I just fyi- almost all services are brought in to a panel that has 3 phase. To lower the total load across a single phase. My point is that if the engineer / electrician wired a dual Rv box to feed 2 RV’s the two 30amp May actually be 3pase there and this plug if it is a true 30 amp with neutral could be disastrous. I could see that the manufacturer of this Wye adapter would only connect one power phase for each 30amp plug and the neutrals be connected. (So the plug is only 30amp not 60amp)
But diy’ers might connect both and have the 60 amp as long as these were the same phase otherwise boom!
JCrockett is offline   Reply With Quote
Join the #1 RV Forum Today - It's Totally Free!

iRV2.com RV Community - Are you about to start a new improvement on your RV or need some help with some maintenance? Do you need advice on what products to buy? Or maybe you can give others some advice? No matter where you fit in you'll find that iRV2 is a great community to join. Best of all it's totally FREE!

You are currently viewing our boards as a guest so you have limited access to our community. Please take the time to register and you will gain a lot of great new features including; the ability to participate in discussions, network with other RV owners, see fewer ads, upload photographs, create an RV blog, send private messages and so much, much more!

Old 10-10-2022, 08:11 AM   #58
Senior Member
 
Join Date: May 2018
Posts: 890
Quote:
Originally Posted by JCrockett View Post
I just fyi- almost all services are brought in to a panel that has 3 phase. To lower the total load across a single phase. My point is that if the engineer / electrician wired a dual Rv box to feed 2 RV’s the two 30amp May actually be 3pase there and this plug if it is a true 30 amp with neutral could be disastrous. I could see that the manufacturer of this Wye adapter would only connect one power phase for each 30amp plug and the neutrals be connected. (So the plug is only 30amp not 60amp)
But diy’ers might connect both and have the 60 amp as long as these were the same phase otherwise boom!

If you have two 30 anp outlets wired to supply 2 separate RVs then by definition the neutral wires have to be set up to handle the full 60 amps, so I don't believe you will ever have an issue of overloading the supply neutral.

It's a commercial Y adapter so it's safe to assume that the neutral wires inside the adapter are wired to allow for the two 30 amp wires to both feed the 6 guage terminal in the 50 amp plug to allow 50+ amps on the neutral wire to the RV, since both outlets could be on the same phase.

You could potentially overload the neutral in the rv since 30+30>50 if both are fed from the same phase. But the 6 guage wires are really rated at 55 amps. So to overload it would require almost exactly 30 amps on each of the 2 sides of the electrical system, which is possible, but unlikely so as long as you don't go too crazy you should be fine.

I don't have one of these adapters and can't think of anytime it would have been useful. My motorhome is only 34 feet long and I have a Victron MultiplusII hybrid inverter, so a 30 amp plug doesn't require me to significantly change my electrical usage.
dssl is offline   Reply With Quote
Old 10-10-2022, 12:47 PM   #59
Junior Member
 
Winnebago Owners Club
Join Date: Jun 2019
Location: Kingston, WA
Posts: 10
Blog Entries: 1
I have an adapter that plugs into a 30a and the 15a standard plug to 50a plug, giving you 45a. so if you need 50a and only have a 30a plug it boosts you up to 45a.
Garyst is offline   Reply With Quote
Old 10-10-2022, 01:09 PM   #60
Senior Member
 
Join Date: Oct 2014
Posts: 7,881
Quote:
Originally Posted by Garyst View Post
I have an adapter that plugs into a 30a and the 15a standard plug to 50a plug, giving you 45a. so if you need 50a and only have a 30a plug it boosts you up to 45a.

While I understand what you are saying (assuming the 15 amp outlet is not GFI protected and therefore will not work), BUT


15 +30= 45 OK, but limits one leg to 15 amps.


But that is not 45 vs 50. It is 45 vs 2X 50= 100 amps


So, quite a difference is what you can run.
__________________
Brett Wolfe
Ex: 2003 Alpine 38FDDS. Ex: 1997 Safari Sahara. Ex: 1993 Foretravel U240
wolfe10 is offline   Reply With Quote
Old 10-10-2022, 01:18 PM   #61
Senior Member
 
Join Date: May 2018
Posts: 890
Quote:
Originally Posted by Garyst View Post
I have an adapter that plugs into a 30a and the 15a standard plug to 50a plug, giving you 45a. so if you need 50a and only have a 30a plug it boosts you up to 45a.
That is a different beast. If both the 30 and 15 amp circuits are on the same phase then this can overload the park wires an is a bad idea. You can check this by measuring the hot wire to hot wire voltage. If the voltage is 240 then they are on different phases and no problem. If however the hot to hot voltage measures 0 volts you SHOULDN'T use it.
dssl is offline   Reply With Quote
Old 10-10-2022, 01:18 PM   #62
Senior Member
 
Join Date: Jul 2014
Posts: 35,424
Quote:
Originally Posted by Garyst View Post
I have an adapter that plugs into a 30a and the 15a standard plug to 50a plug, giving you 45a. so if you need 50a and only have a 30a plug it boosts you up to 45a.
That adaptor gives you 30 amps one one leg and 15 amps on the other, not a combined 45 amps.

Your 50 amp cord, in a 50 amp outlet, gives you 50 amps on one leg and and 50 amps on the other leg.
twinboat is offline   Reply With Quote
Old 10-10-2022, 03:29 PM   #63
Senior Member
 
Tha_Rooster's Avatar
 
Join Date: Aug 2008
Location: Georgia
Posts: 8,638
Quote:
Originally Posted by Garyst View Post
I have an adapter that plugs into a 30a and the 15a standard plug to 50a plug, giving you 45a. so if you need 50a and only have a 30a plug it boosts you up to 45a.


I believe you have 15 amps on half of Rv and 30 amps on other side.
__________________
2007 Fleetwood Revolution LE 40V
Tha_Rooster is offline   Reply With Quote
Old 10-10-2022, 03:31 PM   #64
Senior Member
 
Join Date: Oct 2014
Posts: 7,881
Quote:
Originally Posted by Tha_Rooster View Post
I believe you have 15 amps on half of Rv and 30 amps on other side.

Correct. And that is if (unlikely) the 15 amp outlet is not GFI protected.
__________________
Brett Wolfe
Ex: 2003 Alpine 38FDDS. Ex: 1997 Safari Sahara. Ex: 1993 Foretravel U240
wolfe10 is offline   Reply With Quote
Old 10-10-2022, 05:56 PM   #65
Senior Member
 
Join Date: Feb 2017
Posts: 184
Quote:
Originally Posted by twinboat View Post
A 50 amp breaker is a double bbreaker.

You can't put a 60 amp double breaker in its place. You would install a double 30 amp bteaker.

Hmmm... Guess my double pole 70 doesn't exist for my welder either?
Attached Thumbnails
Click image for larger version

Name:	51kiCEkiw9L._AC_SL1178_.jpg
Views:	16
Size:	45.1 KB
ID:	378412  
__________________
'17 Montana 3950BR
Todd727 is offline   Reply With Quote
Old 10-10-2022, 07:07 PM   #66
Senior Member
 
Join Date: Jul 2014
Posts: 35,424
Quote:
Originally Posted by Todd727 View Post
Hmmm... Guess my double pole 70 doesn't exist for my welder either?
The circuit in question is wired for 50 amps. It's against code and a fire hazard to install a larger breaker.

Did you remove a 50 amp breaker and just pop in a 70 amp one for your welder OR did you wire the circuit for 70 amps.
twinboat is offline   Reply With Quote
Old 10-10-2022, 07:19 PM   #67
Senior Member
 
Join Date: May 2018
Posts: 3,204
Welding machines, like motors, have special rules and their own sections in the NEC which allows for circuit sizes that would otherwise be in violation. There are plenty of welding machines and AC units running on AWG 10 wire and 35, 40, 45 and 50 amp circuit breakers, all to code. That has nothing to do with RV circuits.
__________________
Brian, 2011 Winnebago Via Class A on Sprinter Chassis
2000 Jeep TJ toad
Tucson, AZ
bigb56 is online now   Reply With Quote
Old 10-10-2022, 08:50 PM   #68
Community Moderator
 
TonyDi's Avatar


 
Newmar Owners Club
Join Date: Feb 2011
Location: Point Pleasant Beach, NJ
Posts: 31,520
WARNING

The responses are starting to go off topic. Let's get back on track.
__________________
Tony & Ruth........... FMCA#F416727
2016 London Aire 4519, Freightliner chassis, Cummins ISX, 2018 Jeep Wrangler Unlimited, Blue Ox Avail with AF1. TST 507 TPMS
No amount of money can buy you an extra second of time.
TonyDi is online now   Reply With Quote
Old 10-11-2022, 07:21 AM   #69
Member
 
Join Date: Aug 2020
Location: Western New York
Posts: 97
Quote:
Originally Posted by JCrockett View Post
I just fyi- almost all services are brought in to a panel that has 3 phase. To lower the total load across a single phase. My point is that if the engineer / electrician wired a dual Rv box to feed 2 RV’s the two 30amp May actually be 3pase there and this plug if it is a true 30 amp with neutral could be disastrous. I could see that the manufacturer of this Wye adapter would only connect one power phase for each 30amp plug and the neutrals be connected. (So the plug is only 30amp not 60amp)
But diy’ers might connect both and have the 60 amp as long as these were the same phase otherwise boom!
JCrocket brings up an excellent point that I skipped over. At a commercial site, three phase is the most likely source and distribution.

At this point, my take is that the risks of using such an adapter outweigh the potential convenience.
Mongobird is offline   Reply With Quote
Old 10-11-2022, 08:58 PM   #70
Senior Member
 
permitwriter's Avatar


 
Newmar Owners Club
Winnebago Owners Club
Ford Super Duty Owner
Join Date: Jun 2019
Location: Pinckney, MI
Posts: 460
Pulled into a campsite yesterday, typical 50 amp pedestal with a 50 amp outlet controlled by 2 50 amp breakers ganged together, a 30 amp outlet, and a 15 amp outlet. Plugged into the 50 amp outlet and went on my merry way thinking I had all the power we needed.

We're camping with a church group and friends pulled in next to us today. She was complaining about the power supply and explained that they were told at check in that those 50 amp outlets only supply 30 amps. What?!?! I checked my power panel. Sure enough, 30 amps.

Why would they do that? I wonder if it meets code? They didn't tell us, we could have overloaded the 30 amp supply. I guess my dual 30 amp to 50 amp Y cord won't help.
__________________
Mike, Evie, Chelsea, Zelda
2017 Newmar Canyon Star 3513, Safe-T-Plus Steering Stabilizer, Roadmaster Rear Anti-Sway Bar, 2017 Winnebago Brave 31C, Demco Tow Bar, Blue Ox Baseplate
2016 Chevy Colorado Extended Cab, Z71 Off Road Pkg.
permitwriter is offline   Reply With Quote
Reply

Tags
ada, amps



Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
RV is 50 amps, RV Park Spot is 30 amps jmraz73 Winnebago Industries Owner's Forum 30 01-06-2014 05:12 PM
30 Amps vs. 50 Amps! BigRandy Class A Motorhome Discussions 4 01-22-2012 06:53 AM
30 Amps vs 50 Amps !!! BigRandy MH-General Discussions & Problems 16 06-20-2010 06:33 AM
15 amps vs 30 amps Fatbear5 MH-General Discussions & Problems 10 01-26-2010 09:09 AM
Converted trailer from 30 amps to 50 amps. Hitchhiker 5th Wheel Discussion 3 08-30-2006 04:19 PM

» Featured Campgrounds

Reviews provided by


All times are GMT -6. The time now is 08:15 PM.


Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.