Not being able to run generator during winter storage

I've always stored my motor home outdoors. I run the generator under load (gas) every month for at least a 1/2 hour. I have an opportunity to store indoors in a heated building at a reasonable price but there is now access to run the generator. So my generator would not be ran 4 to 5 months. I know this isn't good but in my mind it seems to outweigh the wear and tear from outdoor storage. Last winter it got so cold in Ohio my bathroom floor split.
Any thoughts?
Flick is offline   Reply With Quote
Join the #1 RV Forum Today - It's Totally Free!

iRV2.com RV Community - Are you about to start a new improvement on your RV or need some help with some maintenance? Do you need advice on what products to buy? Or maybe you can give others some advice? No matter where you fit in you'll find that iRV2 is a great community to join. Best of all it's totally FREE!

You are currently viewing our boards as a guest so you have limited access to our community. Please take the time to register and you will gain a lot of great new features including; the ability to participate in discussions, network with other RV owners, see fewer ads, upload photographs, create an RV blog, send private messages and so much, much more!

Old 10-13-2014, 02:37 PM   #2
Senior Member
 
BFlinn181's Avatar
 
Gulf Streamers Club
Join Date: Jan 2012
Location: Cincinnati
Posts: 19,925
Use Sea Foam in the carb and I think the indoor storage will do no harm to the generator. Being out of the weather should be better for the rest of the RV.
__________________

Bob & Donna
'98 Gulf Stream Sun Voyager DP being pushed by a '00 Beetle TDI
BFlinn181 is offline   Reply With Quote
Old 10-13-2014, 02:47 PM   #3
Senior Member
 
dennis45's Avatar
 
Join Date: Jun 2012
Location: AB
Posts: 7,587
Here's my take,
The reason for running the generator under load at regular intervals is to keep the windings from accumulating moisture since, during normal operation, the generator is exposed to varying temperatures and humidity.

So, If you are storing the coach in a heated facility, even if only moderately heated, the chances of moisture accumulation is virtually nil. Storage inside a heated facility trumps all.
__________________
2019 Unity LTV CB, pushed by a 2013 Honda CRV, BlueOx Baseplate, Aventa Bar & Patriot Brake
dennis45 is offline   Reply With Quote
Old 10-14-2014, 06:09 AM   #4
Senior Member
 
Murf2u's Avatar
 
Join Date: Aug 2011
Location: Near Toronto, Canada
Posts: 1,842
Quote:
Originally Posted by dennis45 View Post
The reason for running the generator under load at regular intervals is to keep the windings from accumulating moisture since, during normal operation, the generator is exposed to varying temperatures and humidity.

The problem with that theory is that warming the generator would only burn off the moisture 1 day out of 30. It would also leave a warm generator cooling off in damp winter weather so the condensation would be right back within hours.

I have a friend with an old Onan 4kw unit from an RV that powers his off-grid island summer place. It gets Sea Foam and Sta-bil early each fall and never touched till the end of May and has for years.

It starts and run perfectly each spring. No problem.
__________________
Ted 'n' Laurie, plus Jackson (aka Deputy Dog, the Parson Russell Terrier 'fur kid') and, Rylie (who crossed the Rainbow Bridge June 14, 2012).
Murf2u is offline   Reply With Quote
Old 10-20-2014, 02:05 PM   #5
Senior Member
 
Join Date: Jun 2014
Posts: 118
New to RVing and Generators, please enlighten me on what Sea Foam is and where to purchase it. Also, I have anti gel conditioner in the MH main fuel tank for the winter months, gen set runs off of main fuel tank.
__________________
Dave, Vanessa & Mindye
SFC E-7, US Army Retired
2003 Kit Road Ranger 5th Wheel
dvkiel is offline   Reply With Quote
Old 10-20-2014, 02:08 PM   #6
Senior Member
 
BFlinn181's Avatar
 
Gulf Streamers Club
Join Date: Jan 2012
Location: Cincinnati
Posts: 19,925
Quote:
Originally Posted by dvkiel View Post
New to RVing and Generators, please enlighten me on what Sea Foam is and where to purchase it. Also, I have anti gel conditioner in the MH main fuel tank for the winter months, gen set runs off of main fuel tank.
Sea Foam is a fuel system cleaner. You can read about it here and find where to buy:

Homepage - Sea Foam Sales Company
__________________

Bob & Donna
'98 Gulf Stream Sun Voyager DP being pushed by a '00 Beetle TDI
BFlinn181 is offline   Reply With Quote
Old 10-20-2014, 06:57 PM   #7
Senior Member
 
94-Newmar's Avatar
 
Join Date: Nov 2009
Posts: 2,043
Onan has always recommended monthly exercises for their gensets, gasoline or diesel. In all actuality it has more to do with the field brushes becoming stuck in the brush holder or becoming stuck on the slip rings from sitting for so long. The absolute worst thing to do is start it and only let it run a few minutes with zero load on it and never coming up to running temperature. So IF you are not able to move your coach outside once a month to exercise the generator properly, then the next best thing would be to simply allow it to turn over just once or twice without starting. This will help prevent the brushes from becoming stuck in the brush holder and help to prevent them sticking to the slip rings and breaking the brushes.
__________________
94-Newmar Kountry Star 40-KSDP
Spartan/Cummins 8.3C-300HP/Allison 3060 WTEC-II/25yr RV Tech RVIA Certified/Onan-Cummins Certified
94-Newmar is offline   Reply With Quote
Old 10-20-2014, 07:06 PM   #8
Senior Member
 
Mr_D's Avatar
 
Country Coach Owners Club
Solo Rvers Club
iRV2 No Limits Club
Join Date: May 2011
Location: Vancouver, WA
Posts: 37,725
Quote:
Originally Posted by Murf2u View Post
The problem with that theory is that warming the generator would only burn off the moisture 1 day out of 30. It would also leave a warm generator cooling off in damp winter weather so the condensation would be right back within hours.
Not a "theory", running the gen for an hour or so each month is exactly what most of the gen set manufacturers say to do.
__________________
2009 45' Magna 630 w/Cummins ISX 650 HP/1950 Lbs Ft, HWH Active Air
Charter Good Sam Lifetime Member, FMCA,
RV'ing since 1957, NRA Benefactor Life, towing '21 Jeep JLU Rubicon Ecodiesel
Mr_D is offline   Reply With Quote
Old 10-20-2014, 07:13 PM   #9
Community Administrator
 
NLOVNIT's Avatar


 
Pond Piggies Club
LA Gulf Coast Campers
Outdoors RV Owners Club
Entegra Owners Club
Skyline Owners Group
Join Date: Mar 2002
Posts: 40,765
Blog Entries: 1
I'm not going to say what I do is right or wrong, just what I do & it's worked for 9 seasons. When we winterize in Oct, Stabil goes in the fuel tank & the gen is run under full load for at least an hour while I'm doing interior packing/cleaning. Then it's shut off & not started until at least April as it's stored in a place not easy for us to get to over winter.

Lori-
__________________
Lori (& Dave, my spirit guide) - RV/MH Hall of Fame Lifetime Member | My iRV2 Photo Albums
2016 Phoenix Cruiser 2350S, 2018 Phaeton 40IH,2006 Bounder 36Z, 2004 Cougar 285EFS, 2000 Aerolite 25FBR
There is great need for a sarcasm font.
NLOVNIT is offline   Reply With Quote
Old 10-20-2014, 07:28 PM   #10
Senior Member
 
Murf2u's Avatar
 
Join Date: Aug 2011
Location: Near Toronto, Canada
Posts: 1,842
Quote:
Originally Posted by Mr_D View Post
Not a "theory", running the gen for an hour or so each month is exactly what most of the gen set manufacturers say to do.

You mean the manufacturers who have a bunch of lawyers writing all that crap that they hope will get them out of a warranty claim or lawsuit?

Yes, I said "theory", do you have facts and or scientific data to prove otherwise? Because I have proof that running an engine a few minutes a month versus putting it away properly is a poor choice.
__________________
Ted 'n' Laurie, plus Jackson (aka Deputy Dog, the Parson Russell Terrier 'fur kid') and, Rylie (who crossed the Rainbow Bridge June 14, 2012).
Murf2u is offline   Reply With Quote
Old 10-20-2014, 07:45 PM   #11
Community Administrator
 
NLOVNIT's Avatar


 
Pond Piggies Club
LA Gulf Coast Campers
Outdoors RV Owners Club
Entegra Owners Club
Skyline Owners Group
Join Date: Mar 2002
Posts: 40,765
Blog Entries: 1
Let's watch the tone folks. Community Rules:
Quote:
Do not engage in personal attacks. Challenge others' points of view and opinions, but do so respectfully and thoughtfully.
Lori-
__________________
Lori (& Dave, my spirit guide) - RV/MH Hall of Fame Lifetime Member | My iRV2 Photo Albums
2016 Phoenix Cruiser 2350S, 2018 Phaeton 40IH,2006 Bounder 36Z, 2004 Cougar 285EFS, 2000 Aerolite 25FBR
There is great need for a sarcasm font.
NLOVNIT is offline   Reply With Quote
Old 10-21-2014, 11:32 AM   #12
Senior Member
 
Workhorse Chassis Owner
Join Date: Jun 2003
Location: Palisade CO
Posts: 3,588
It appears that the addition of ethanol to gas in the last few years has caused build ups of varnish in the carbs of small engines when they sit for some time.
I used to be able to run the gen every few months (in a dry climate) and had no problems but three years ago I had a hip replacement and didn't run it for a whole summer.
Before we headed south I could not get it to start. In our winter RV park I worked on it. I could get it to run (very roughly) by holding the choke down. After doing that for a while it would run for a while with the choke released. Finally the carb got clean enough for the gen to run normally.

This year we are no longer snow birding so I added Stabil to the motor home fuel tank, waited a few days for it to mix with the 50 gallons of fuel in the tank and ran the gen for about an hour.
I will find out in the spring if this will work or not.
__________________
Clay WA5NMR - Ex Snowbird - 1 year, Ex Full timer for 11 years - 2004 Winnebago Sightseer 35N Workhorse chassis. Honda Accord toad.
Clay L is offline   Reply With Quote
Old 10-21-2014, 12:29 PM   #13
Community Moderator


 
Join Date: Aug 2011
Posts: 6,200
Seafoam really works well to remove the varnish. Stabil is more of a prevention then a "treatment" once the varnish has taken hold.
pasdad1 is offline   Reply With Quote
Old 10-21-2014, 12:38 PM   #14
Senior Member
 
BFlinn181's Avatar
 
Gulf Streamers Club
Join Date: Jan 2012
Location: Cincinnati
Posts: 19,925
I agree with Clay L, gasoline doesn't do well in long storage, especially in carburetors. Stabil and SeaFoam can help. It's interesting that the reason to run the generator monthly is being given as to keep the brushes, stator, and windings in good condition, not the passages in the carb. Of course diesel and LP generators don't suffer from varnish and the issues of the gasoline models. In a perfect world running the generator to keep the electrical parts shiny and bright would be a good idea, but I think it's a bit overstated that you'll suffer doom from letting it rest through the winter. The electrical contacts mentioned are mostly copper and will be buffed shiny after a long winter's rest within seconds of starting to spin. JMHO
__________________

Bob & Donna
'98 Gulf Stream Sun Voyager DP being pushed by a '00 Beetle TDI
BFlinn181 is offline   Reply With Quote
Reply

Tags
generator, storage, winter



Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Winter usage of 2009 DADP TButterfield Newmar Owner's Forum 22 10-17-2014 12:54 AM
Inverter to run Microwave? Wayco RV Systems & Appliances 16 08-04-2014 04:21 AM
Genset won't run. 2travel Class A Motorhome Discussions 5 05-25-2014 07:06 PM
Inverters, BIRD and Storage usdave1t Newmar Owner's Forum 7 04-02-2014 07:24 PM
Wondering how many days will a tank of propane lasts heating a coach in winter ? Markrving iRV2.com General Discussion 13 08-01-2013 09:12 AM

» Featured Campgrounds

Reviews provided by


All times are GMT -6. The time now is 12:30 AM.


Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.