The Onan 4000 series generators have an 8 pin connector of which 5 pins are used ...
If it the Thor cable is connected to the generator and it won't start OR stop from the inside switch I'd suspect the center pin on the start/stop switch is not getting ground. The generator itself must be grounded or the generator would NOT start outside.
A Battery Ground
B Stop (connected to ground with start/stop switch in Stop
C Start (connected to ground with start/stop switch in Start
D Not used
E +12 present when generator running (generally drives hours meter)
F Status Ind (+12 when ind. lit, flashes fault codes like Ind in switch on gen)