06-16-2022, 08:14 PM
|
#1
|
Senior Member
Join Date: Nov 2020
Location: South Dakota
Posts: 445
|
Quietpac 75D stops producing power when hot
My generator runs great until it gets very hot outside. It runs for a while, then loses all ac power. It stays off for a minute or so, then comes back on. It does it 2 or 3 times, then I need to shut down the generator and restart
Then the same thing happens until it cools off then fund good until it gets hot. Temp outside today was 102 when it stopped working.
Is there a thermal cutoff switch on these generators?
__________________
2004 Rexhall Roseair. 3955ET 370
|
|
|
|
Join the #1 RV Forum Today - It's Totally Free!
iRV2.com RV Community - Are you about to start a new improvement on your RV or need some help with some maintenance? Do you need advice on what products to buy? Or maybe you can give others some advice? No matter where you fit in you'll find that iRV2 is a great community to join. Best of all it's totally FREE!
You are currently viewing our boards as a guest so you have limited access to our community. Please take the time to register and you will gain a lot of great new features including; the ability to participate in discussions, network with other RV owners, see fewer ads, upload photographs, create an RV blog, send private messages and so much, much more!
|
06-17-2022, 01:45 AM
|
#2
|
Senior Member
Join Date: Mar 2019
Location: Braidwood Il.
Posts: 8,300
|
Down load manual . shows how to retrieve fault codes . Its common for high temp and oil pressures switches to get bad. Don't 100% trust antifreeze level in recovery tank ,if caps get old it can stop drawing liquid back when engine cools, pull rad cap to check for sure. The radiator can get dirty and there's a fan belt that runs the radiator fan can get old.
.
__________________
95 Monaco Crown Royale
M11 400hp, 4060 trans.
Aquahot, Generac Guardian7.5k
|
|
|
06-18-2022, 05:24 AM
|
#3
|
Senior Member
Join Date: Aug 2008
Location: Georgia
Posts: 8,638
|
Quote:
Originally Posted by bduemig
My generator runs great until it gets very hot outside. It runs for a while, then loses all ac power. It stays off for a minute or so, then comes back on. It does it 2 or 3 times, then I need to shut down the generator and restart
Then the same thing happens until it cools off then fund good until it gets hot. Temp outside today was 102 when it stopped working.
Is there a thermal cutoff switch on these generators?
|
Is it throwing codes?
__________________
2007 Fleetwood Revolution LE 40V
|
|
|
06-19-2022, 04:47 AM
|
#4
|
Senior Member
Join Date: Nov 2020
Location: South Dakota
Posts: 445
|
My.manual doesn't show how our if I can retract codes. I did pull the radiator cap and found coolant level low but the overflow tank.was full. I need to get b the specs on the cap and order va new one.
__________________
2004 Rexhall Roseair. 3955ET 370
|
|
|
06-19-2022, 07:29 AM
|
#5
|
Senior Member
Newmar Owners Club
Join Date: Dec 2011
Posts: 724
|
Look at the voltage regulator, might be failing due to heat.
__________________
2002 KSDP 3669/Freightliner XC CHASSIS/Cummins 5.9 ISB 300hp
Joplin, MO
|
|
|
06-20-2022, 04:44 PM
|
#6
|
Senior Member
Join Date: Nov 2020
Location: South Dakota
Posts: 445
|
Thank you. I will n check the voltage regulator
__________________
2004 Rexhall Roseair. 3955ET 370
|
|
|
07-07-2022, 12:36 PM
|
#7
|
Senior Member
Join Date: Nov 2020
Location: South Dakota
Posts: 445
|
Well, it is not the voltage regulator or the circuit breaker next to it.
Is out time to take it to a shop or is there something else I can check?
__________________
2004 Rexhall Roseair. 3955ET 370
|
|
|
07-07-2022, 07:44 PM
|
#8
|
Senior Member
Join Date: Mar 2019
Location: Braidwood Il.
Posts: 8,300
|
The psi should be on cap auto parts will have one. Most common issues is to stop drawing back fluid from expansion tank.once they get large air pocket in the top it stops working. Then just compresses air like old large top tank radiators worked before recover tanks. Problem is these new engines and radiators are designed to be free of even the smallest air pockets.
You need to retrieve codes. There are repair and diagnostic manuals online for practical all RV Onan generators online.
Before smart ones with codes was common to just replace temp and out pressure switch if there was a problem.
.An exhaust leak caused my radiator to plug up with carbon on my 75D Generac. With all the covers off I replaced , brushes, inline fuel strainer,weak starter,alt. belt . The fan belt looked new. I repaired exhaust flex pipe with stainless NPT pipe much higher quality rated over 100psi.
__________________
95 Monaco Crown Royale
M11 400hp, 4060 trans.
Aquahot, Generac Guardian7.5k
|
|
|
07-08-2022, 05:54 AM
|
#9
|
Senior Member
Newmar Owners Club
Join Date: Dec 2011
Posts: 724
|
Generac doesn’t have retrievable codes.
__________________
2002 KSDP 3669/Freightliner XC CHASSIS/Cummins 5.9 ISB 300hp
Joplin, MO
|
|
|
07-10-2022, 09:22 AM
|
#10
|
Senior Member
Gulf Streamers Club Ford Super Duty Owner
Join Date: Aug 2015
Location: Memphis, TN
Posts: 4,338
|
If 75D is water cooled, thermals should shut down engine, not electric, in my diesel experience, so if just doing electric, I would more suspect a circuit board solder issue, or loose wire somewhere that is disconnecting under higher loads? CAN BE a SCREW connection, or a PUSH-ON at a circuit board, or a simple circuit board loose solder joint?
__________________
(TerryH.) 2000-GS Conquest Limited 6266 Class-C 99-E450SD V10
|
|
|
|
Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
|
|