We keep blowing a 15 amp fuse?

We have a 15amp bedroom light circuit that blew yesterday. When I replaced, it arched and blew again. Flipped the AC distribution beaker to the circuit off, and also cut off the main breaker. Replaced, and it arched and blew again! Don't believe there's anything on this circuit but the overhead fluoresc
__________________
Roger, Sandy & Phoebe
05 Monaco Knight 40PLQ
05monacoer is offline   Reply With Quote
Join the #1 RV Forum Today - It's Totally Free!

iRV2.com RV Community - Are you about to start a new improvement on your RV or need some help with some maintenance? Do you need advice on what products to buy? Or maybe you can give others some advice? No matter where you fit in you'll find that iRV2 is a great community to join. Best of all it's totally FREE!

You are currently viewing our boards as a guest so you have limited access to our community. Please take the time to register and you will gain a lot of great new features including; the ability to participate in discussions, network with other RV owners, see fewer ads, upload photographs, create an RV blog, send private messages and so much, much more!

Old 03-23-2011, 06:59 PM   #2
Senior Member
 
AFChap's Avatar
 
Forest River Owners Club
Join Date: Aug 2002
Location: ...East Texas
Posts: 5,325
You have a direct short on that circuit. The first thing to try is replacing the bulbs. If that doesn't work, take a look inside the switch. Beyond that, you will need to be able to trace the circuit wherever it goes ...you may have to get some assistance in tracking down the short.
__________________
Paul (KE5LXU) ...was fulltimin', now parttimin'
2022 Coachmen Leprechaun 319MB
towing 2017 Jeep Grand Cherokee Limited
AFChap is offline   Reply With Quote
Old 03-23-2011, 07:14 PM   #3
Senior Member
 
OLYLEN's Avatar
 
Monaco Owners Club
Join Date: Jan 2008
Location: Olympia, Wa
Posts: 2,772
First turn off all the lights you think are on that circuit. Then replace the fuse, if it blows again disconnect the wires from what you think is the offender. Replace fuse if it still blows then a direct short and might be tough to find. If it does not blow with switch/switch's off then the light lights are the problem, then replacing light bulbs or light fixtures is in order.

LEN
__________________
2004 Clss C 31' Winnebgo
OLYLEN is offline   Reply With Quote
Old 03-23-2011, 07:44 PM   #4
Senior Member
 
Happycarz's Avatar
 
Monaco Owners Club
Join Date: Sep 2007
Location: Scottsdale, AZ
Posts: 2,321
Instead of going through a bunch of fuses, just go to the auto parts supply and buy a 15 amp circuit breaker and install it. It will protect the circuit and will reset after tripping. As you move down the circuit and find the short to ground, your circuit breaker will reset and stay on.
__________________
Harry

2008 Monaco Camelot 40' PDQ
Happycarz is offline   Reply With Quote
Old 03-23-2011, 08:34 PM   #5
Junior Member
 
05monacoer's Avatar
 
Join Date: Feb 2011
Posts: 18
I do know there's a burned out bulb on that circuit. I'll replace it, then try replacing the fuse again. If it still blows, I may need to find help chasing down a direct short. I like the idea of replacing the fuse with a breaker. Thanks for the posts!
__________________
Roger, Sandy & Phoebe
05 Monaco Knight 40PLQ
05monacoer is offline   Reply With Quote
Old 03-23-2011, 09:59 PM   #6
Senior Member
 
dons2346's Avatar
 
Country Coach Owners Club
Join Date: Dec 2010
Posts: 7,804
Turning off the AC power will not help as this is most likely a 12VDC problem.

Why replace the fuse with a breaker? There is still a problem and it needs to be found. Disconnect everything that you can think of that is fed by 12VDC. Install the fuse and see what happens. If it doesn't blow, then start connecting one item at a time until the fuse blows. You have now found the culprit.
dons2346 is offline   Reply With Quote
Old 03-23-2011, 10:20 PM   #7
Senior Member
 
MegaRoadie's Avatar
 
Winnebago Owners Club
Workhorse Chassis Owner
Join Date: Feb 2011
Location: On the Road
Posts: 346
The problem will be found after the fire..... jeez where is common sense here ???

Find the darned short and fix it, or make sure you dont park next to me... I dont want my sidewalls melted in the upcoming fire !
__________________
05 Itasca Suncruiser, Stock w/ScanGuage II,
2017 Honda Accord TOAD,Home Based in Uniontown, Pa. Retired Navy Officer
MegaRoadie is offline   Reply With Quote
Old 03-23-2011, 10:32 PM   #8
Senior Member
 
Join Date: Feb 2010
Posts: 4,654
15 amp no-blow

Some folks insert a 1/4 inch bolt, works great, the smoke indicates the short...

Enough, get a blown fuse, a 12 volt light, some wire (2o ft of zip cord) and solder

Solder one conductor to each end of the blown fuse, the bulb to the other ends.

To test, hold fuse between hot and ground and the light goes on.

Yes, same as a test light, but this does not require you to hold it and 20 feet allows the light to be placed where it can be seen anywhere you are looking for the short.

Insert into fuse position with problem, the light should lightup.

Now start disconnecting things on that circuit, when light goes out, reconnect to see light come back on.

If this does not work then a wire is pinched, hand trace wire from fuse to loads, look for flat spots or where it goes through a panel.

Always make sure you can breake it after you think you fixed it. Reconnect the wire or push it back into the corner to make sure the problem can be restored, otherwise you may be working on a new issue.

Then after you have fixed it, continue checking for more shorts as these types of problems never travel alone, they like friends.
__________________
Tony & Lori
1989 Country Coach Savannah SE
TQ60 is offline   Reply With Quote
Old 03-24-2011, 05:47 AM   #9
Senior Member
 
H. Miller's Avatar
 
Monaco Owners Club
Texas Boomers Club
Join Date: Jan 2009
Posts: 2,529
Ours is an '04 Monaco product and we've done some electrical work in the bedroom area. It IS 12 volts so all the 120 VAC switching shouldn't effect it.
The Inner wall will be 1/4" plywood with a thick aluminum sheet underneath. Then 1-2" of "batt" insulation followed by the outside wall.
You'll probably find the fixture is grounded to the aluminum sheet or the "feed" wires have worn thru and are grounded.
Have you taken out the fixture?
We found all the cutout holes had VERY sharp edges in the aluminum
__________________
Hal & Ginny Miller '04 Beaver Santiam PRT40
'04 Saturn Vue - US Gear Brake - Blue Ox tow
3"girls" (2 Irish Setters - 1 Retriever) - RIP Annie & Emily (12/26/2017)
H. Miller is offline   Reply With Quote
Old 03-24-2011, 08:59 AM   #10
Senior Member
 
wa8yxm's Avatar
 
Damon Owners Club
Workhorse Chassis Owner
Join Date: Mar 2009
Posts: 24,024
First: The AC breaker most likely has no effect on this fuse as in most RV's fuses are used only in the DC circuit and that can be battery powered, You also said it is a lighting circuit and again, that is normally 12 volt so the only thing you can do with the AC breakers is kill the battery charger/converter.

Now, to the problem.. As others have said you have a short.. The MOST common location for shorts in 12 volt is the light socket itself, Turn OFF all the lights on that circuit and if the fuse holds (See next suggestion by the way) if the fuse holds turn them on one at a time When it blows, check that socket.

Others have suggested other places to check, Rather than repeat I'll just 2nd.

Suggestion 2:

Get a 12 volt light socket, I recommend a wedge type (This type of bulb has a flat "wedge" base with wires on the sides near each end) and a fairly large one (Back up lamp is good) Put tabs on the ends of the wires and replace the fuse with this lamp/socket assembly.

Now... A short is indicated by BRIGHT LIGHT.

If you turn on a light and the lamp comes on about 70% (Both lamps, the test lamp and the selected lamp) turn it off and move on to the next lamp. Do one lamp at a time.. The one with a shorted socket the test lamp will come on full and the lamp under test not at all.. No blown fuses that way and it's safe.

Get the matching connectors for the tabs (Insulated type please) and some more wire and test clips or probes and you have a very very very useful 12 volt diagnostic tool,,, Often much easier to use than a volt meter when chasing power problems.
__________________
Home is where I park it!
wa8yxm is offline   Reply With Quote
Old 03-24-2011, 04:53 PM   #11
Senior Member
 
Alan_Hepburn's Avatar


 
Fleetwood Owners Club
Workhorse Chassis Owner
Join Date: Feb 2000
Location: San Jose, Ca, USA
Posts: 2,698
Quote:
Originally Posted by TQ60 View Post
Some folks insert a 1/4 inch bolt, works great, the smoke indicates the short...
Actually, a .22LR cartridge is almost a perfect fit for the typical round glass fuse...
__________________
Alan Hepburn - San Jose, Ca
2007 Bounder 35E being pushed by a 2020 Jeep Gladiator Sport S or a 2022 Jeep Wrangler Unlimited (JLU) Sport S
Alan_Hepburn is offline   Reply With Quote
Old 03-24-2011, 05:01 PM   #12
Senior Member
 
4Knights's Avatar
 
Oklahoma Boomers Club
Fleetwood Owners Club
Join Date: Jan 2011
Posts: 1,801
Quote:
Originally Posted by Alan_Hepburn

Actually, a .22LR cartridge is almost a perfect fit for the typical round glass fuse...
Make sure it's already be fired! Hate to have the heat from a short cause the primer to shoot the round off.

Ron & Wendy 94 Pace Arrow 454
__________________
Ron & Wendy-Kansas
94 Pace Arrow 34 ft
25 yr Army retired 2006
4Knights is offline   Reply With Quote
Old 03-24-2011, 05:31 PM   #13
Senior Member
 
Ford Super Duty Owner
Join Date: Dec 2009
Location: Mcdonough, Ga.
Posts: 5,932
99% sure you have a bad circuit board. Fluorsent lights have a printed circuit board. these are prone to shorting out. Remove the cover remove the bulbs. pinch the center cover and remove it. you will almost for sure see a burned board. you can replace the board for about half of what a new light cost. To double check this you can take the hot wire loose from the light fixture and energize the circuit. if the fuse doesnt blow the light is the problem.
ga traveler is offline   Reply With Quote
Old 03-25-2011, 06:00 PM   #14
Senior Member
 
Alan_Hepburn's Avatar


 
Fleetwood Owners Club
Workhorse Chassis Owner
Join Date: Feb 2000
Location: San Jose, Ca, USA
Posts: 2,698
Quote:
Originally Posted by 4Knights View Post
Make sure it's already be fired! Hate to have the heat from a short cause the primer to shoot the round off.

Ron & Wendy 94 Pace Arrow 454
Awww - where's your sense of adventure!!!
__________________
Alan Hepburn - San Jose, Ca
2007 Bounder 35E being pushed by a 2020 Jeep Gladiator Sport S or a 2022 Jeep Wrangler Unlimited (JLU) Sport S
Alan_Hepburn is offline   Reply With Quote
Reply


« Koni shocks | TPMS »

Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
HWH Fuse Blowing rtymer Freightliner Motorhome Chassis Forum 2 07-25-2010 11:03 AM
200 amp fuse no-go on Inverter? (as per Battery Store?) BadBoy MH-General Discussions & Problems 21 06-30-2010 10:24 AM
Help with fuse blowing solution LandHo Winnebago Industries Owner's Forum 10 04-26-2008 05:39 PM
Dash light fuse blowing dnebout Workhorse and Chevrolet Chassis Motorhome Forum 5 11-15-2007 02:18 AM
right signal fuse keeps blowing Motorhome05 Winnebago Industries Owner's Forum 3 03-14-2007 11:29 AM

» Featured Campgrounds

Reviews provided by


All times are GMT -6. The time now is 06:53 PM.


Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.