Replace heat pump unit with A/C only unit

Has anyone replaced a heat pump with an A/C-only model?

I had a Coleman 48004-969, ducted. I've ordered a replacement unit Coleman 48203-969.

The former is 15K BTU and the latter is 13.5K BTU. We can save discussions about whether I'll regret going down in BTU. This was a mostly monetary decision since the units are about $200 cheaper (15K HP to 13.5K A/C only) for what I consider an overpriced item anyway. The old one was only 6 seasons old and had a soft copper line snap. Yes, snap.

Anyway, I feel that the control box will be fine and not know what's missing. The plug will be the same with fewer pins, I would think, due to the lack of a heat pump.

Do you think this will be okay? Will the thermostat be fine as well, even if it's slid to "Elec Heat" position? I figure nothing will happen if there's nothing to turn on.

I guess I might need to disconnect a couple of 12v wires going into the control box and maybe even on the back of the thermostat.

Thank you.
ike1562 is offline   Reply With Quote
Join the #1 RV Forum Today - It's Totally Free!

iRV2.com RV Community - Are you about to start a new improvement on your RV or need some help with some maintenance? Do you need advice on what products to buy? Or maybe you can give others some advice? No matter where you fit in you'll find that iRV2 is a great community to join. Best of all it's totally FREE!

You are currently viewing our boards as a guest so you have limited access to our community. Please take the time to register and you will gain a lot of great new features including; the ability to participate in discussions, network with other RV owners, see fewer ads, upload photographs, create an RV blog, send private messages and so much, much more!

Old 04-15-2021, 06:33 AM   #2
Senior Member
 
gljurczyk's Avatar
 
Join Date: Mar 2016
Posts: 420
Replace heat pump unit with A/C only unit

Quote:
Originally Posted by ike1562 View Post
Has anyone replaced a heat pump with an A/C-only model?

I had a Coleman 48004-969, ducted. I've ordered a replacement unit Coleman 48203-969.

The former is 15K BTU and the latter is 13.5K BTU. We can save discussions about whether I'll regret going down in BTU. This was a mostly monetary decision since the units are about $200 cheaper (15K HP to 13.5K A/C only) for what I consider an overpriced item anyway. The old one was only 6 seasons old and had a soft copper line snap. Yes, snap.

Anyway, I feel that the control box will be fine and not know what's missing. The plug will be the same with fewer pins, I would think, due to the lack of a heat pump.

Do you think this will be okay? Will the thermostat be fine as well, even if it's slid to "Elec Heat" position? I figure nothing will happen if there's nothing to turn on.

I guess I might need to disconnect a couple of 12v wires going into the control box and maybe even on the back of the thermostat.

Thank you.

I can’t see why it wouldn’t work, you would have to disconnect the reversing valve wire from the stat. Remember that stat also controls your propane furnace.
gljurczyk is offline   Reply With Quote
Old 04-15-2021, 06:39 AM   #3
Junior Member
 
jaysheridoc's Avatar
 
Mid Atlantic Campers
Ford Super Duty Owner
Entegra Owners Club
Join Date: Jun 2017
Posts: 15
While I haven’t replaced an a/c unit in a RV, my profession is HVAC, so maybe I can help a little.

In regards to your thermostat question. If there is no connection to the terminal, that controls the electric heat, nothing can happen when you select the thermostat to electric heat.

Heat pump and straight a/c thermostat stats differ based on a heat pump thermostats control over the reversing valve (needed to convert straight a/c to HP). Traditionally the Y, or yellow circuit, is used to energize the compressor and that is typical for HP as well as a/c. In short, HP stats can be used for straight a/c, and some additional work is needed to get an a/c stat to work on a HP.

I doubt you’ll ever notice a 2,000 btuh difference...
__________________
"Once a Marine, Always a Marine"
2020 Entegra Coach, Esteem 27U
2017 Winnebago Minnie 2401RG - Sold
jaysheridoc is offline   Reply With Quote
Old 04-25-2021, 12:43 PM   #4
Junior Member
 
Join Date: Jan 2015
Posts: 15
Quote:
Originally Posted by gljurczyk View Post
I can’t see why it wouldn’t work, you would have to disconnect the reversing valve wire from the stat. Remember that stat also controls your propane furnace.
Thanks for your response. I did unplug the "heat" wire from the control box, but didn't touch the back of t-stat at all. Testing was limited to the fan works at both speeds (cold in Colorado still) and I did slide the switch to "Elec Heat" but nothing happened of course, except a "click" in the stat, indicating it wanted to start something. Nothing happened, not even furnace coming on. The furnace comes on like normal in "Gas Heat" position. I don't see why I need to open up the t-stat.

Also, there was a freeze sensor connected to control box (other end was jammed into fins), which I unplugged both connectors, thinking the new one would have one. It didn't.

Do I need the freeze sensor if it's just A/C or is that for the heat pump only model? I still have the wires to use if it's necessary.

Thanks again.
ike1562 is offline   Reply With Quote
Old 04-25-2021, 12:53 PM   #5
Senior Member
 
ivykrewe's Avatar
 
Monaco Owners Club
Join Date: Feb 2012
Location: Belle Chasse, La
Posts: 245
It should last longer than that. My 3 are 15 years old. If it was mine i would repair it. I repaired one for a friend about 5 years ago and it is still working great.
__________________
Gene @ Alice Ivy 2007 Monaco Dynasty, 2012 Wrangler
ivykrewe is offline   Reply With Quote
Old 04-25-2021, 01:16 PM   #6
Junior Member
 
Join Date: Jan 2015
Posts: 15
Quote:
Originally Posted by jaysheridoc View Post
While I haven’t replaced an a/c unit in a RV, my profession is HVAC, so maybe I can help a little.

In regards to your thermostat question. If there is no connection to the terminal, that controls the electric heat, nothing can happen when you select the thermostat to electric heat.

Heat pump and straight a/c thermostat stats differ based on a heat pump thermostats control over the reversing valve (needed to convert straight a/c to HP). Traditionally the Y, or yellow circuit, is used to energize the compressor and that is typical for HP as well as a/c. In short, HP stats can be used for straight a/c, and some additional work is needed to get an a/c stat to work on a HP.

I doubt you’ll ever notice a 2,000 btuh difference...
Thanks. The control box was labeled and the "Y" connector was the one labeled "Heat", although it wasn't a yellow wire. That confused me for a moment but I decided to disconnect that terminal only (even if it was a different color), for the moment, aside from the freeze terminals. I did remove those but the new unit did not come with that wire so I'm not sure if I need it.

Thanks for the vote of confidence in the 2K drop. It uses less power too, which some of us can use at times with additional appliances at same time.

I noticed that the new one has only a smaller copper line running through the same zone as the old one. That bigger one is the line that busted. See sideways pic. It seems to be 7/16" soft copper. I soldered with two 45's 3/8" rigid fittings to fix it before deciding that I didn't want to buy the other equipment needed, nor roll the dice on a hundred bucks worth of R410. That, and I don't have the skill. I got only one guy to give me a number and it was $550 dollars to "maybe" get it working again. Yes I know they're usually braised, but read that soldering can work too, just not as strong. I had used a 3% silver solder before giving up.
Attached Thumbnails
Click image for larger version

Name:	IMG_20210329_153356467_HDR.jpg
Views:	27
Size:	228.3 KB
ID:	326281  
ike1562 is offline   Reply With Quote
Old 04-25-2021, 05:23 PM   #7
Junior Member
 
Join Date: Jan 2015
Posts: 15
Quote:
Originally Posted by ike1562 View Post
Thanks for your response. I did unplug the "heat" wire from the control box, but didn't touch the back of t-stat at all. Testing was limited to the fan works at both speeds (cold in Colorado still) and I did slide the switch to "Elec Heat" but nothing happened of course, except a "click" in the stat, indicating it wanted to start something. Nothing happened, not even furnace coming on. The furnace comes on like normal in "Gas Heat" position. I don't see why I need to open up the t-stat.

Also, there was a freeze sensor connected to control box (other end was jammed into fins), which I unplugged both connectors, thinking the new one would have one. It didn't.

Do I need the freeze sensor if it's just A/C or is that for the heat pump only model? I still have the wires to use if it's necessary.

Thanks again.

Okay, I found out after testing (warmed up here today) that, yes, I do need that freeze sensor hooked up. Fan ran but compressor wouldn't kick on. Hooked it up and it works fine.
ike1562 is offline   Reply With Quote
Old 04-25-2021, 05:30 PM   #8
Junior Member
 
Join Date: Jan 2015
Posts: 15
Quote:
Originally Posted by ike1562 View Post
Thanks. The control box was labeled and the "Y" connector was the one labeled "Heat", although it wasn't a yellow wire. That confused me for a moment but I decided to disconnect that terminal only (even if it was a different color), for the moment, aside from the freeze terminals. I did remove those but the new unit did not come with that wire so I'm not sure if I need it.

Thanks for the vote of confidence in the 2K drop. It uses less power too, which some of us can use at times with additional appliances at same time.

I noticed that the new one has only a smaller copper line running through the same zone as the old one. That bigger one is the line that busted. See sideways pic. It seems to be 7/16" soft copper. I soldered with two 45's 3/8" rigid fittings to fix it before deciding that I didn't want to buy the other equipment needed, nor roll the dice on a hundred bucks worth of R410. That, and I don't have the skill. I got only one guy to give me a number and it was $550 dollars to "maybe" get it working again. Yes I know they're usually braised, but read that soldering can work too, just not as strong. I had used a 3% silver solder before giving up.
Okay, I got some things wrong. A few corrections: The "Heat" connector on the control box is "W" but the wire IS yellow. See, I told you I got confused! And it's only 1500 BTU reduction, not 2000. The new unit is 13.5K. Thanks again.
ike1562 is offline   Reply With Quote
Old 04-25-2021, 05:37 PM   #9
Junior Member
 
Join Date: Jan 2015
Posts: 15
Quote:
Originally Posted by ivykrewe View Post
It should last longer than that. My 3 are 15 years old. If it was mine i would repair it. I repaired one for a friend about 5 years ago and it is still working great.
It ought to, but didn't. The one you fixed, did it have a complete refrigerant line break? You must have the vacuum and other equipment, and the skill. So that makes all the difference. Your friend got theirs fixed for the cost of refrigerant and a couple beers, I'm guessing. I wasn't lucky enough to have a friend in the biz.
ike1562 is offline   Reply With Quote
Reply

Tags
ace, heat, heat pump, pump, replace



Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Dometic Heat Pump to No Heat Pump Memphisbobby Newmar Owner's Forum 5 03-07-2021 06:07 AM
Need To Replace Your Failed Carrier AC Upper Unit Only? bamaguy911 RV Systems & Appliances 0 10-08-2017 12:32 PM
Replace Penguine AC/Heat pump with AC only? adamfolger Monaco Owner's Forum 9 08-19-2015 07:45 PM
Duo-therm A/C unit runs only in heat pump mode Pusherpilot RV Systems & Appliances 9 08-09-2012 07:18 PM
To heat pump or not heat pump Bruce and Jenna Excel Owner's Forum 17 04-15-2009 10:20 PM