Old 01-22-2021, 11:03 AM   #29
Senior Member
 
TimmyB's Avatar
 
Join Date: Apr 2019
Location: Florida, originally Michigan
Posts: 1,588
Quote:
Originally Posted by Fiesta48 View Post
I gave up on my heat pumps. We just use $20 space heaters now. Too expensive to maintain and replace heat pumps. 1 gave up but still works as A/C.
Ours has done a decent job so far, but I'm with you. I'll burn through a few portable $30 units before worrying about trying to fix something for four figures!

Thanks.
__________________
==============================
2020 Fleetwood Bounder 35P, Blue Ox Avail towbar, Blue Ox Patriot II brake system, EezTire TPMS system, 2021 Ford Ranger Tremor (toad)
TimmyB is offline   Reply With Quote
Join the #1 RV Forum Today - It's Totally Free!

iRV2.com RV Community - Are you about to start a new improvement on your RV or need some help with some maintenance? Do you need advice on what products to buy? Or maybe you can give others some advice? No matter where you fit in you'll find that iRV2 is a great community to join. Best of all it's totally FREE!

You are currently viewing our boards as a guest so you have limited access to our community. Please take the time to register and you will gain a lot of great new features including; the ability to participate in discussions, network with other RV owners, see fewer ads, upload photographs, create an RV blog, send private messages and so much, much more!

Old 01-25-2021, 09:19 AM   #30
Senior Member
 
Argosy's Avatar
 
Join Date: May 2004
Location: MI
Posts: 2,190
You're welcome, I hope it helps you long term.

FWIW it was a BIG job to find this. As this will be the third time you've had it in and knowing what they might have to do to find the problem I'd try to talk a little sense to them and "encourage" them to save time and money by replacing the furnace. Dometic is going to cover the cost of a new furnace, maybe the labor to replace it. At this point it doesn't make sense to keep trying to repair a problem they didn't create and are having a very difficult time finding.

Good luck!!
Argosy is online now   Reply With Quote
Old 01-25-2021, 09:30 AM   #31
Senior Member
 
TimmyB's Avatar
 
Join Date: Apr 2019
Location: Florida, originally Michigan
Posts: 1,588
Quote:
Originally Posted by Argosy View Post
You're welcome, I hope it helps you long term.

FWIW it was a BIG job to find this. As this will be the third time you've had it in and knowing what they might have to do to find the problem I'd try to talk a little sense to them and "encourage" them to save time and money by replacing the furnace. Dometic is going to cover the cost of a new furnace, maybe the labor to replace it. At this point it doesn't make sense to keep trying to repair a problem they didn't create and are having a very difficult time finding.

Good luck!!
Yeah, I plan on calling the service manager about this in the coming days and let him know of your experience. Thanks, again.
__________________
==============================
2020 Fleetwood Bounder 35P, Blue Ox Avail towbar, Blue Ox Patriot II brake system, EezTire TPMS system, 2021 Ford Ranger Tremor (toad)
TimmyB is offline   Reply With Quote
Old 01-31-2021, 07:46 PM   #32
Senior Member
 
Charlie 5320's Avatar
 
Join Date: Mar 2017
Posts: 698
You need to know the sequence of operation. It was in one of the earlier posts. You need a volt meter to check this out yourself. All the system does is call for heat, makes a switch between the r and w circuit on the furnace control board. R is 12v power and the W is the heat circuit on the control board. There should be a schematic for the furnace on the door or some where. Anyways, when the stat calls for heat it switches power to the W terminal on the board. The blower will start, close the sail switch, then the ignition will cycle, probably be a spark, you may or may not be able to hear, then the gas valve will open. The furnace will light , and if the control board isn't grounded thru the flame in so many seconds, it will go thru a retrial. MAKE SURE THE BOARD IS GROUNDED. Turn the stat up should be 12v + on the meter if not have to find out why. If 12v + move to the next item, sail switch, should be 12v + on both sides of the switch. If you do this test right after the furnace shuts off you will find out what the problem is. If you have 12v + on the sail switch move to the limit switch, verify that switch is working.
__________________
1996 Challenger 313

2003 Dolphin 5320 sold
Charlie 5320 is offline   Reply With Quote
Old 02-01-2021, 03:08 PM   #33
Senior Member
 
TimmyB's Avatar
 
Join Date: Apr 2019
Location: Florida, originally Michigan
Posts: 1,588
Quote:
Originally Posted by Charlie 5320 View Post
You need to know the sequence of operation. It was in one of the earlier posts. You need a volt meter to check this out yourself. All the system does is call for heat, makes a switch between the r and w circuit on the furnace control board. R is 12v power and the W is the heat circuit on the control board. There should be a schematic for the furnace on the door or some where. Anyways, when the stat calls for heat it switches power to the W terminal on the board. The blower will start, close the sail switch, then the ignition will cycle, probably be a spark, you may or may not be able to hear, then the gas valve will open. The furnace will light , and if the control board isn't grounded thru the flame in so many seconds, it will go thru a retrial. MAKE SURE THE BOARD IS GROUNDED. Turn the stat up should be 12v + on the meter if not have to find out why. If 12v + move to the next item, sail switch, should be 12v + on both sides of the switch. If you do this test right after the furnace shuts off you will find out what the problem is. If you have 12v + on the sail switch move to the limit switch, verify that switch is working.
Thanks. I appreciate the help.
__________________
==============================
2020 Fleetwood Bounder 35P, Blue Ox Avail towbar, Blue Ox Patriot II brake system, EezTire TPMS system, 2021 Ford Ranger Tremor (toad)
TimmyB is offline   Reply With Quote
Old 02-02-2021, 08:06 PM   #34
"Formerly Diplomat Don"
 
Dutch Star Don's Avatar
 
Newmar Owners Club
Join Date: Apr 2005
Location: Moorpark, Ca.
Posts: 24,090
I would go about this differently. I would call Precision Circuits and let one of their techs go through the system with you on the phone. Don't be afraid to explain to them that you need them to speak in plain English, not techno speak.

They may know exactly what is wrong and send you what you need.
__________________
Don & Mary
2019 Newmar Dutch Star 4018 (Freightliner)
2019 Ford Raptor
Dutch Star Don is offline   Reply With Quote
Old 02-02-2021, 08:44 PM   #35
Senior Member
 
TimmyB's Avatar
 
Join Date: Apr 2019
Location: Florida, originally Michigan
Posts: 1,588
Quote:
Originally Posted by Dutch Star Don View Post
I would go about this differently. I would call Precision Circuits and let one of their techs go through the system with you on the phone. Don't be afraid to explain to them that you need them to speak in plain English, not techno speak.

They may know exactly what is wrong and send you what you need.
I've already tried that. After talking with their tech, he was convinced that it could not be their control, simply because of how little their system does in the process of turning the furnace on our off. I'm planning on calling the service manager for REV next week and discussing the plan of attack.

Thanks for helping!
__________________
==============================
2020 Fleetwood Bounder 35P, Blue Ox Avail towbar, Blue Ox Patriot II brake system, EezTire TPMS system, 2021 Ford Ranger Tremor (toad)
TimmyB is offline   Reply With Quote
Old 02-03-2021, 10:20 AM   #36
Senior Member
 
Charlie 5320's Avatar
 
Join Date: Mar 2017
Posts: 698
Quote:
Originally Posted by Dutch Star Don View Post
I would go about this differently. I would call Precision Circuits and let one of their techs go through the system with you on the phone. Don't be afraid to explain to them that you need them to speak in plain English, not techno speak.

They may know exactly what is wrong and send you what you need.
And you would be wasting your time and their time. I've been in the HVAC field for 30 years and can't tell him where the problem is with out seeing the furnace. I would know where the problem is by watching the furnace one time most likely. The SYSTEM IS working, it IS telling the furnace to run. The problem IS in the furnace, period.
__________________
1996 Challenger 313

2003 Dolphin 5320 sold
Charlie 5320 is offline   Reply With Quote
Old 02-03-2021, 10:29 AM   #37
Senior Member
 
TimmyB's Avatar
 
Join Date: Apr 2019
Location: Florida, originally Michigan
Posts: 1,588
Quote:
Originally Posted by Charlie 5320 View Post
And you would be wasting your time and their time. I've been in the HVAC field for 30 years and can't tell him where the problem is with out seeing the furnace. I would know where the problem is by watching the furnace one time most likely. The SYSTEM IS working, it IS telling the furnace to run. The problem IS in the furnace, period.
I understand your sentiment, Charlie, but I'm not convinced for one VERY strange reason. When the issue happens, it not only happens to the furnace, it causes the rooftop heat pump/AC unit to stop working. The sequence of events is exactly as it should be for the first 10-15 minutes. Then, not only does the burner stop (while the blower continues), but the rooftop heat pump/AC unit, which was running perfectly for the past 10 hours with constant fan on whether there was a call for heat or not, suddenly stops. No fan running.

You being in the business for all of that time, maybe you can help me. What is there that when the issue happens, it causes a malfunction with BOTH the furnace and the rooftop AC unit? I'm totally without even a guess.

Thanks for any wisdom you can share my way!
__________________
==============================
2020 Fleetwood Bounder 35P, Blue Ox Avail towbar, Blue Ox Patriot II brake system, EezTire TPMS system, 2021 Ford Ranger Tremor (toad)
TimmyB is offline   Reply With Quote
Old 02-03-2021, 10:46 AM   #38
Senior Member
 
Old Scout's Avatar
 
Join Date: Nov 2005
Posts: 7,400
….haven't reviewed the whole thread but for most Dometic systems with a heat pump, there are three main components that must work in concert--the furnace, the heat pump and the thermostat. Somewhat beyond the obvious that all three have to be compatible and function properly, is that the dip switch config on the heat pump must be set correctly to support the furnace, eg, at low ambient temps [mid to low 30s] the heat pump locks out and the thermostat then starts the furnace automatically. Sorry if I missed it, have you already investigated and confirmed the dip switch settings?
__________________
Old Scout
2015 IH45 Foretravel
2003 Alpine 40' MDTS [Sold]
New Braunfels, Texas
Old Scout is offline   Reply With Quote
Old 02-03-2021, 10:49 AM   #39
Senior Member
 
Charlie 5320's Avatar
 
Join Date: Mar 2017
Posts: 698
Quote:
Originally Posted by TimmyB View Post
I understand your sentiment, Charlie, but I'm not convinced for one VERY strange reason. When the issue happens, it not only happens to the furnace, it causes the rooftop heat pump/AC unit to stop working. The sequence of events is exactly as it should be for the first 10-15 minutes. Then, not only does the burner stop (while the blower continues), but the rooftop heat pump/AC unit, which was running perfectly for the past 10 hours with constant fan on whether there was a call for heat or not, suddenly stops. No fan running.

You being in the business for all of that time, maybe you can help me. What is there that when the issue happens, it causes a malfunction with BOTH the furnace and the rooftop AC unit? I'm totally without even a guess.

Thanks for any wisdom you can share my way!
With out seeing the schematic for the system, it's just a guess, but. The heat pump is supposed to run first on most systems and IF it can't satisfy the call for heat in a length of time, the gas furnace will come on to satisfy the call and they BOTH shut down, when the call for heat is satisfied. Do you have the heat pump blower on auto or manual? Now your system most likely will have an outdoor stat the should keep the heat pump out of the circuit below a certain temp.

To test just the furnace, remove the wire from the R terminal on the furnace control board. Hook up a jumper wire from the R terminal to the W terminal, this will place a call for heat and the furnace SHOULD light and run till you remove the jumper wire. If it does NOT, the problem IS in the furnace. Then you have to trouble shoot the furnace. IF the furnace does work correctly, there may be a problem with the data cable on your system. I had that on my Dolphin a couple years ago, but I didn't have heat pumps to contend with.
__________________
1996 Challenger 313

2003 Dolphin 5320 sold
Charlie 5320 is offline   Reply With Quote
Old 02-03-2021, 10:55 AM   #40
Senior Member
 
Charlie 5320's Avatar
 
Join Date: Mar 2017
Posts: 698
Quote:
Originally Posted by Old Scout View Post
….haven't reviewed the whole thread but for most Dometic systems with a heat pump, there are three main components that must work in concert--the furnace, the heat pump and the thermostat. Somewhat beyond the obvious that all three have to be compatible and function properly, is that the dip switch config on the heat pump must be set correctly to support the furnace, eg, at low ambient temps [mid to low 30s] the heat pump locks out and the thermostat then starts the furnace automatically. Sorry if I missed it, have you already investigated and confirmed the dip switch settings?
Good comment, being this is a new coach, the setup could be where the problem is. Problem is, when he took the coach back for repair they just thru a new control board on it and let it go. Parts changers rarely have any idea how to repair.
__________________
1996 Challenger 313

2003 Dolphin 5320 sold
Charlie 5320 is offline   Reply With Quote
Old 02-03-2021, 11:02 AM   #41
Senior Member
 
TimmyB's Avatar
 
Join Date: Apr 2019
Location: Florida, originally Michigan
Posts: 1,588
Quote:
Originally Posted by Charlie 5320 View Post
With out seeing the schematic for the system, it's just a guess, but. The heat pump is supposed to run first on most systems and IF it can't satisfy the call for heat in a length of time, the gas furnace will come on to satisfy the call and they BOTH shut down. Now your system most likely will have an outdoor stat the should keep the heat pump out of the circuit below a certain temp.

To test just the furnace, remove the wire from the R terminal on the furnace control board. Hook up a jumper wire from the R terminal to the W terminal, this will place a call for heat and the furnace SHOULD light and run till you remove the jumper wire. If it does NOT, the problem IS in the furnace. Then you have to trouble shoot the furnace. IF the furnace does work correctly, there may be a problem with the data cable on your system. I had that on my Dolphin a couple years ago, but I didn't have heat pumps to contend with.
In the PCI board, they are two separate systems with two separate sensors (heat pump sensor in bedroom, furnace sensor in living room). I can (and most often, do) have them on separately. Since we have no "reliable" heat from the furnace, on a cold night (55 or below), we'll just put the rooftop heat pump on at about 67 with fan on constant HIGH. She works like she's supposed to the entire night. Only if I get up in the morning and try to warm the living room up with the gas furnace do I get any issue with the rooftop heat pump unit, and it only happens when the furnace has the issue. It takes 15 to 20 minutes to manifest itself, but it almost always does.
__________________
==============================
2020 Fleetwood Bounder 35P, Blue Ox Avail towbar, Blue Ox Patriot II brake system, EezTire TPMS system, 2021 Ford Ranger Tremor (toad)
TimmyB is offline   Reply With Quote
Old 02-03-2021, 11:04 AM   #42
Senior Member
 
TimmyB's Avatar
 
Join Date: Apr 2019
Location: Florida, originally Michigan
Posts: 1,588
Quote:
Originally Posted by Old Scout View Post
….haven't reviewed the whole thread but for most Dometic systems with a heat pump, there are three main components that must work in concert--the furnace, the heat pump and the thermostat. Somewhat beyond the obvious that all three have to be compatible and function properly, is that the dip switch config on the heat pump must be set correctly to support the furnace, eg, at low ambient temps [mid to low 30s] the heat pump locks out and the thermostat then starts the furnace automatically. Sorry if I missed it, have you already investigated and confirmed the dip switch settings?
No, I have no idea where to even look for these dip switches? Where might I find them?
__________________
==============================
2020 Fleetwood Bounder 35P, Blue Ox Avail towbar, Blue Ox Patriot II brake system, EezTire TPMS system, 2021 Ford Ranger Tremor (toad)
TimmyB is offline   Reply With Quote
Reply

Tags
ace, furnace



Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Winter Months: Better to drive or let sit 3-4 months JoJoKnight Jayco Owner's Forum 1 11-25-2018 08:39 PM
Fitness: 3 months in an RV vs. 3 months in a space ship NealC iRV2.com General Discussion 24 04-11-2018 08:05 AM
After 5 months...still looking! AB7R 5th Wheel Discussion 34 01-09-2017 07:00 PM
After months of research decided to go with Entegra Coach Seascapeguy Entegra Owner's Forum 47 03-25-2014 11:18 AM
3 months and still waiting for a new dash JCM Workhorse and Chevrolet Chassis Motorhome Forum 15 09-28-2006 03:02 AM

» Featured Campgrounds

Reviews provided by


All times are GMT -6. The time now is 08:20 PM.


Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.