When A Portable Generator Won’t Power Your RV

I received this email from a reader who wants to power his RV from a Honda portable generator.

I have a 2011 Fleetwood 40-footer. I am trying to get my Honda EU3000 generator to power up the motorhome for a few items. My display after plugging in will show NO LOAD. This generator will power anything else I try such as a 30-foot trailer with one air conditioner, compressor, etc. I also have a Coleman 5000 and that will power up the motorhome. I have an adapter cord 50-amp female going to 30-amp (3 prong) male. The Honda worked with my 2002 Monaco hooking the same way. The reason I like to use the Honda is when I am at the track this time of year, there is no need to run the motorhome generator since there is no need for air conditioning. I have called Honda and they where no help. John Z., (Purcellville, VA)

John, all RV electrical systems are wired with their Ground and Neutral buses floated (un-bonded from each other). There’s lots of good reasons for this, most specifically that it’s an NEC and RVIA code requiment that the safety ground wire never carries any load current, and there can be only one Ground-To-Neutral bonding point in any distributed electrical system in the USA. Now, when you’re plugging your RV into power from a building (your garage outlet) or campground (pedestal outlet), your RV has its Ground and Neutral buses “bonded” (connected) together externally as part of the service panel’s earthed safety ground system. Again, lots of reasons for this, but the fact is you can only have a single G-N bonding point according to the National Electrical Code and RVIA building codes.

So when your RV is powered by its on-board generator, this G-N bond connection is created by the transfer switch set to generator mode. But when the transfer switch is set to receive shore power, your RV expects the external power source to bond its Ground and Neutral wires together. Now if you have an inline voltage monitor system from a manufacturer such as TRC or Progressive Industries, your voltage monitor is checking for the Neutral and Ground voltages to be very close to each other, probably within 3 volts or so. This works well if you’re plugged into shore power that’s properly grounded and bonded, but this voltage protector can be tripped off by plugging your RV shore power plug into a portable generator without an internal Ground-Neutral bond. If you don’t have a voltage protection device on your RV, then you may never know that your generator has a floated neutral (un-bonded G-N bus).

Contractor-type generators such as your Coleman 5000 are generally G-N bonded internally, which is why it runs your RV just fine. However, many portable inverter generators from companies such as Yamaha and Honda (your EU3000 specifically) have floated Neutrals (no internal Ground-Neutral Bond) since they expect an external G-N bond to happen somewhere else. And while RV-approved generators may have an internal G-N bond, it seems that many of the most popular portable inverter generators from Honda and Yamaha have floating neutrals. Now I discussed this very point with Honda engineering , and they confirmed that their inverter generators have floated Neutrals and simply say that you should follow all local electrical codes for bonding-grounding. So your EU3000 isn’t providing the Ground-Neutral Bond that your RV requires to think it’s getting properly grounded power, while your Coleman 5000 has a Ground-Neutral bond already so it operates your RV properly. Seems crazy, but that appears to be the scenario.

It’s pretty simple to wire a special “Ground-Neutral Bond” jumper cable for your Honda or Yamaha generator which will allow you to power your RV through its voltage protection device. You can obtain or make a dummy 15 or 20 amp “Edison” plug with the Neutral (white) and Ground (green) screws jump together with a piece of 12 or 14 gauge wire (see photos below). This G-N jumper plug can be plugged into one of the generator’s unused 20-amp outlets, and the entire generator’s electrical system will be N-G bonded. You can then use the other 20-amp Edison outlet or the 30-amp outlet to power the RV.



Just be sure to mark this plug specifically for its intended purpose. It won’t really hurt anything if it’s plugged into a correctly wired home outlet, but it will create a secondary G-N bonding point that could induce ground loop currents and create hum or buzz in a sound system.

So this is a generator-only G-N bonding plug which should be only plugged into a portable generator while powering your RV.





Mike Sokol











47 COMMENTS TO “GENERATOR GROUND-NEUTRAL BONDING”
Ray says:
April 14, 2013 at 11:40 pm
Thanks for the great information Mike. I have a Champion brand inverter generator with the floating neutral. I found out when I got a surge protector and it threw an error code when hooking up the generator. Lucky the surge protector had a bypass switch, but it would be nice to use it’s full functionality so thanks for the Edison plug tip.


This is what I did. It has worked fine with no problems so far. I had my personal Electrical Engineer, Son, look over this before I hooked it up to my MH and he agreed with the author of this article.
__________________
Roger And Kim Goodwin
bout them DAWGS!!
Roger G is offline   Reply With Quote
Join the #1 RV Forum Today - It's Totally Free!

iRV2.com RV Community - Are you about to start a new improvement on your RV or need some help with some maintenance? Do you need advice on what products to buy? Or maybe you can give others some advice? No matter where you fit in you'll find that iRV2 is a great community to join. Best of all it's totally FREE!

You are currently viewing our boards as a guest so you have limited access to our community. Please take the time to register and you will gain a lot of great new features including; the ability to participate in discussions, network with other RV owners, see fewer ads, upload photographs, create an RV blog, send private messages and so much, much more!

Old 02-11-2014, 04:36 PM   #58
Senior Member
 
SCVJeff's Avatar
 
Join Date: Dec 2006
Location: Santa Clarita, CA.
Posts: 2,644
My fix
__________________
_______________________________

Jeff - WA6EQU
'06 Itasca Meridian 34H, CAT C7/350
SCVJeff is offline   Reply With Quote
Reply

Tags
generator



Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


» Featured Campgrounds

Reviews provided by


All times are GMT -6. The time now is 03:06 AM.


Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.