Breaker never tripped!
How is this possible?! Almost a fire Between my surge protector and extension cord and the campground breaker never tripped! Had to hacksaw them apart!
|
|
|
|
Join the #1 RV Forum Today - It's Totally Free!
iRV2.com RV Community - Are you about to start a new improvement on your RV or need some help with some maintenance? Do you need advice on what products to buy? Or maybe you can give others some advice? No matter where you fit in you'll find that iRV2 is a great community to join. Best of all it's totally FREE!
You are currently viewing our boards as a guest so you have limited access to our community. Please take the time to register and you will gain a lot of great new features including; the ability to participate in discussions, network with other RV owners, see fewer ads, upload photographs, create an RV blog, send private messages and so much, much more!
|
09-03-2020, 04:19 PM
|
#2
|
Senior Member
Newmar Owners Club
Join Date: Oct 2009
Posts: 10,310
|
Breaker needs to see higher amp draw than its rated for or a dead short, what you had is bad connectections at low amp draw making high resistance which makes heat.......and in time stuff melts. The wiring never went to ground, came in contact with each other thus no breaker trip. Loose wiring , bad connections cause this. I have seen outlets, plugs do this when drawing close to breakers rated amps. Glad you caught it !
__________________
2012 Essex 4544 2011 Jeep JK, M&G Braking, 2014 MTI 27' Hog Hauler, Wireless brake control, 2006 Ultra & 1989 Springer, 2003 Harley-Davidson
FLHR Road King Anniversary
|
|
|
09-03-2020, 09:06 PM
|
#3
|
Senior Member
Join Date: May 2010
Posts: 1,048
|
I had that happen at the 30 amp inlet on my rv wall. First trip in new class c. White wire in the wall had never been tightened from factory. Lost power when it built up carbon from arching I guess. Went out to check problem and smelled burnt rubber. Ruined outlet and power cord. Forest river paid!
__________________
2008 Tundra DC, 5.7L, Airlift 5000 Airbags
2013 Rockwood 8282WS
Signature Untralight Diamond Package
|
|
|
09-03-2020, 11:28 PM
|
#4
|
Senior Member
Gulf Streamers Club Ford Super Duty Owner
Join Date: Aug 2015
Location: Memphis, TN
Posts: 4,343
|
Quote:
Originally Posted by Johnynorthla
How is this possible?! Almost a fire Between my surge protector and extension cord and the campground breaker never tripped! Had to hacksaw them apart!
|
(Further), I say your problem was LOOSE WIRE/ LOOSE CONNECTION in the RECEPTACLE NEUTRAL, noting greater heat damage on Receptacle, but also Greater Neutral Insulation melt than on the HOT while NOT enough to say the PLUG was the cause, but more enough that it was a symptom. LUCK
__________________
(TerryH.) 2000-GS Conquest Limited 6266 Class-C 99-E450SD V10
|
|
|
09-04-2020, 08:59 AM
|
#5
|
Senior Member
Join Date: Mar 2012
Location: Florida panhandle
Posts: 1,235
|
plug looks like heavily tarnished causing resistance causing heat causing melt down
need to remove tarnish on old plugs and replace tarnished receptacles
__________________
2018 Adventurer 19RD 19’ 11”
Ford E350 V10 Cutaway Chassis Class C
#10050 GVWR, #18500 GCWR Smoke that!
|
|
|
09-04-2020, 09:18 AM
|
#6
|
Moderator Emeritus
Ford Super Duty Owner
Join Date: Aug 2000
Location: Bryan, TX when not traveling.
Posts: 22,948
|
Looks like a loose connection of a loose plug was the problem. I keep some No-Ox on the plugs to help out.
Ken
__________________
Amateur Radio Operator (KE5DFR)|No Longer Full-Time! - 2023 Cougar 22MLS toted by 2022 F150, 3.5L EcoBoost Tow Max FX4 Lariat Travel with one Standard Schnauzer and one small Timneh African Gray Parrot, retired mechanical engineer
|
|
|
09-04-2020, 09:30 AM
|
#7
|
Senior Member
Join Date: Nov 2018
Location: Beaver Dam, Wisconsin
Posts: 5,152
|
Good advice above.
30 amp circuit breaker in pedestal did not trip.
30 amp? circuit breaker in RV did not trip.
So current was not too high.
Socket got hot.
Plug less so.
High resistance equals heat.
Probably one or more bad connections in the socket. Could be corroded blades or socket or could be screws loose.
I can't tell if your picture shows plug or socket.
Good luck! Minimal Damage! Repair, replace and move on.
Checking and tightening all screw connections in RV service entrance area is a good practice. Check breaker connections. Check all buss bar connections. Check all inverter, charger, converter, transfer switch connections. Check all ground connections. It tends to prevent these kinds of issues inside the RV.
I wish you good luck and happy trails ahead!
__________________
Paul Bristol
Kodiak Cub 176RD
Nissan Pathfinder 2015
|
|
|
09-04-2020, 09:43 AM
|
#8
|
Senior Member
Join Date: Mar 2019
Location: Lansing MI
Posts: 2,825
|
Quote:
Originally Posted by TXiceman
Looks like a loose connection of a loose plug was the problem. I keep some No-Ox on the plugs to help out.
Ken
|
What he said!
|
|
|
09-04-2020, 02:16 PM
|
#9
|
Senior Member
Join Date: Sep 2013
Location: Pacific Northwest and Arizona
Posts: 2,048
|
I replaced the cord end on my power cord because of signs it was heating up. It was a molded plug so no way to tighten the internal connection.
Its pretty amazing how much heat is generated by a loose connection. One time at work I entered a mechanical room to access the roof and before I flipped the lights on noticed a bright red glow on the wall. Turning on the lights I saw it was a screw connection on a piece of equipment. It was glowing bright enough to see even with the light on. I suspect a decent amount of RV fires caused are caused by connections vibrating loose over time.
__________________
Tom and Pris M. along with Buddy the 18 year old Siamese cat
1998 Safari Serengeti 3706, 300HP Cat 3126 Allison 3060, 900 watts of Solar.
Dragging four telescopes around the US in search of dark skies.
|
|
|
09-04-2020, 02:27 PM
|
#10
|
Senior Member
Join Date: Jun 2018
Location: Los Angeles area
Posts: 1,416
|
Quote:
Originally Posted by astrnmrtom
I suspect a decent amount of RV fires caused are caused by connections vibrating loose over time.
|
One comment I read somewhere.... "A RV or travel trailer in motion is a studio apartment in a continuous earthquake."
Mike
__________________
Semi-retired technogeek...electronics / computer / 2-way / ham radio... WA6ILQ (45+years)
1985 Fleetwood 32' Southwind (Chev P30/454/TH400), dubbed "Lazarus" by friends... I resurrected it from the dead...
|
|
|
09-04-2020, 02:51 PM
|
#11
|
Senior Member
Join Date: Nov 2005
Posts: 7,400
|
What they said!....basically you had a 30 amp toaster plugged in--no short, just lots of resistance.....you tend see this a lot at older campgrounds and with more modern 30 amp rigs with lots of electric toys, or with 50 amp rigs using 30 amp dog-bones....scary part is that this sort of thing can also happen to any loose connection inside your rig, eg, transfer switch, surge protector, inverter, breaker boxes, and wall plugs!!!!!
__________________
Old Scout
2015 IH45 Foretravel
2003 Alpine 40' MDTS [Sold]
New Braunfels, Texas
|
|
|
09-04-2020, 03:03 PM
|
#12
|
Senior Member
Join Date: Jul 2014
Posts: 35,438
|
Quote:
Originally Posted by astrnmrtom
I replaced the cord end on my power cord because of signs it was heating up. It was a molded plug so no way to tighten the internal connection.
Its pretty amazing how much heat is generated by a loose connection. One time at work I entered a mechanical room to access the roof and before I flipped the lights on noticed a bright red glow on the wall. Turning on the lights I saw it was a screw connection on a piece of equipment. It was glowing bright enough to see even with the light on. I suspect a decent amount of RV fires caused are caused by connections vibrating loose over time.
|
Elecric welding is a bad connection.
You make the connection to start the arc and then back away.
|
|
|
09-04-2020, 03:15 PM
|
#13
|
Senior Member
Join Date: Nov 2005
Posts: 7,400
|
TB--great description of a "loose connection"....my compliments...
__________________
Old Scout
2015 IH45 Foretravel
2003 Alpine 40' MDTS [Sold]
New Braunfels, Texas
|
|
|
09-23-2020, 10:29 AM
|
#14
|
Senior Member
Join Date: Mar 2019
Posts: 964
|
I am OP on this subject.
I contacted Sure guard, whom is Actually Southwire, (the company who manufactures and sells the surge protection device),. I explain to them the unit is 5 years old and I was looking for service, a new male end and testing the unit and that I was not looking for warranty work. see the below response. At $250, I Don’t think I’ll ever purchase another item from them in the future.
“Hi John:
If your male plug melted, that is usually due to a loose connection in the female plug it is inserted in. Normal configuration is to plug 34730 into pedestal and use an extension cord on the load side. That will keep the 34730 off of the ground.
The 34730 is an older device and the unit only had a one year warranty. We do not service any devices nor sell any spare parts due to the safety nature of it’s protection.
Regards,
S.
Image
Steve Guarcello
Technical Support
Southwire Company, LLC
Phone 727-812-0578
Email stephen.guarcello@southwire.com”
|
|
|
|
|
Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
|
|
Posting Rules
|
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts
HTML code is Off
|
|
|
|
» Recent Discussions |
|
|
|
|
|
|
|
|
|
|
|
|
|