avail towbar, Blue Ox Patriot II brake system, EezTire TPMS system, 2021 Ford Ranger Tremor (toad)
TimmyB is offline   Reply With Quote
Old 06-07-2023, 02:05 PM   #13
Junior Member
 
Freightliner Owners Club
Overland Owners Club
Join Date: Apr 2020
Posts: 9
Update

Hi All:

Thanks again for all your suggestions. Here's where I am.

The park checked out the electrical pedestal and said it was good.
The RV Tech did the following:
Checked all the capacitors (start, run, and thermal) and they all showed they were good.
Compressor tested as good.
Cleaned the coils thoroughly with a no rinse coil cleaner.
Opened the Progressive EMS and tightened all the lugs. (a couple would turn an 1/8 of a turn)
Opened the Automatic Transfer Switch and tightened all the lugs (again a couple of them would turn a slight amount).

It has not acted up again until today. The pattern is early to mid afternoon in the heat (Texas). It has a couple of false starts where it tries to click on, but fails. It repeats the process every minute or two and then the compressor starts and everything is fine.

Could the start capacitor test okay, but be slowly failing?

Thanks again for your input!
__________________
1998 Odessa Overland Lorado - 41.5'
Cummins Diesel, Allison Transmission
Toad - 2015 Jeep Renegade with Acme Tow Dolly
Mark Lane is offline   Reply With Quote
Old 06-07-2023, 02:17 PM   #14
Senior Member
 
Join Date: Oct 2014
Posts: 7,278
What is the AC voltage when this happens?
__________________
Brett Wolfe
Ex: 2003 Alpine 38FDDS. Ex: 1997 Safari Sahara. Ex: 1993 Foretravel U240
wolfe10 is offline   Reply With Quote
Reply

Tags
electric, electrical, problem



Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Please please help with gray water problem ParryTack Class A Motorhome Discussions 108 04-01-2013 08:56 AM
Electrical problem, please help Abo Nour Class A Motorhome Discussions 2 04-10-2011 05:17 PM
electrical problem need help!!!! please PEPPER9950 Class A Motorhome Discussions 4 10-04-2010 06:10 AM

» Featured Campgrounds

Reviews provided by


All times are GMT -6. The time now is 05:55 AM.


Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2023, vBulletin Solutions, Inc.