Old 06-22-2021, 05:26 PM   #1
Senior Member
 
volvik's Avatar
 
Join Date: Jan 2013
Location: Vancouver Island, BC
Posts: 349
Rear A/C stalls Generator

Situation:

2 x 20a AC units.

Generator on, AC1 (front) on and works no problem. Turn AC2 (rear) on and generator stalls. The generator will stall when AC2 is turned on regardless if AC1 is on or not.

Shore power plugged into a house 15a circuit. AC1 turned on works no problem. AC1 turned off. AC2 turned on and nothing happens at all.

In the morning I will go up on the roof and remove the cover for AC2 to inspect the coils for cleaning.

In the meantime, is it possible that the culprit is the 20a breaker? This is the first test since winterizing in the fall.

Thanks in advance!
__________________
2007 Fleetwood Southwind
volvik is offline   Reply With Quote
Join the #1 RV Forum Today - It's Totally Free!

iRV2.com RV Community - Are you about to start a new improvement on your RV or need some help with some maintenance? Do you need advice on what products to buy? Or maybe you can give others some advice? No matter where you fit in you'll find that iRV2 is a great community to join. Best of all it's totally FREE!

You are currently viewing our boards as a guest so you have limited access to our community. Please take the time to register and you will gain a lot of great new features including; the ability to participate in discussions, network with other RV owners, see fewer ads, upload photographs, create an RV blog, send private messages and so much, much more!

Old 06-22-2021, 09:32 PM   #2
Senior Member
 
windsorbill's Avatar
 
Monaco Owners Club
Join Date: Jun 2011
Location: CA
Posts: 3,699
Quote:
Originally Posted by volvik View Post
Situation:

2 x 20a AC units.

Generator on, AC1 (front) on and works no problem. Turn AC2 (rear) on and generator stalls. The generator will stall when AC2 is turned on regardless if AC1 is on or not.

Shore power plugged into a house 15a circuit. AC1 turned on works no problem. AC1 turned off. AC2 turned on and nothing happens at all.

In the morning I will go up on the roof and remove the cover for AC2 to inspect the coils for cleaning.

In the meantime, is it possible that the culprit is the 20a breaker? This is the first test since winterizing in the fall.

Thanks in advance!
Your generator wouldn't stall if the breaker was bad. It would trip the breaker or the breaker wouldn't set at all. See if your motor on the roof will rotate. My first thought is that AC compressor is frozen and not repairable.
__________________
Bill & Brigitte
06 Windsor PEQ, Cummins 400 ISL
2014 Honda CRV
windsorbill is offline   Reply With Quote
Old 06-22-2021, 09:32 PM   #3
Senior Member
 
Diesel-Lover's Avatar
 
Join Date: Nov 2002
Location: OH
Posts: 729
There are many possibilities and a piece meal checking of the components is called for. If you look at the wiring diagram you may find the circuit breaker is the same one that is handling the load when plugged into the shore power.


If the start capacitors are the issue it may be a good time to also put in a soft start to make every thing work smoothly and reducing the drain jolts on compressor startup. Best of luck and keep us posted.
__________________
RUSTIC is good.
Kudos to those who make Local, State & Federal Parks & Campgrounds possible and to those picking up the slack by Providing Private Campgrounds.
Diesel-Lover is offline   Reply With Quote
Old 06-22-2021, 10:02 PM   #4
Senior Member
 
Damon Owners Club
Join Date: Apr 2020
Posts: 2,299
Blog Entries: 3
Agreed. You have an AC problem, not a generator issue
__________________
2006 Damon Daybreak 3276 35'with 5 Star Tuner. 3 200 Amp Lithium batteries and 2000 watt PSW inverter/charger. 2013 Elantra on a Master Tow dolly.
Retired AF
HarryStone is offline   Reply With Quote
Old 06-23-2021, 10:44 AM   #5
Senior Member/RVM #90
 
MSHappyCampers's Avatar


 
Monaco Owners Club
Join Date: Nov 2002
Location: Columbus, MS
Posts: 47,951
I would suspect that the A/C compressor is locking up, but I would think it would trip the breaker.
__________________
Joe & Annette
Sometimes I sits and thinks, sometimes I just sits.....
2002 Monaco Windsor 40PBT, 2013 Honda CRV AWD
MSHappyCampers is offline   Reply With Quote
Old 06-23-2021, 11:19 AM   #6
Senior Member
 
96 Wideglide's Avatar
 
Holiday Rambler Owners Club
Join Date: Aug 2010
Posts: 7,897
Quote:
Originally Posted by windsorbill View Post
Your generator wouldn't stall if the breaker was bad. It would trip the breaker or the breaker wouldn't set at all. See if your motor on the roof will rotate. My first thought is that AC compressor is frozen and not repairable.
This sounds like the most likely cause.

If you get on the roof and everything spins freely, may want to look at the capacitors.
__________________
Ben & Sharon
2008 43' Holiday Rambler Scepter PDQ
96 Wideglide is online now   Reply With Quote
Old 06-23-2021, 06:07 PM   #7
Senior Member
 
jacwjames's Avatar
 
Monaco Owners Club
Join Date: Jun 2014
Posts: 9,454
My front AC was pulling high amps when starting and eventually started to trip the breaker. It was also louder.
So I got on the roof, pulled the cover off and tried to spin the blower motor, could barely move it by hand.

So I bought a new motor for ~$125 ~6 years ago and it replace. One thing I found also was that the rubber isolation pads on the motor were essentially wore out letting the squirrel cage fan hit the metal. The new motor came with new rubber pads.

That fixed the problem, AC runs good and is a lot quieter.
__________________
Jim J
2002 Monaco Windsor 38 PKD Cummins ISC 350 8.3L
2005 Jeep Grand Cherokee w/5.7 Hemi
jacwjames is offline   Reply With Quote
Old 06-23-2021, 06:54 PM   #8
Senior Member
 
volvik's Avatar
 
Join Date: Jan 2013
Location: Vancouver Island, BC
Posts: 349
Well I poked around more, read more, tried more all without much success so I'm going to pass this AC issue onto a shop. One additional thing that did happen which may explain the generator stall when I tried to turn that one AC unit.

I tried to start the generator today and it would turn over but not run. When I had a look at the unit I noticed it was giving a fault code......#27. Something about Controller unable to sense output voltage etc and sadly the remedy is to take it to an Onan Service Rep. Now the AC unit should still have worked off the 15a house circuit I'm plugged into as I did try that with the other AC turned off.

I'm hoping that it's an AC unit repair and not replace as so many parts are hard to get during Covid.

The AC unit is an AirXcel which has since been replaced with a Coleman Mach I believe.
__________________
2007 Fleetwood Southwind
volvik is offline   Reply With Quote
Old 06-23-2021, 07:12 PM   #9
Community Moderator
 
Lt Dan's Avatar


 
Tiffin Owners Club
Join Date: Sep 2013
Location: DFW, Texas
Posts: 10,778
I just had the same thing happen with our front A/C. When it tried to start you could hear the generator sort of stall. I watched the power draw and saw a 60 amp pull when it tried to start. The breaker didn't trip as it takes an over amp draw over a longer period. That high of an amperage draw indicates a locked rotor condition and I replaced the unit yesterday.
__________________
2017 Phaeton 40IH XSH Maroon Coral - Power Glide Chassis with IFS
Previously '15 Tiffin Allegro RED 38QRA and '06 Itasca Sunrise 35A
'16 Jeep JKU Wrangler Sahara or '08 Honda Goldwing
Lt Dan is offline   Reply With Quote
Old 06-24-2021, 07:53 PM   #10
Senior Member
 
Gulf Streamers Club
Ford Super Duty Owner
Join Date: Aug 2015
Location: Memphis, TN
Posts: 2,387
If AC over-amping, it should trip the 20a breaker; if not, maybe breaker contacts welded shut?
__________________
(TerryH.) 2000-GS Conquest Limited 6266 Class-C 99-E450SD V10
THenne1713 is offline   Reply With Quote
Old 06-24-2021, 08:09 PM   #11
Senior Member
 
96 Wideglide's Avatar
 
Holiday Rambler Owners Club
Join Date: Aug 2010
Posts: 7,897
Quote:
Originally Posted by volvik View Post

I tried to start the generator today and it would turn over but not run. When I had a look at the unit I noticed it was giving a fault code......#27. Something about Controller unable to sense output voltage etc and sadly the remedy is to take it to an Onan Service Rep.
That could be a bad one like thrown magnets, bad control box, or like when I had a fault code #27, and once I got the top panel off, found a wire connector came apart !
__________________
Ben & Sharon
2008 43' Holiday Rambler Scepter PDQ
96 Wideglide is online now   Reply With Quote
Old 06-25-2021, 04:21 PM   #12
Senior Member
 
volvik's Avatar
 
Join Date: Jan 2013
Location: Vancouver Island, BC
Posts: 349
Ok well I know believe that the generator stalling is a different issue and while Onan fault code 27 suggests a controller issue I now recall 5 years ago I had a similar issue when the generator was under any load it would stall and/or when it was very hot out (like it is now) it would turn over but not run. When I put a new fuel filter in at that time the problem went away. The auto shop will have one for me in the morning so I'll change that then.

Now for the rear AC, I opened the service panel and put a meter lead on AC2 (rear unit) and the neg on the service panel neutral bar. The reading was 3.0v. The breaker is on during this test. When I then test AC1 (front unit) I get a reading of 107.x v.

Oddly enough the water heater only gives me 3.0v as well. The microwave, fridge and general small appliances give the 107v)

The circuit breaker for AC2 is a Murray MP2020. It's a tandem breaker, 20a for the AC and a 20a for a general appliance breaker.

Odd?
__________________
2007 Fleetwood Southwind
volvik is offline   Reply With Quote
Old 06-30-2021, 11:14 PM   #13
Senior Member
 
Gulf Streamers Club
Ford Super Duty Owner
Join Date: Aug 2015
Location: Memphis, TN
Posts: 2,387
Cycle Breker, it is half tripped
__________________
(TerryH.) 2000-GS Conquest Limited 6266 Class-C 99-E450SD V10
THenne1713 is offline   Reply With Quote
Old 07-01-2021, 10:23 PM   #14
Senior Member
 
volvik's Avatar
 
Join Date: Jan 2013
Location: Vancouver Island, BC
Posts: 349
Nope, already checked that possibility.

However what I have done is taken the wire from that AC circuit breaker in the coach service panel and then started the generator. It started fine and then I turned that AC breaker on and the generator continued to run instead of quitting. I then metered the circuit breaker and it read 120v.

So, the generator is providing power to that circuit breaker which now leads me to believe that the problem is upstream from the circuit breaker ie: from it's power lead from the CB to the AC unit on the roof.

I assume if there's a short somewhere it will cause the generator to die. Odd that the generator CB didn't trip and quit instead.

I have read that a symptom of a bad AC start capacitor is that the unit wont start and could give low voltage. Low voltage is also one of the reasons listed in the Onan fault code 27 I get when it dies.
__________________
2007 Fleetwood Southwind
volvik is offline   Reply With Quote
Reply

Tags
generator, rear



Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Generator stalls when going around bend supergroomer MH-General Discussions & Problems 10 06-09-2012 09:13 AM
Generator cranks, but immediately stalls Learn2Q RV Systems & Appliances 10 03-31-2011 02:03 AM
Generator Stalls gMw MH-General Discussions & Problems 9 12-08-2007 12:57 PM
Generator stalls on bumps drp46 New Member Check-In 5 08-20-2007 01:14 PM

» Featured Campgrounds

Reviews provided by


All times are GMT -6. The time now is 11:45 AM.


Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2021, vBulletin Solutions, Inc.