Journey with Confidence RV GPS App RV Trip Planner RV LIFE Campground Reviews RV Maintenance Take a Speed Test Free 7 Day Trial ×
RV Trip Planning Discussions

Go Back   iRV2 Forums > MOTORHOME FORUMS > MH-General Discussions & Problems
Click Here to Login
Register FilesVendors Registry Blogs FAQ Community Calendar Today's Posts Search Log in
Join iRV2 Today

Mission Statement: Supporting thoughtful exchange of knowledge, values and experience among RV enthusiasts.
Reply
  This discussion is proudly sponsored by:
Please support our sponsors and let them know you heard about their products on iRV2
 
Thread Tools Search this Thread Display Modes
 
Old 01-11-2016, 08:08 PM   #15
Senior Member
 
Mr_D's Avatar
 
Country Coach Owners Club
Solo Rvers Club
iRV2 No Limits Club
Join Date: May 2011
Location: Vancouver, WA
Posts: 37,725
Quote:
Originally Posted by Slolane View Post
Another issue with generators is that the insulation on the windings absorbs moisture from the air. Wet insulation is not good........

Running the generator under load will heat the insulation and drive off the moisture, prolonging the life of the generator.
That is what the generator manufacturers say is the reason for running diesel, gas and propane generators. With gas units it's to also keep fresh gas in the float bowl. Diesel and propane units don't need to worry about that last one though, but the windings can still go bad due to moisture in the windings so they should also be run with a half load.
__________________
2009 45' Magna 630 w/Cummins ISX 650 HP/1950 Lbs Ft, HWH Active Air
Charter Good Sam Lifetime Member, FMCA,
RV'ing since 1957, NRA Benefactor Life, towing '21 Jeep JLU Rubicon Ecodiesel
Mr_D is offline   Reply With Quote
Join the #1 RV Forum Today - It's Totally Free!

iRV2.com RV Community - Are you about to start a new improvement on your RV or need some help with some maintenance? Do you need advice on what products to buy? Or maybe you can give others some advice? No matter where you fit in you'll find that iRV2 is a great community to join. Best of all it's totally FREE!

You are currently viewing our boards as a guest so you have limited access to our community. Please take the time to register and you will gain a lot of great new features including; the ability to participate in discussions, network with other RV owners, see fewer ads, upload photographs, create an RV blog, send private messages and so much, much more!

Old 01-11-2016, 08:51 PM   #16
Senior Member
 
Ray,IN's Avatar
 
Join Date: Aug 2001
Location: North America somewhere
Posts: 30,951
Cummins/Onan made the "rule". Read your owners manual.

Quote:
Originally Posted by jondrew View Post
Fortunately they have not figured out how to put corn squeezings into diesel yet
Yep, it's "figured out"; Ethanol Information: E Diesel
Some folks worry about bio-diesel made from soybeans, just wait_. Currently some engineers are concerned about the corrisiveness and flamability of ethanol in diesel fuel systems.
__________________
2000 Winnebago Ultimate Freedom USQ40JD, ISC 8.3 Cummins 350, Spartan MM Chassis. USA IN 1SG 11B5MX,Infantry retired;Good Sam Life member,FMCA." My fellow Americans, ask not what your country can do for you, ask what you can do for your country. John F. Kennedy
Ray,IN is offline   Reply With Quote
Old 01-11-2016, 09:30 PM   #17
"Formerly Diplomat Don"
 
Dutch Star Don's Avatar
 
Newmar Owners Club
Join Date: Apr 2005
Location: Moorpark, Ca.
Posts: 24,115
Personally, I've never exercised either of my Onan diesel generators (two different coaches) in 11 years. With that said, I live in warm/dry Southern California. If I lived in a wet climate I would probably do differently.
__________________
Don & Mary
2019 Newmar Dutch Star 4018 (Freightliner)
2019 Ford Raptor
Dutch Star Don is offline   Reply With Quote
Old 01-12-2016, 05:59 AM   #18
Senior Member
 
Murf2u's Avatar
 
Join Date: Aug 2011
Location: Near Toronto, Canada
Posts: 1,842
Quote:
Originally Posted by twinboat View Post
A year and a half ago, I picked up a 1999 MH with 6 hours on the original generator.

I put 500 trouble free hours on it since.

It will now be stored for up to a year with no running.

I did pull the gas line and run it dry.
Wish me luck.

Exactly my experience.

In fact I have a friend with a summer place on an island in the Great Lakes. The utility people wanted a small fortune to bring electricity to the island so he bought a used 4K Onan from a motorhome and installed it in a shed. It gets used a LOT during the summer, then run dry in October and left until the next April. Never had a problem yet. He's been doing this for 10+ years now.
__________________
Ted 'n' Laurie, plus Jackson (aka Deputy Dog, the Parson Russell Terrier 'fur kid') and, Rylie (who crossed the Rainbow Bridge June 14, 2012).
Murf2u is offline   Reply With Quote
Old 01-12-2016, 06:14 AM   #19
Senior Member
 
69Stang's Avatar
 
Join Date: Jul 2015
Posts: 1,881
When my parents still had my MH it sat for 2 1/2 years without being ran. Once I fixed the loose wire on the coil it fired right up and works great. I ran it for 2 hrs straight on our trip to Brunswick over New Years without an issue. Dad did use a gas stabilizer, but that was it.
__________________
2010 Phaeton 40QTH on a PG Chassis.
2017 Lincoln MKX.
Air Force One brake system and Blue OX Towbar.
69Stang is offline   Reply With Quote
Old 01-12-2016, 06:25 AM   #20
Senior Member
 
dnystrom's Avatar
 
Winnebago Owners Club
Join Date: Jan 2014
Posts: 539
When I was working we started our Fire Station Generator (35k) Weekly and ran for 1/2 hour with load. So yes, They liked to be run. That's what they do.
__________________
07 Meridian 34H 350 Cat
2010 Subaru Forester Tow
Home Port is Kingman,Az
KA7UYZ NRA Endowment Member Retired Fire Service
dnystrom is offline   Reply With Quote
Old 01-12-2016, 06:26 AM   #21
Member
 
Join Date: Feb 2011
Posts: 55
Many, many years ago 50 plus, my dad used to start the lawn mowing tractor just be for it put it away for the winter. He then took to air cleaner of and poured oil into the carburetor and then shut it down. He then drained the gas. Next spring new gas and it started right up. He basically coated the cylinder walls and valves with oil. An excellent rust inhibitor. Drain gas or use a gas inhibitor to keep varnish from forming. I feel the area that you are in or have been in, would dictate whether starting is necessary.
Maverick50 is offline   Reply With Quote
Old 01-12-2016, 06:58 AM   #22
Senior Member
 
Join Date: Jul 2014
Posts: 35,438
Quote:
Originally Posted by dnystrom View Post
When I was working we started our Fire Station Generator (35k) Weekly and ran for 1/2 hour with load. So yes, They liked to be run. That's what they do.
I'm not sure what running a generator every week actually proves.

I understand that it is a test run to make sure it will start.

That does not guarantee it will start the next time.

On the day it don't, you will still have to fix it.
twinboat is offline   Reply With Quote
Old 01-12-2016, 07:55 AM   #23
Senior Member
 
dnystrom's Avatar
 
Winnebago Owners Club
Join Date: Jan 2014
Posts: 539
[QUOTE=Mr_D;2897604]That is what the generator manufacturers say is the reason for running diesel, gas and propane generators. With gas units it's to also keep fresh gas in the float bowl. Diesel and propane units don't need to worry about that last one though, but the windings can still go bad due to moisture in the windings so they should also be run with a half load.[/QUOTE



Well that makes sense as the generator I was mentioning was in Western Washington where it's very damp.
__________________
07 Meridian 34H 350 Cat
2010 Subaru Forester Tow
Home Port is Kingman,Az
KA7UYZ NRA Endowment Member Retired Fire Service
dnystrom is offline   Reply With Quote
Old 01-12-2016, 08:04 AM   #24
Senior Member
 
TonyMac's Avatar
 
Monaco Owners Club
Join Date: Oct 2014
Location: Rigby, Idaho
Posts: 3,948
From my Owners' Manual:
Generator Exercise
Ifuse of the generator is infrequent, “exercise” the generator once a month byoperating it at approximately half the maximum rated output for two hours. This“exercise” will help promote better starting, more reliable operation andlonger engine life. This procedure drives off moisture, lubricates the internalengine parts, replaces the old stale fuel with a fresh supply, and alsopromotes removing oxides from the electrical switches and contacts.
NOTE:
Avoid short run periods of the generator. Run thegenerator set under a load for a minimum of one-half hour.

__________________
Cheers,
TonyMac
2006 Monaco Safari Cheetah 40PMT
TonyMac is offline   Reply With Quote
Old 01-12-2016, 08:15 AM   #25
Senior Member
 
Join Date: Aug 2001
Location: FL
Posts: 1,355
I made the 30-day rule; are you failing to comply? Seriously, l've seen the suggestion from generator mfgr. Onan but can't put my hands on the source. Otherwise, the general consensus, anecdotally, is to run gensets monthly, under load, but do not run the RV engine at all unless it can be brought up to operating temps for some length of time, commonly thought to be one hour or more. This topic has been bandied around the internet for years and I really don't think it much matters what you do.
__________________
--2005 F350 Superduty Crewcab, 6.0, 4wd, short bed, 3.73 gears
--2016 Montana 3711FL, 40'
--SOLD 2014 Wildcat 327CK, 38'
ralphie is offline   Reply With Quote
Old 01-12-2016, 08:43 AM   #26
Senior Member
 
Join Date: Jan 2014
Posts: 4,669
Well you don't want to run your coach engine at idle for very long so you don't plug up your DPF system (newer engines). But I try to drive my coach at least once a month. Just like the generator I've got so much invested in this thing I want to see and hear it running.

There's lots of videos on YouTube of people starting up diesel generators that haven't run for 10 years. Kind of interesting to watch.


Quote:
Originally Posted by ralphie View Post
I made the 30-day rule; are you failing to comply? Seriously, l've seen the suggestion from generator mfgr. Onan but can't put my hands on the source. Otherwise, the general consensus, anecdotally, is to run gensets monthly, under load, but do not run the RV engine at all unless it can be brought up to operating temps for some length of time, commonly thought to be one hour or more. This topic has been bandied around the internet for years and I really don't think it much matters what you do.
__________________
2023 Winnebago Travato
2023 Airstream Flying Cloud BH 30'
jondrew55 is offline   Reply With Quote
Old 01-12-2016, 08:54 AM   #27
Senior Member/RVM #90
 
MSHappyCampers's Avatar


 
Monaco Owners Club
Join Date: Nov 2002
Location: Columbus, MS
Posts: 54,780
Onan says to run it and that's good enough for me!
__________________
Joe & Annette
Sometimes I sits and thinks, sometimes I just sits.....
2002 Monaco Windsor 40PBT, 2013 Honda CRV AWD
MSHappyCampers is offline   Reply With Quote
Old 01-12-2016, 09:03 AM   #28
Senior Member
 
Join Date: Jul 2014
Posts: 35,438
Quote:
Originally Posted by MSHappyCampers View Post
Onan says to run it and that's good enough for me!
I completely agree, if I or someone I know and trust was anywhere near it.

Like I said wish me luck.
twinboat is offline   Reply With Quote
Reply

Tags
generator



Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
November 11 Remembrance Day in Canada Lac Just Conversation 10 11-11-2015 04:39 PM
Miles per day in winter? BillL Camping Locations, Plans & Trip Reports 7 09-22-2015 04:36 PM
Our trip, Starting Labor day weekend.... Lloyd in S.C. Camping Locations, Plans & Trip Reports 4 06-24-2015 11:58 AM
Happy Memorial Day Weekend !! oakcreekeric Just Conversation 4 05-22-2015 01:02 PM

» Featured Campgrounds

Reviews provided by


All times are GMT -6. The time now is 03:07 AM.


Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.