I don't think you'll be able to see this problem with a meter. The voltage outage is too short. You would need a recording oscilloscope to see it.

I still think that the problem is that when the generator is in the process of shutting down, the output voltage drops slower than the inverter recognizes as an outage. So it goes low (under 100V?) and the sat receiver reboots, then (within miliseconds) it goes even lower (80V?) and the inverter sees that as an outage and kicks in. But it's too late for the sat receiver.

As I said before, the solution is to turn off the breaker feeding the inverter before shutting down the generator. Just remember to turn it back on again after shore power is connected or the generator is re-started.

I have experienced the exact same problem, and that is how I deal with it.
__________________
2008 King Aire 4562, Spartan K3(GT) w/ Cummins ISX 600
2014 Jeep Grand Cherokee Overland 5.7L V8 Hemi w/ Blue Ox Aventa LX Tow Bar and baseplate, SMI Air Force One brake
FlyingDiver is offline   Reply With Quote
Join the #1 RV Forum Today - It's Totally Free!

iRV2.com RV Community - Are you about to start a new improvement on your RV or need some help with some maintenance? Do you need advice on what products to buy? Or maybe you can give others some advice? No matter where you fit in you'll find that iRV2 is a great community to join. Best of all it's totally FREE!

You are currently viewing our boards as a guest so you have limited access to our community. Please take the time to register and you will gain a lot of great new features including; the ability to participate in discussions, network with other RV owners, see fewer ads, upload photographs, create an RV blog, send private messages and so much, much more!

Old 03-31-2014, 01:27 PM   #16
Senior Member
 
Join Date: Jun 2013
Posts: 194
Rossi6998,
iI decided to look into your system even deeper. I have found your issue and your drop out is as designed. First here is the documentation that I found on the vendors web site.

http://gpelectric.com/files/gpelectr...ide2011_vB.pdf

http://gpelectric.com/files/gpelectr...SW1500-600.pdf

http://gpelectric.com/files/gpelectr...h_GP-TS_vC.pdf

If you look at the transfer switch wiring diagram on page 4 of the PDF file you will see how the weekender package that you have is interconnected. Your inverter output has two outlets. There is a plug from the transfers switch which connects to the inverter. The plug is wired to the normally closed contacts of the 30 amp power relay in the transfer switch housing. The AC load panel is connected to the common contacts of the relay. The relay is DPDT relay. It just switches the hot and neutral wires of the AC. So with no AC and you turn on the inverter, it supplies AC to the AC panel ie your satellite receiver. When the generator or shore power is available the 30 amp relay is energized. The NO contacts are now closed and AC power is connected to the AC panel which is providing power to your satellite receiver. Also the same contacts provide power to your battery charger. When you lose shore power or the generator. The relay switches back to the inverter. Its this drop out that your having. Also the inverter is still providing power as long as the on/off switch is in the on position. Also note that the inverter AC sine wave is not synchronized with the incoming AC from the generator.

So the power transfer switch works as designed.

Here is a solution to fix your problem. The inverter has an available outlet that can be used to plug in your TV, sat receiver, dvd, etc. You have about 12.5 amps AC available total. If I remember correctly in my last RV the larger loads where wired to the AC panel and then I had another panel which was wired to the inverter all the time. I had outlets that were hot always so the kids could plug in there electronics.

I hope this discussion and solution helps others understand how there AC power in the rv/campers actually works.

-Brian
cowrv39 is offline   Reply With Quote
Old 03-31-2014, 04:07 PM   #17
Registered User
 
Monaco Owners Club
Join Date: Oct 2009
Location: Varies Depending on The Weather
Posts: 8,517
I think Flying Driver has a better solution to his problem.

Just my opinion.

Dr4Film ----- Richard
Dr4Film is offline   Reply With Quote
Old 03-31-2014, 05:08 PM   #18
Senior Member
 
Join Date: Jun 2013
Posts: 194
Dr4film,
Look at the diagram for the transfer switch. It's a switch. Off/on. When no shore power or generator the inverter feeds the power panel. Everything is happy. When the shore power or generator is a source the transfer switch is energized and the AC panel is now being feed by the shore power or generator. Turn the shore power of and the transfer switch relay opens and switches to the inverter. Two different power sources the inverter is bypassed when on shore power or generator. This is working as designed. As an engineer I would of designed the same way but split t,he AC panel into two panels. Critical and non critical. The critical one is always hot. It's always being feed by the inverter when the on/off switch is on. The non critical load is only available when the shore power or generator is available. The diagram shows everything clearly. Some times design engineers don't think out the use cases clearly. The inverter is always connected to the battery. Always on power unless the batteries are low. The original OP says he also has a 30 amp solar charger. It came withe the weekend kit. So all the OP needs to do is plug his critical load into the second outlet. Instant UPS. The OP can either hard wire or run an extension cord. This is a cheap solution.
I am just trying to explain the design.

-Brian
cowrv39 is offline   Reply With Quote
Old 03-31-2014, 05:23 PM   #19
Senior Member
 
FlyingDiver's Avatar
 
Newmar Owners Club
Join Date: May 2007
Location: Somewhere....
Posts: 4,054
Quote:
Originally Posted by cowrv39 View Post
Dr4film,
Look at the diagram for the transfer switch. It's a switch. Off/on. When no shore power or generator the inverter feeds the power panel. Everything is happy. When the shore power or generator is a source the transfer switch is energized and the AC panel is now being feed by the shore power or generator. Turn the shore power of and the transfer switch relay opens and switches to the inverter. Two different power sources the inverter is bypassed when on shore power or generator. This is working as designed. As an engineer I would of designed the same way but split t,he AC panel into two panels. Critical and non critical. The critical one is always hot. It's always being feed by the inverter when the on/off switch is on. The non critical load is only available when the shore power or generator is available. The diagram shows everything clearly. Some times design engineers don't think out the use cases clearly. The inverter is always connected to the battery. Always on power unless the batteries are low. The original OP says he also has a 30 amp solar charger. It came withe the weekend kit. So all the OP needs to do is plug his critical load into the second outlet. Instant UPS. The OP can either hard wire or run an extension cord. This is a cheap solution.
I am just trying to explain the design.

-Brian
You're getting hung up on the transfer switch being something special. That diagram is essentially the same as the internal transfer switch built into all higher-end inverters. They just show it as separate components. In my Magnum inverter, the inverter, transfer switch, and charger are all in the same box, wired essentially the same.

What you haven't explained is why the load isn't going BACK to the inverter when the generator shuts off. That diagram doesn't actually show what power is tripping the relay to go from NO to NC and back. In reality, it's ANY power on the Shore Power/Generator line. If there's power there, the NO contacts are connected to the output line (to the AC Panel). If there isn't, the NC contacts (from the Inverter) are connected.

IF the system was working exactly as intended, then the relay would close (switching to inverter) before the voltage from the generator dropped low enough for the DVR to shut down. But it doesn't.

With this setup, the owner might not be able to shut off the power to the transfer switch before turning off the generator, as it appears that there's no panel breaker there. I'm not sure where the breakers are in this setup. The output breakers on the generator would do as well, if it's easily accessible.
__________________
2008 King Aire 4562, Spartan K3(GT) w/ Cummins ISX 600
2014 Jeep Grand Cherokee Overland 5.7L V8 Hemi w/ Blue Ox Aventa LX Tow Bar and baseplate, SMI Air Force One brake
FlyingDiver is offline   Reply With Quote
Old 03-31-2014, 05:32 PM   #20
Senior Member
 
Pusherman's Avatar
 
Join Date: Oct 2006
Location: Rochester NY
Posts: 2,706
Seems to me this problem can be solved quite simply. What's needed is an UN-interrupted power supply (UPS) like is found on many computer servers to protect against power outages.

There are smaller ones available under 1000 watts (you probably need about 100 watts) for under $100. Looks like the VIP211K takes about 25 watts max.

Plug the UPS in-line with the satellite receiver, and it should not drop out. No muss, no fuss. No switching breakers. No worries on transfer switch lag times.
__________________
Don
'07 Winnebago Journey 34H - CAT C7, Koni's, MCU's, SS Bell Crank, Safe-T-Plus
'07 HHR Toad, SMI AFO, Blue OX
Pusherman is offline   Reply With Quote
Old 03-31-2014, 05:44 PM   #21
Senior Member
 
Ford Super Duty Owner
Join Date: Dec 2005
Location: Buxton, North Dakota
Posts: 3,940
A UPS wouldn't be a good solution for various reasons. All that has to be done is to change the connection to the transfer switch coil from the shore power/generator to the inverter. When the inverter is turned on, it pulls in the contacts changing the power source from shore power/generator to inverter. Turn the inverter off and the transfer switch reverts back to shore power/generator. All you need to do is leave the inverter on when you watch TV. When you start the generator, it powers the non inverter powered circuits without affecting the circuits on inverter power.
__________________
2003 Winnebago Adventurer 38G F53/ V10 605 watts of Solar
1999 Winnebago Brave 35C F53V10 Handicap Equipped
1999 Jeep Cherokee, 1991 Jeep Wrangler Renegade and 2018 Chevrolet Equinox Diesel
John Hilley is offline   Reply With Quote
Old 03-31-2014, 06:40 PM   #22
Senior Member
 
BFlinn181's Avatar
 
Gulf Streamers Club
Join Date: Jan 2012
Location: Cincinnati
Posts: 19,925
Quote:
Originally Posted by Pusherman View Post
Seems to me this problem can be solved quite simply. What's needed is an UN-interrupted power supply (UPS) like is found on many computer servers to protect against power outages.

Plug the UPS in-line with the satellite receiver, and it should not drop out. No muss, no fuss. No switching breakers. No worries on transfer switch lag times.
Quote:
Originally Posted by John Hilley View Post
A UPS wouldn't be a good solution for various reasons.
Maybe I'm missing something, but WHY wouldn't a UPS "be a good solution for various reasons."?? Seems simpler than rewiring. Remember, to shut off the generator, you shut down the generator engine and it spins down. The transfer switch is always going to delay until the voltage drops off enough to trigger the switch. That interruption has proven long enough to reboot the satellite receiver, thus a UPS would bridge the gap.

I'd be curious to know your 'various reasons.' As I suggested, wire the inverter and UPS together, you wouldn't leave one on without the other, or, as Pusherman suggested, the UPS could go in the cabinet with the Sat Rec. and shut off UPS and Sat Rec. at the same time.
__________________

Bob & Donna
'98 Gulf Stream Sun Voyager DP being pushed by a '00 Beetle TDI
BFlinn181 is offline   Reply With Quote
Old 03-31-2014, 06:41 PM   #23
Registered User
 
Monaco Owners Club
Join Date: Oct 2009
Location: Varies Depending on The Weather
Posts: 8,517
A UPS was suggested early in this thread but post #5 by the OP states why it's not a solution for him.

Dr4Film ----- Richard
Dr4Film is offline   Reply With Quote
Old 03-31-2014, 06:45 PM   #24
Senior Member
 
BFlinn181's Avatar
 
Gulf Streamers Club
Join Date: Jan 2012
Location: Cincinnati
Posts: 19,925
Quote:
Originally Posted by Dr4Film View Post
A UPS was suggested early in this thread but post #5 by the OP states why it's not a solution for him.

Dr4Film ----- Richard
Then after further suggestions about a work-a-round for the UPS in post #7, the OP agreed a UPS could work in post #12.
__________________

Bob & Donna
'98 Gulf Stream Sun Voyager DP being pushed by a '00 Beetle TDI
BFlinn181 is offline   Reply With Quote
Old 03-31-2014, 06:52 PM   #25
Senior Member
 
Ford Super Duty Owner
Join Date: Dec 2005
Location: Buxton, North Dakota
Posts: 3,940
Depending on the inverter, it may or may not like it as a power source. There are two types of UPS, standby and on line. It will also be less efficient and be bulky.
__________________
2003 Winnebago Adventurer 38G F53/ V10 605 watts of Solar
1999 Winnebago Brave 35C F53V10 Handicap Equipped
1999 Jeep Cherokee, 1991 Jeep Wrangler Renegade and 2018 Chevrolet Equinox Diesel
John Hilley is offline   Reply With Quote
Old 03-31-2014, 06:54 PM   #26
Registered User
 
Monaco Owners Club
Join Date: Oct 2009
Location: Varies Depending on The Weather
Posts: 8,517
Bob,

You're correct. Me bad.

To me that would be the simplest thing to do but it's not my RV or my problem.

Dr4Film ----- Richard
Dr4Film is offline   Reply With Quote
Old 03-31-2014, 06:56 PM   #27
Senior Member
 
Join Date: Jun 2013
Posts: 194
The magnum series inverters are a far superior product. That product can synchronize with the incoming AC sine wave and provide transparent switchover in less that 16 milliseconds. Let's not go there but focus on the low end product.

Yes I am hung up on the relay. The relay only energizes when there is shore power or generator. I didn't see a delay circuit to wait for the shore power or generator to come up to speed. Other transfer switch wait for up to 15 sec. So understand this when on shore power or generator the AC power is passed directly to the AC panel. The inverter output is disconnected. When shore power or generator is disconnected the relay contacts I open and the inverter is supply power. AC is a sine wave. There is no way to synchronize the two in this design. The relay opens and what ever part of the phase of the sine wave happens in that moment is being supplied. So the load has to start up again. I can't explain this any clearer. Anytime power is interrupted the DC capacitors on the load side of a device might be able to sustain power for a fraction of a second. But now a days they make power supplies so cheap that the extra capacitors are not designed in. So there is no residue voltage.

I standby my previous posts. I can call the manufacture tech support but the diagram they provide is clear.

-Brian
cowrv39 is offline   Reply With Quote
Old 03-31-2014, 09:13 PM   #28
Senior Member
 
Rossi6998's Avatar


 
Winnebago Owners Club
Join Date: May 2008
Location: Surprise, AZ
Posts: 816
Hi Brian,

Thanks for the input. When I was asking the RV service advisor about the system, I do believe he said the inverter would be in bypass mode when the generator was on.

I contacted the maker of my solar system today (GoPower/Carmanah) and spoke to one of their techs. He said there will be a very slight delay as the transfer switch determines the generator is shutting down and the need to switch to the battery for power. He said this is done to prevent backload. He said although the delay is very slight, it must be enough of a delay to cause my DirecTV receiver to reboot.

Makes sense to me, but what do I know... Anyway, I am starting to like the UPS ideal more and more. For the amount of time I will be dry camping (maybe 5% of the time), the UPS will work for me.
Rossi6998 is offline   Reply With Quote
Reply

Tags
power



Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Tripp Lite RV inverter fan running always when on shore power wanderso RV Systems & Appliances 1 03-15-2014 10:50 AM
2004 Seabreeze power cord Reida Class A Motorhome Discussions 1 03-07-2014 06:37 PM
Transfer switch BayouMan Newmar Owner's Forum 3 01-16-2014 07:41 AM
Power to antenna power booster Ace 123 Gulf Stream Owner's Forum 5 11-09-2013 08:38 PM
No power when plugging in RedWing Nut iRV2.com General Discussion 5 06-27-2013 01:37 PM

» Featured Campgrounds

Reviews provided by


All times are GMT -6. The time now is 05:54 PM.


Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.